we have a 400 watt wind generator and a 200 watt solar panel on a bank of 4 batteries and they are running cctv and not coping as wind generator is not kicking in we have the dual control panel .The solar is working but cant cope , thanks for any advice .
Comments
-
How many batteries?
And what is "cctv"?Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year. -
security cameras 4 x 110 amp batteries don't last more than a couple of days
-
Welcome to the forum WorDave,
CCTV=Closed Circuit TV (security cameras)?
To help you here--Details matter.
What is your daily energy usage? Amp*Hour at XX Amp*Hours or XXX Watt*Hours per day?
What is your battery bank type and size (Lead Acid / Li Ion / XX Volts and YYY Amp*hours)?
Location... I guess you are somewhere in Great Britain... So not a lot of sun, on average.
What is the "dual control panel"? (one Solar and one Wind controller?)
My suggestion... Define your power needs. Design the battery bank to support those loads (typically 2 days of storage and 50% max discharge). And design the solar array to both power your loads (based on minimum sun such as December to both charge the battery bank and support your loads--And if you want to have minimum genset/backup power--The solar array should support 2x your daily loads at minimum predicted sun for December.
The wind turbine would, hopefully, supply energy during cloudy/windy conditions---Personally, I am not a fan of small wind systems. They tend to not perform very well (at least most of the units you can purchase) and they require maintenance (need to tilt tower down and/or a lift truck to access turbine).
Like to get the solar working first.
So, working backwards, what could a 200 Watt solar panel support battery and load wise?
The battery bank should be charged at 5% to 10% to 13% rate of charge--And 10% minimum for a full time off grid system suggested (usually for deep cycle lead acid storage batteries--10% to 13% is a good rate of charge for battery life).- 200 Watt array * 0.77 derating * 1/14.5 volts charging = 10.6 Amps nominal (average best case charging current)
- 10.6 Amps * 1/0.13 rate of charge = 82 AH @ 12 volts minimum battery bank
- 10.6 Amps * 1/0.10 rate of charge = 106 AH @ 12 volts nominal battery bank
- 10.6 amps * 1/0.05 rate of charge = 212 AH @ 12 volts "max suggested" battery bank
- 26.5 AH / 25 hours per day = 1.1 Amp average load (for CCTV system @ 24 hours per day)--Example
- 106 AH * 1/2 days of storage * 0.50 max discharge (for long battery life) = 26.5 AH per day @ 12 volts suggested load
- 26.5 AH * 12 volts = 318 Watt*Hours per day suggested battery load
http://www.solarelectricityhandbook.com/solar-irradiance.htmlNewcastle upon Tyne
Measured in kWh/m2/day onto a solar panel set at a 20° angle from vertical:
Average Solar Insolation figures
(Optimal winter settings)
For December, a 200 Watt array would produce (on average):Jan Feb Mar Apr May Jun 1.24
2.22
3.03
3.76
4.33
4.07
Jul Aug Sep Oct Nov Dec 3.95
3.85
3.34
2.52
1.46
0.98
- 200 Watts * 0.61 DC off grid system eff * 0.98 hours of sun per day (December) = 120 WH per day
- 120 Watts * 0.5 solar fudge factor "base load" derating = 60 Watts suggested average base load support with 200 Watt panel in December in Newcastle upon Tyne (I really like the city names in the UK)
The idea would be to upgrade your solar panels (more panels) at least, to get the system were it works "most of the time"--Then look at wind for stormy weather backup (if that is your only other option).
Your thoughts/corrections/updates?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I am not sure as i dont know a lot about it ,I know the windmill isnt running ,yes i live in the north east of England plenty wind not a lot of sun , thanks for your reply i will try and work it out ,get back to you .
-
Yep add solar . Pv is cheap and no moving parts .2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed