Fuse help on small solar setup.
kcarr2010
Registered Users Posts: 1 ✭
I know this has to been asked 100 times but I want to make sure I got it right.
2 - 100w panels wired parallel.
1 -2000w inverter
1 -12v 100ah battery
1 - 20a charge controller
So from what I gather I need a 30 amp fuse between the panels and the charge controller. I need a 20a fuse between controller and battery and last I need a 200a fuse between battery and inverter. Is this correct. Sorry I am new so if i left something out in the description please let me know.
I appreciate your help!!
Thank you
Kyle
2 - 100w panels wired parallel.
1 -2000w inverter
1 -12v 100ah battery
1 - 20a charge controller
So from what I gather I need a 30 amp fuse between the panels and the charge controller. I need a 20a fuse between controller and battery and last I need a 200a fuse between battery and inverter. Is this correct. Sorry I am new so if i left something out in the description please let me know.
I appreciate your help!!
Thank you
Kyle
Tagged:
Comments
-
Welcome to the forum Kyle2st, your 100 AH battery (assuming a flooded cell Lead Acid) can, at best, supply about 20% of its AH capacity for any length of time. I.e.:
- 100 AH * 0.20 (C/5 rate of discharge) = 20 Amps continuous max suggested
- 20 amps * 12 volts = 240 Watts
- 2,000 Watts * 1/0.85 AC inverter eff * 1/10.5 battery cutoff = 224 Amps
- 100 AH / 224 amps * 60 min/Hr = 26 minutes (an in reality, at high discharge rates AH apparent capacity goes down)
- 200 Watt array / Vmp~18 volts = 11.1 amps in full sun
- 100 AH / 11.1 amps = 9 hours of full sun
I suggest that a 2,000 Watt 12 VDC AC inverter would need an ~800+ AH Lead Acid battery bank @ 12 volts minimum to run somewhat reasonably, and a 1,200 to 2,400+ Watt solar array...
Regarding fuses/circuit breakers, I would suggest that you take the planned maximum current, and use the NEC derating factor of 1/0.80 or 1.25x against fuse/breaker ratings to prevent false trips (generally a breaker/fuse will not trip at 80% of rating, and should trip at 100%+ of rating).
Your thoughts?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
WRT to fuse/breaker sizing, note that these should be sized to protect the smallest connected wiring. For example, you could (but shouldn't) wire the inverter to the battery with some small gauge wire, for which a 200a fuse would be far too big.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed