Hi
i have just change my inverter to an 8kw hybrid from mpp company.
have 8 solar panels of 500w each
voc 58.95 isc 10.28
had in parrallel and serie total 98v and the company said the best is 8 panel in serie gives me 472
max voc of 500vdc the inverter take
had a question as both the 98v and the 472b v charge the batteries but which combination is better?
have 16 batt of 12 v 250 ah
awaiting a reply of some of my friens on this forum
Bob
i have just change my inverter to an 8kw hybrid from mpp company.
have 8 solar panels of 500w each
voc 58.95 isc 10.28
had in parrallel and serie total 98v and the company said the best is 8 panel in serie gives me 472
max voc of 500vdc the inverter take
had a question as both the 98v and the 472b v charge the batteries but which combination is better?
have 16 batt of 12 v 250 ah
awaiting a reply of some of my friens on this forum
Bob
Comments
-
Bob,
Can you give us a link to the Hybrid Inverter specifications you wish to use?
Also, what are the Vmp/Imp specifications of your panels?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
hi Bill
model pip8048max max pv array power 8kw max pv array open circuit voltage 500vdc pv array mppt range 90vdc-450vdc
start up voltage voc 80vdc
panel vmp 48.63 voc 58.95 imp 10.87A isc 10.28 A
its written : please make sure that the max input voltage of each pv input connector is 18
for your info I do have 4 battery banks in use each battery is250ah 12v
Hope this is sufficient
Robertsorry i mean max input current of each pv input connecter is 18AGood day Robert,
First, we should keep the discussions in your "thread", and not post on your wall (don't check walls for Q&A's).
I did not find a manual on a quick search--Just these links:
https://www.mppsolar.com/v3/pip-max/
http://www.mppsolar.com/v3/catalogs/PIP-MAX.pdf
This unit has 2x solar input PV inputs, each a max of 18 Amps.
With your panels having an Imp of 10.87 Amps it looks like you are limited to one string per input. 100 VDC minimum (Vmp-array-hot) and 500 VDC max (Voc-array-cold).
You are on a warm Caribbean island Curaçao as I recall, so you do not have very cold winter temperatures (not below 20C?).
The min/max number of series connected panels:- 100 VDC / 48.63 Vmp-std = 2 panel in series minimum ( would suggest 3 series to allow for hot panels/hot weather relaible starting of charge controller)
- 500 VDC / 58.95 Voc-cold = 8.45 = 8 panels max series
- 8 series panels * 48.63 volts Vmp * 10.87 amps Imp per string (one per 2 total PV inputs) = 4,229 Watt array with 8 panels only
- 8 series panels * 48.63 volts Vmp * 10.87 amps Imp * 2 parallel strings (one per 2 total PV inputs) = 8,458 Watt maximum array with 16 panels
- 4,229 Watt array * 0.77 typical panel+controller deratings = 3,256 Watts typical best case (cool/clear day/solar noon/ few hours a year)
- 3,256 Watt effective array * 1/59 volts battery charging = 55 Amps typical "best case" charging current with 8 panels (at 59 VDC battery bus--Max of controller 120 Amps)
- You have the option of 8 series x 1 string, or, 4 series x 2 strings... Either would work (suggest 8s x 1p as you can use smaller diameter copper wire and/or longer wire run from array to inverter-charger)
- 1,000 Watt AC inverter and solar array suggested max per 100 AH battery bank * 250 AH = 2,500 Watt max AC inverter and array
For a solar array, fixed:
http://www.solarelectricityhandbook.com/solar-irradiance.htmlWillemstad
Measured in kWh/m2/day onto a solar panel set at a 78° angle from vertical:
Average Solar Insolation figures
(For best year-round performance)
The average daily harvest for April on a fixed array woud be:Jan Feb Mar Apr May Jun 6.65
6.95
6.92
6.23
6.58
6.78
Jul Aug Sep Oct Nov Dec 6.74
6.61
6.42
6.41
6.28
6.32
- 4,229 Watt array * 0.52 off grid AC system eff * 6.23 hours of sun per day (April) = 13,700 WH per day
- 70 watts * 24 hours per day = 1,680 WH per day (or >10% of your daily harvest)
- 70 Watts / 48 VDC battery bank = 1.5 amps
- 1.5 amps inverter Tare * 24 hours per day = 36 AH
- 36 AH per day / 250 AH battery bank = 0.144 = 14.4% of your battery bank capacity discharge
If there are special needs (lots of power for a short period of time--Such as a shop) and used AGM or LiFePO4 batteries--Maybe would make sense for your needs. On the other hand, you do live in a "very sunny" location.Also one quick search for your hybrid inverter-solar charger--Make sure you have current firmware--They have been making updates/bug fixes:https://forums.aeva.asn.au/viewtopic.php?t=6714-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed