MX60
jACKr
Registered Users Posts: 16 ✭✭
Curious and Stumped! What signs would a MX60 show, if it was failing?
I have 1 PV string (72vdc) reading correct voltage. At the outback combiner 15' away on uninterrupted 10ga wire, is only reading 10 vdc. That's across the ground buss and the In terminal to the 15 amp breaker, and the buss bar for all breakers
(no other breakers at this time).
MX60 works with battery status display, reads gen charging, when it is.
Any advice is greatly appreciated!
I have 1 PV string (72vdc) reading correct voltage. At the outback combiner 15' away on uninterrupted 10ga wire, is only reading 10 vdc. That's across the ground buss and the In terminal to the 15 amp breaker, and the buss bar for all breakers
(no other breakers at this time).
MX60 works with battery status display, reads gen charging, when it is.
Any advice is greatly appreciated!
Comments
-
A little clarification...
Your array should be round 72 Volts Vmp-array in normal operation?
What do you read with a volt meter on the Vpanel-input to the Breaker/Combiner box and on the Vinput-solar connections to the MX60? Do you read 72 Volts with a DMM?
What does the MX60 report on its screen? Sometimes 72 volts (agreeing with the DMM)? And other times it reads 10 VDC while DMM reports 72 volts/10 volts/or what?
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Check for loose connections.
Is that "ground buss' in the combiner, where the PV negatives connect.
Try measuring the PV voltage in the combiner between the PV negative cable, and the PV + bussbar. I do not know if you have multiple strings of PVs or not, it is all a mystery, to me.
Good Luck, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Aloha Vic, Just 1 string totaling 72vdc. More to come.
I think you just gave me a clue? I recently removed some older 12vdc PVs. I haven't cleaned up the old 6ga (tells you how old?) wire yet, they're still connected at Bussbar. And waiting for removal. I only removed the old Positive leads from breakers, hoping to save $.
I may of miscalculated by leaving the old 6 Ga for ground side of the new PVs.?
The problem started when I took the above mentioned PVs down. Something may of loosened? Or, I simply can't use 2 different gauges, 10Ga + and 6Ga-? It worked for 3-4 months.
I appreciate your response? -
I greatly appreciate your input. I had inadvertently loosened the ground buss.
-
jACKr said:I greatly appreciate your input. I had inadvertently loosened the ground buss.
This sounds encouraging. Hope that things will work much better, now. Good Luck, take care, thanks for the update, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed