Enphase IQ7X-96 micro inverter application
Davtherav1
Registered Users Posts: 1 ✭
I have a large number of REC 235 PV panels and after looking at the specs for the IQ7X-96, I realized that two of my panels wired in series would meet the spec for one IQ7X-96. Any concerns you would have about an installation of this sort?? Cost savings would be significant if one inverter would service two smaller PV panels. thanks, dave
Comments
-
Looking at the IQ7 and REC 235 specifications... It appears that you could have issues in cold weather (you are in Colorado).
http://www.solardesigntool.com/components/module-panel-solar/REC-Solar/541/REC230-PE-US/specification-data-sheet.html
https://enphase.com/sites/default/files/downloads/support/IQ7X-DS-EN-US.pdf
So, you need to know the minimum temperature for your location, and see what the Voc-array-cold maximum would be. Two of your panels in sereis could exceed the 79.5 VDC max input voltage (in sub freezing temperatures?).
The IQ7 is designed for 96 Cell panels... Your two panels in series would be 60+60=120 cells.
Also, there is always the question of how you will be monitoring your panels/arrays. Will you get an Enphase monitoring box too (wireless networking) so you can keep track of how everything will work?
Using a string sizing tool from Midnite Solar:
http://www.midnitesolar.com/sizingTool/index.phpPV Array Rated PV Array Power: 460 Watts Anticipated Array Power @ 95F: 439 Watts Rated PV Array Current: 7.8 Amps Battery Charging Current @ 57.6 V: 8 Amps VMP (Maximum Power Point Voltage) : 58.8 Volts VOC (Open Circuit Voltage): 74.2 Volts VMP @ 0 F°: 70.2 Volts VOC @ 0 F°: 84.6 Volts Classic, Classic SL & Classic Lite Charge Controller Selection150 200 250 Max Operating Voltage 150 200 250 Max Non operating VOC (HyperVOC) @ 48V Nominal Battery Voltage 198 248 298 Maximum Number Of Modules In Series 3 4 5 Max Number Of Modules In Series (Using HyperVOC) 4 5 7 Max Allowable Output Current Per Classic
Based On This Current Configuration86 78 55 Max Allowable Wattage Per Classic
Based On This Current Configuration5022 4550 3212 Present PV Array Wattage Of This Configuration 460 460 460 Design Check Max VOC OK OK OK Temperature The Classic Will
Enter HyperVOC-481 F° -848.2 F° -1215.4 F° Array Power (Wattage) OK OK OK Classics Required 0.1 0.2 0.2
Voc-cold would be ~84.6 VDC at 0F (guessing your cold weather minimum temperature) and exceed the IQ7 79.5 volt max.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed