Different Solar Panels
Comments
-
It is more complicated than what you ask... Need to start from the beginning.
- What is battery bank Voltage / AH rating / type (FLA, AGM, LiFePO4, etc.)?
- What is the minimum temperature for your location (i.e., tropical island at 65F, or far north at -40F)?
- Look up limits for controller: MPPT type (MorningStar has a PWM model that looks identical and named very similarly):
The TriStar TS-MPPT-60 MPPT is designed for off-grid PV systems as large as 3.0 kWp, and is rated for 60 amps at up to 150 volts PV open circuit. This product is extremely reliable since it has a robust thermal design, no internal cooling fan and no mechanical relays.More or less, the input requirement of the TS MPPT controller is 150 VDC max (which works out to around 110 volts or less Vmp-array--Note we are looking for Vmp-array-cold to be less than 150 VDC (to not damage the controller).
Vmp-array minimum voltage is typically Vmp=17.5 volts @ 12 volt bak; Vmp-array=35 volts @ 24 volt bank; and Vmp-array=70 volts @ 48 volt bank.
Vmp-array "Optimum Voltage" is typically around 2x (roughly) Vbatt--I.e., 14.8 volts charging then 2x14.8v=29.6 volts Vmp-array optimum (up to Vmp-array~110 volts or so max for very cold climates). The controller works fine at any of those voltages, but is usually 1-2% or so less efficient closer to 110 Volts Vmp-array.
Your panels appear to be:- 2x 200 Watts / 21.052 volts Vmp (are you sure? That is not a very standard voltage) = 9.5 Amps Imp
- 1x 150 Watts / 17.85 Volts Vmp = 8.4 amps Imp
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks Bill for getting back with me. I have one 150 Vikram Eldora panel seen here: https://www.vikramsolar.com/wp-content/uploads/2016/04/ELDORA-150P-Micro-Series-1.pdf. and 2 x 200 watt Hightec solar panel seen here: https://www.continuousresources.com/collections/solar-panels-and-hardware/products/hightec-solar-200w-36-cell-12v-nominal-solar-panel-5-busbar
My battery bank is 4 T105 Trojan batteries for a total of 450 amp hours, I believe, and it is a 12 volt system. I have 2 TS-MPPT-60 Controllers. One controller has the set up above and the other has 3x 200 watt Hightec solar panels. This system is on an RV. Six months out of the year the RV gets used in the winter in Arizona. The other six months it is in storage in Michigan.
There is a huge difference on the output of the controllers. I have been trying different things but the bank with the 150 watt panel just does not preform well. I have a little bit of log data on the 2 banks. The left column is controller 1 and the right column is controller 2. My absorption rate is set to 14.82. This data is being logged in south western Arizona.Date
Max Batt Voltage
Min Batt Voltage
Amp Hours
Watt Hours
Max Array Voltage
Max Array Watts
Minute Absorption
Minutes in Float
Time Equalize
Trimetic % Return
Weather Condition
12/11/2020
14.9_14.9
12.7_12.7
25.5_46.6
360_670
69.7_70.8
437_526
210_210
141_141
107
Mostly Cloudy
12/12/2020
15.5_15.5
11.9_11.9
59.4_79.1
860_1140
68.5_69.9
454_569
248_246
0_0
96_96
114 eq to 120
Sun Morning
12/15/2020
16.4_15
11.9_11.9
50.8_75.1
720_1070
69.7_70.9
487_642
205_209
0_0
107
Sunny
12/16/2020
15.5_15.5
12.1_12.1
62.4_106.4
890_1530
24.5_70.5
427_672
246_204
0_0
112
Sunny
12/17/2020
13.8/13.8
11.6_11.6
42.8_63.8
560_850
23.3_70.3
217_347
0_0
0_0
87%
Cloudy
12/18/2020
15.3_15.3
11.6_11.5
85.8_138.2
1190_1930
24.2_70.4
426_658
112_50
0_0
110%
Sunny
12/19/2020
15.3_15.4
11.8_11.8
71.2_107.3
1020_1530
65.9_70.3
427_659
246_247
0_0
120%
Sunny
12/20/2020
15.4_15.4
11.8_11.8
66.2_96.6
940_1400
69.1_70.2
582_642
317_259
0_0
116%
Sunny
12/21/2020
15.4_15.3
11.8_11.7
62_108.6
870_1570
68.3_69.4
613_652
294_243
0_0
112%
Sunny
12/22/2020
15_15
13.1_13.1
22.5_75.8
320_1110
67.3_69.6
626_668
89_152
188_0
Reset controller
118%
Pt Cloudy
12/23/2020
15.3_15.3
11.8_11.7
61.6_114.4
860_1650
70.1_70.6
642_720
259_187
0_0
111%
Pt Cloudy
12/24/2020
-
Hi Bill, Starting from the paper design side... 5% to 10%-13% rate of charge:
- 450 AH * 14.5 volts charging * 1/0.77 panel+controller deraring * 0.05 rate of charge = 424 Watt array minimum (backup system/summer/sunny weather usage)
- 450 AH * 14.5 volts charging * 1/0.77 panel+controller deraring * 0.10 rate of charge = 847 Watt array nominal (full time off grid minimum suggested)
- 450 AH * 14.5 volts charging * 1/0.77 panel+controller deraring * 0.13 rate of charge = 1,102 Watt array "typical" cost effective maximum
The Eldora panel is Vmp~17.85 volts per panel and Imp~8.41 amps.
Hytech is Vmp~21.052 volts (seems a bit high) and Imp~9.5 amps.
The controller 1 and controller 2 are reporting Vmp-array near 70 volts... That would seem to indicate that you have 3x panels (?) in series for each. Although, controller 1 indicates a couple days at ~24 volts max voltage... Does not make sense (bad panel/weird connections)?
I don't see how you are reaching those voltages with just 2x panels in series for both controllers... But that configuration (2x sets panels in series on 2x different controllers) is fine for now.
Battery votlage is a bit high... Typically around 14.75 volts @ 75F for absorb charging... >15.x volts is for Equalize charging... Although, it is possible for batteries to exceed 15.x volts for short periods of time as the MPPT controllers sweep to figure out Vmp/Imp for the array (guessing).
Your Trimetric numbers seem to be good... You are typically recharging >=110% (AH?) most every sunny day.
Low battery voltage is pretty low--Unless you have surge loads (typically want to avoid running below ~11.5 volts except for short periods of surge loads--Such as starting a pump/motor). You are pulling 100-200 AH per day (both controllers added together). Typically like to see ~25% for daily loads (0.25*450AH=125 AH per day) to 50% discharge for an RV/heavy loading... It seems to be that you are "using" your battery bank/solar harvest pretty well.
Things to check for... Controller 1 and 2 -- May be identical configuration/arrays--But they will probably not be in "sync"--Minor differences in voltage readings/accuracy of meters could make one go to float sooner/etc... Perfectly OK. The controller with the 'highest' effective charging voltage "wins".
I suggest that each controller be "home run" back to the battery bus ("star" wired--Each controller has its own wiring back to the battery bank). Suggest to not "daisy chain" from controller 1 to 2 to battery bank (one set of cables shared for both controllers to battery bank). Sharing the wiring can cause controllers to confuse each other.
The other thing to make sure... Always connect controllers to battery bank first, then to the (energized) solar array. And disconnect solar first, then battery bank. Some controllers can get "confused" when booted from the solar array first--Or even be damaged.
If you have a voltmeter--Measure the Vpanel and Vbatt terminal voltages of the controllers (under sun, hopefully charging). Would like to double check the Varray and Vbatt voltages at the controllers (you can also measure Vbatt bus at the same time--Vbatt controller and Vbatt bus should be very close).
Your numbers are a bit "erratic" for the solar charge controllers--But they do seem to be work pretty well (and confirmed with the Trimetric).
Your panels (voltage does not make sense)--But if you have 2x series panels on two different TS MPPT 60 controllers, that is fine too.
Checking voltage with a meter at various points (and times of day) to confirm operation... A hydrometer would be nice too (specific gravity)...
Is the system working (producing energy) the way you expect?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
The controller 1 and controller 2 are reporting Vmp-array near 70 volts... That would seem to indicate that you have 3x panels (?) in series for each. Although, controller 1 indicates a couple days at ~24 volts max voltage... Does not make sense (bad panel/weird connections)?
You are correct 3 panels in series..The 24 volt max voltage days is when I series 2 200w hightec panels and just hooked the 150 Vikram into the combiner box. I believe in that type of installation the control would read the lower voltage panel.
Battery votlage is a bit high... Typically around 14.75 volts @ 75F for absorb charging... >15.x volts is for Equalize charging... Although, it is possible for batteries to exceed 15.x volts for short periods of time as the MPPT controllers sweep to figure out Vmp/Imp for the array (guessing).
I believe this is more about temperature compensation that anything else. My absorption set point is 14.82 volts compensated at .005 v/cell would easily put me over 15 volts on days below 25*c
Low battery voltage is pretty low--Unless you have surge loads (typically want to avoid running below ~11.5 volts except for short periods of surge loads--Such as starting a pump/motor). You are pulling 100-200 AH per day (both controllers added together). Typically like to see ~25% for daily loads (0.25*450AH=125 AH per day) to 50% discharge for an RV/heavy loading... It seems to be that you are "using" your battery bank/solar harvest pretty well.
It would be surge loads......I get up in the morning and have to have a cup of coffee. My coffee pot draws the voltage down but is recovers quickly. I use 20 to 30% of my battery capacity most nights as taken from my trimetric
Things to check for... Controller 1 and 2 -- May be identical configuration/arrays--But they will probably not be in "sync"--Minor differences in voltage readings/accuracy of meters could make one go to float sooner/etc... Perfectly OK. The controller with the 'highest' effective charging voltage "wins".
Interesting
I suggest that each controller be "home run" back to the battery bus ("star" wired--Each controller has its own wiring back to the battery bank). Suggest to not "daisy chain" from controller 1 to 2 to battery bank (one set of cables shared for both controllers to battery bank). Sharing the wiring can cause controllers to confuse each other.
Well Bill.......This may be some of my problem! As it stands now I do have one set of cables running to the battery bank. This is an easy fix I hope. The reason I have done this is the lack of termination space on the battery terminals. I will look at this today and try and make changes.
Your numbers are a bit "erratic" for the solar charge controllers--But they do seem to be work pretty well (and confirmed with the Trimetric).
I have made a lot of adjustments to the wiring of the combiner box to try and get the best output to the batteries. This would explain why the numbers are so erratic. I will get a weeks worth of data before I make any more changes
Your panels (voltage does not make sense)--But if you have 2x series panels on two different TS MPPT 60 controllers, that is fine too.
At present I have taken the odd 150 volt panel out of the mixture. I am running with 3 hightec panels in series to controller #1 and 2 hightec panels to controller #2. I will keep it this way for sometime to gain some logging data.
Is the system working (producing energy) the way you expect?
The system is working fairly well considering the shorten days. It does get back to 100% charge most everyday. The specific gravity is a little bit different in the cells on a daily basis I would like to see the trimetric return a bit more "return percentages" maybe 115% to 120% daily. I have been working a little on the temperature compensation to accomplish this. I do equalize about once every couple of months. For the most part I am happy with it. I believe I will leave that odd ball panel off. If I ever think I need more wattage I will get a another Hightec panel. Too many variables mixing different panels.
Thanks Bill for all this information!! Merry Christmas!
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed