Inverter set up for a three phase 7.25kw system
greenlightenergy
Registered Users Posts: 1 ✭
I have got myself in a bit of a quagmire - my company has just signed a sales agreement for a 7.25 kw system. The small commercial building has three phase 240v main feed. We are trying to figure out what inverter to use for such a system. SolarEdge, the inverter company we use, doesnt make three phase inverters sub 9k. Solaredge recommends buying three 3k single phase inverters but that doesnt sound right to me either. We target 1.3x dc for inverters as it is hot where we install and it is rare to have a perfectly south array. If anyone has ran into this problem before and has a suggestion, I'd really appreciate your suggestion.
Comments
-
Check with the customer's utility/engineering department... If I recall correctly, our utilty allows a maximum 10 kWatts of "unbalanced" power between phases (at least for smaller installations. Many of the smaller 3 phase installations have only two pole transformers (open Delta)--So, back feeding 3 phases (or the "wrong" phase) may be an issue for the utility (don't know, just something else to watchout for).
There should be no issue with 2x 3.5 kWatt inverters (single phase). Or even 1x 7.25 kWatt inverter (again single phase).
You may get into the question of having a loss of phase shutdown for the 1/2 inverter solution (if one phase is lost, then all three phases for GT inverter may need to be shutdown for safety/utility issues). I am sure there is lots of "stuff" out there that can be used (directly on AC output of GT inverters, or possibly an AC Inhibit line into the inverter):
https://www.eaton.com/us/en-us/catalog/machinery-controls/phase-monitoring-relays.html
Also, is the 7.5 kWatt the array? In general, the suggested "minimum" size AC inverter would be:- 7.5 kWatt * 0.77 panel+inverter deratings = 5.775 kWatt output...
-Bill "not a power/utility engineer" B.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
As long as the solar edge are designed to run 3 phase which I do not know. Ask if they can be run in clusters!
Clusters is how Schneider XW and Outback Radian battery based hybrids do this. Schneider is about 7KW 3 phase up to 76KW and Radian is 8KW up to near 100KW. If this is in California both Schneider and Outback are Rule 21 compliant. Below are the IEEE requirements.
I get that you probably do not want a hybrid solution but the cluster method may be helpful, it may not
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I should also add, there are 240 VAC 3 phase (Delta) and 208 VAC 3 phase drops (Wye)... So you may need to confirm what the exact drop your customer has (in our area, office parks are typically 3 phase 208 Wye drops).
And I guessed/assumed that this is a pure Grid Tied system... And not a hybrid/battery based system (backup power for power failure support). If I was wrong, I am sorry.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Might this not fit the bill?
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed