Battery s

Brand new to solar.
I decided to give this a look at after being interested in it for about 20 year's. I never did check into it much but thought it was a good ideal.
I bought a 400 watt unit for experiment and just got it hooked up.
It is a Renolgy 400 watt kit along with a Epever 10415AN CC and a Renolgy 3000 watt inverter.
I have 2 of Renolgy 200 AH agm battery s hooked in parallel.
When I turned on the inverter and hooked a .04 amp LED light up to it for a load my battery % went from 97% to 87% right away.
I have it running for about 3 hour's now and my % is dropping fast, at least to me.
1:46 pm=85%
2:07 pm=68%
3:20 pm=54%.
Going to go out and turn it off as I don't want to ruin a battery.
My question is should I have bought these up to full charge with my charger before I tried to us it?
Thanks
Greg
Comments
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
https://www.renogy.com/content/RNG-INVT-3000-12V-P2/INVT-P2-Datasheet.pdf
- 2.5 amps * 12 volts = 30 Watts
I am guessing that your 0.04 amp LED load is at 120 VAC:- 120 VAC * 0.04 amps = 4.8 Watts
- 4.8 watts / 0.85 AC inverter eff = 5.6 Watts 6DC load
- 5.6 Watts DC / 12 volts = 0.5 amps DC load from LED
Your total battery load would be:- 400 AH (at 12 volts) / 3 amp load = 133 hours (to zero State of Charge)
- 100 Percent * 1/133 hours = 0.8% per hour of battery usage
A 3,000 Watt inverter on a 12 volt battery bank draws max current of:- 3,000 Watts * 1/0.85 AC inverter eff * 1/10.5 volts "dead battery alarm" = 366 Amp max draw (2x that for "surge")
Large inverters on 12 volt battery banks is a copper wiring nightmare (thick, heavy, expensive copper cables and connections).At 3,000 Watts, you would probably not even get 1 hour out of your 2x 200 AH @ 12 volt batteries...
For a "nominal" off grid home/cabin design, would be suggesting a 24 or 48 volt battery bank to keep DC currents "reasonable"...
And for a normal rule of thumb, a 12 volt battery bank should be around 100 AH per 250 Watt of AC inverter load... OR:
- 3,000 Watts * 100 AH * 1/250 Watts = 1,200 AH @ 12 volt suggested minimum battery bank size (for lead type batteries)
Your smaller 400 Watt inverter probably drew around 1.0 amps no load...The math, while not great, does not really show why your battery SoC readings are "crashing" so quickly... Should be dropping at less than 1% SoC per hour with your inverter+LED loads...
If you want to do a bit more detailed review/understanding of your solar power system, an AC+DC Current Clamp DMM (Digital Multi-Meter) would be a good tool to have:
https://www.amazon.com/UNI-T-Digital-Handheld-Resistance-Capacitance/dp/B0188WD1NE (example of "good enough" inexpensive meter)
https://www.amazon.com/Auto-Ranging-Resistance-Klein-Tools-CL800/dp/B019CY4FB4 (mid-range priced meter)
Very simple to use... Just "clamp" the meter around one cable and it will show the current (for DC current measurements, you do need to "zero" the meter). Very safe/easy/quick.
Note there are AC only, and AC+DC current clamp meters... AC only meters work fine for 120/240/etc. VAC work--But working with batteries/DC power systems, an AC+DC clamp meter is much more useful.
-Bill
http://members.sti.net/offgridsolar/
E-mail [email protected]
Generally for AGM type batteries you want to see ~14.2 to 14.4 volts "held" for ~2-4 hours when charging...
ANY SHADE on solar panels will dramatically reduce their output current.
At high noon, with battery bank "under" 14.0 volts, 400 Watts of panels (pointed at sun, no shade, working charge controller) should be a (maximum) of:
- 400 Watt array * 0.77 panel+controller deratings * 1/14.0 volts charging = 22 Amps DC Charging current to battery bank
Or roughly 11-22 amps "typical" charging current ("average day", discharged battery bank)... 2 amps on a sunny day into your (probably not fully charged) battery bank.Anyway, you need to get a lot more solar charging energy into your battery bank to be successful... 2 amps is a 0.5% rate of charge.
Ideally, a 10% to 13% rate of charge. You can "get away" with 5% rate of charge for light loads/weekend/emergency backup power:
- 400 AH * 10% = 40 Amps "rated" charging for full time off grid
- 400 AH * 5% = 20 Amps "rated" charging for backup/weekend/emergency use
A solar array for 10% or 13% rate of charge (usually minimum for full time off grid) to upwards of 20/25% rate of charge (depending on your average weather, how many AH/WattHours per day for loads, etc.):- 400 AH * 14.4 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 748 Watt "nominal" array
- 400 AH * 14.4 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 973 Watt "typical cost effective" array
One way to understand how fast (or slow) 2 amp rate of charge is:- If you get 5 hours of "good sun" per day, that is:
0.5% * 5 hours of sun = 2.5% per day charging (excluding battery losses) for a 400 AH battery bank... This is not enough to keep a battery bank "happy"... For an "off grid" power system, 10% rate of charge or 50% bank capacity per day is pretty much the minimum needed....And we have not talked about how much sun you have (location, seasons), and what power you will need (Watts of power * Hours per day)...
-Bill
14.7 volts is usually a bit high. You don't want the batteries to gas and vent... That shortens AGM battery life.
Looking around and found this:
https://m.media-amazon.com/images/I/91f0wZKgDgL.pdf
14.7 or 14.8 volt charging maybe the first time... While you are monitoring (watch that battery does not overheat, you do not hear gassing, etc.)... And they recommend recharging every 3 months (if stored at 100%, and left sitting without charging/float charging).9
EQ charging for AGM is that 14.2 volts held for 8-24(?) hours... This is to ensure that all cells are fully charged (not one cell at 100%, another at 80%, etc.). You may want to do this once every six months (my guess)--But it is not really necessary as AGMs in general cells stay pretty balanced (all cells about the same state of charge).
I would "auto charge" with 14.4 volts as a starting point.
And solar electric panels... Almost any shading (even just one cell) can cause 50% loss of charging power on that one panel (or even more--Depending on array wiring, solar controller type, etc.).
-Bill
An example of what an FLA battery graph looks like:
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.