New system set up
Bobbler
Registered Users Posts: 1 ✭
Hi Everyone
I recently purchased a hunting camp and set my system in place but not sure I am maximizing it potential
I have two 245w panels going to eleven 40 Amp mppt charge controller going to two 6v 225ah golf cart batteries running to a 12 v 1000w inverter
only draw in camp is led lights, one ceiling fan and television
the camp is wire so I just feed into my distribution box which has 2 15 amp breakers
eve works fine
I have 34.8v and 2.7amp 87.1 w going to batteries my batteries are at 14.6v 6.2amps my controller is currently set on manual default settings she I be setting my own peripherals in to controller if so what would be best for my set up
thanks any help would be appreciated
I recently purchased a hunting camp and set my system in place but not sure I am maximizing it potential
I have two 245w panels going to eleven 40 Amp mppt charge controller going to two 6v 225ah golf cart batteries running to a 12 v 1000w inverter
only draw in camp is led lights, one ceiling fan and television
the camp is wire so I just feed into my distribution box which has 2 15 amp breakers
eve works fine
I have 34.8v and 2.7amp 87.1 w going to batteries my batteries are at 14.6v 6.2amps my controller is currently set on manual default settings she I be setting my own peripherals in to controller if so what would be best for my set up
thanks any help would be appreciated
Tagged:
Comments
-
I have the same set up on my trailer , the cc charges @ 14.6 and eq every month automatically the battery’s are going on 6 seasons but sits Jan feb March .My new system is charging at 14.8 and 14.9 with 2/3hr absorb
my battery’s seam to like more charge in the winter .I don’t get a lot of sun this time of year , I have 3” of snow on them now.Out back flex power one with out back 3648 inverter fm80 charge controler flex net mate 16 gc215 battery’s 4425 Watts solar . -
Welcome to the forum Bobbler,
I am not quite sure what you intended here "two 245w panels going to eleven 40 Amp mppt"....
Anyway... I am always a big fan of designing a "balanced" system... Loads->battery bank; battery bank->minimum solar array; loads/sun->array too...
So, battery bank is the heart of your system. I will use our rules of thumbs for a full time off grid cabin. But, of course, we can adjust based on your needs (weekend summer usage, etc.)... A good optimum is to define the battery size based on 2 days of storage and 50% maximum discharge (longer battery life, good day to day operation):- 12 volts * 225 AH battery bank * 0.85 AC inverter eff * 1/2 days storage * 0.50 max planned discharge = 574 Watt hours per day battery power
Charging the battery bank, 5%, 10%, 13%+ are common aim points. 5% can work for a summer/weekend cabin. 10% minimum for full time off grid (and good battery life). 13% or so is typically the cost effective maximum unless you have special needs (lots of power during the day, vs using batteries mostly overnight/cloudy weather):- 225 AH * 14.5 volts charging * 1/0.77 solar panel+controller deratings * 0.05 rate of charge = 212 watt array minimum
- 225 AH * 14.5 volts charging * 1/0.77 solar panel+controller deratings * 0.10 rate of charge = 424 watt array nominal
- 225 AH * 14.5 volts charging * 1/0.77 solar panel+controller deratings * 0.13 rate of charge = 551 watt array "typical" cost effective maximum
http://www.solarelectricityhandbook.com/solar-irradiance.htmlOttawa
Measured in kWh/m2/day onto a solar panel set at a 45° angle:
Average Solar Insolation figures
(For best year-round performance)
Lets say drop the bottom three months... assume you are not there, or us a genset when needed.... I will use the 25% per day battery capacity... But actual energy usage numbers are critical for system planning:Jan Feb Mar Apr May Jun 2.63
3.66
4.48
4.74
4.75
4.92
Jul Aug Sep Oct Nov Dec 5.04
4.83
4.23
3.19
2.30
2.09
- 574 Watt*Hours per day * 1/0.52 off grid AC system eff * 1/3.19 hours of sun per day (October) = 346 Watt array October "break even" month
- guess 574 Watts daily base load * 1/0.52 off grid AC eff * 1/3.19 hours of sun (Oct) * 1/0.65 base load fudge factor) = 532 Watt array (65% baseload fudge factor--Reduce genset runtime/more solar power during poor weather)
- 245 Watt panel * 2 panels * 0.52 offgrid system eff * 3.19 hours of sun (October long term average) = 813 WH per ave Oct day
- 225 AH * 250 Watts/100AH (for 12 volt battery bank) = 563 Watt max suggested AC inverter for your bank
If you want to add more panels/battery bank later to the existing controller... The typical "cost effective" maximum array would be:- 40 amps * 14.5 volts charging * 1/0.77 panel+controller derarings = 753 Watts (rough) maximum array for 40 amp MPPT controller
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed