I am getting ready to add more solar panels to my existing array of 2,135 Watts.
I have been given (8) Suniva OPT280-60-4-1B0 panels, with micro inverters, (which I will not use)
Vmp =31.9v and Imp=8.78a on each panel
I will add another controller to go with my outback flex 80 for those. Another combiner box to connect the panels.
Question is Will the total Watts of the 8 280-Watt panels be too much for the outback 80?
I plan on each two panels connect in series then run four to my box.
I have been given (8) Suniva OPT280-60-4-1B0 panels, with micro inverters, (which I will not use)
Vmp =31.9v and Imp=8.78a on each panel
I will add another controller to go with my outback flex 80 for those. Another combiner box to connect the panels.
Question is Will the total Watts of the 8 280-Watt panels be too much for the outback 80?
I plan on each two panels connect in series then run four to my box.
Comments
-
Still 24 VDC battery bank?
The typical "optimum" max power would be:- 29.0 volts charging * 80 amps * 0/0.77 panel+controller deratings = 3,013 Watt array maximum suggested "optimum"
https://www.solar-electric.com/lib/wind-sun/Outback_FM60_FM80_Specifications.pdf
Page 100 of the manual does not say much more about array design (other than Voc-cold):
https://www.solar-electric.com/lib/wind-sun/Flexmax-manual.pdf
In general, good quality MPPT controllers limit their output current to max rated (and derate as controller runs hot)...
You also need to check Voc-array-cold for your location--From the Outback manual and guessing you are in Texas, and that it does not get much below freezing in your area:
Cooler climates can cause the Voc to rise above the array’s rated Voc. In climates that observe temperatures less than about –15°C (5°F), a Voc greater than 125 Vdc is not recommended.
o Hot weather: lower Voc and lower Vmp o Cold weather: higher Voc and higher Vmp If the specific voltage temperature correction factor is not known for a particular module, allow for ambient temperature correction using the following information:
25° to 10°C (77° to 50°F) multiply Voc by 1.06
9° to 0°C (49° to 32°F) multiply Voc by 1.10
–1° to –10°C (31° to 14°F) multiply Voc by 1.13
–11° to –20°C (13° to –4°F) multiply Voc by 1.17
–21° to –40°C (–5° to –40°F) multiply Voc by 1.25 1
145 Volts is max "starting voltage":- 145 VDC max operational / 1.13 derate = 128 VDC Voc-std array voltage
Voc-std ~ 39.2 VDC- 128 VDC temp corrected Voc-array-max / 39.2 VDC panel-std = 3.3 panels in series = 3 panels in series max
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Yes Bill, 24 volt system and gulf coast Texas ,Sugar Valley area close to Van Vleck Texas.
-
If total 2240 Watts is too much for outback, would the Midnite solar 150 charger work and still be able to charge the same battery bank along with the Outback?
-
I don't think it is too much for the Outback... But I am not the expert here. "Over paneling" by 1/0.77 or 1/0.75 (1.33x) is normal.
Perhaps others here can confirm.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Midnite classic 150 will output 2700 watts @ 24 v0lts nominal.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
If your inverter/charger is an outback you should stay with them for the whole system so they can be networked.
If this is Offgrid you will not be heat stressing equipment like a grid tie, I would not worry about 2240W nameplate for an 80 A controller.
Good Luck!"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed