Outback radian/48v system questions

100% off grid system, self design and install. Radian 8048,2 - fm80 charge controllers assembly on a pre box. 8kw panels fixed mount approx 45 deg angle south. 1350 AH rolls lead acid 2v,L16 battery bank.
Monitor with a mate 2 and optics re.
Constant draw approx 600w, running a largish 4200sq ft home in Central utah.
Problem #1 seems like even when the system hits 100% charge and goes to float it drops overnight to low 80%high 75+ and on overcast winter days usually won't make it to sunrise without kicking off to protect batt at around 70% -46v
Problem #2 after previously running a commercial generac diesel jobsite generator to carry the off days for 3 years I bought a brand new diesel multiquip with a touch more output. The new one runs everything fine as expected but twice now has somehow either surged or something and tripped every gfci in the home, 12 of them to be exact. Swapped back to the old generator, no problem again. Any ideas or direction would be greatly appreciated, sorry for the long post in advance!
Monitor with a mate 2 and optics re.
Constant draw approx 600w, running a largish 4200sq ft home in Central utah.
Problem #1 seems like even when the system hits 100% charge and goes to float it drops overnight to low 80%high 75+ and on overcast winter days usually won't make it to sunrise without kicking off to protect batt at around 70% -46v
Problem #2 after previously running a commercial generac diesel jobsite generator to carry the off days for 3 years I bought a brand new diesel multiquip with a touch more output. The new one runs everything fine as expected but twice now has somehow either surged or something and tripped every gfci in the home, 12 of them to be exact. Swapped back to the old generator, no problem again. Any ideas or direction would be greatly appreciated, sorry for the long post in advance!
Comments
so I’m think 600 watts is for your larger system is ok .
My observation is the inverter system uses a lot of power by it self and it makes little diffrence if I’m burn power all nite
or if my inverter is inverting with little draw . I use 10 to 15% over nite .
I’m thinking you are not full charged and need to check the SG of the battery’s at the end of the charging day .
My generator gosent pop them , but heavy draw equipment pops them all the time .☹️
I would not think that would set off the breakers down stream .