Is this normal?

Apica
Registered Users Posts: 35 ✭✭
Good day, I need some clarification on an observation that has me concerned.
I usually turn off my inverter on Saturday evenings before leaving work to allow my battery bank fully charge on Sundays.
I wired an amazon purchased Baylite Digital Multimeter to the system to give me an idea of my load current and power usage which works really well. On several occasions when I get to work on Monday before turning on the inverter the FM80 indicates that the battery bank is Charged and the Multimeter indicates that there is no load on the system which is ok. However after turning on the inverter all loads are powered by the battery bank only but no current comes in from the PV array. The only way to get the PV array to supply current is to turn off the PV & CC breakers then back on.
Is this behavior normal?
I usually turn off my inverter on Saturday evenings before leaving work to allow my battery bank fully charge on Sundays.
I wired an amazon purchased Baylite Digital Multimeter to the system to give me an idea of my load current and power usage which works really well. On several occasions when I get to work on Monday before turning on the inverter the FM80 indicates that the battery bank is Charged and the Multimeter indicates that there is no load on the system which is ok. However after turning on the inverter all loads are powered by the battery bank only but no current comes in from the PV array. The only way to get the PV array to supply current is to turn off the PV & CC breakers then back on.
Is this behavior normal?
System A
Victron Multiplus II 48V|3000VA Inverter || 4,980 Watts JA Solar Panels || Outback Flexmax 80, Outback Flexmax 60 || 2 EG4 48V 100AH Lifepower 4 Batteries V1 & V2 || Trimetric 2030 || Raspberry Pi running Venus OS.
System B
Victron Multiplus II 24V|3000VA Inverter || 4,160 Watts Intenergy Solar Panels. || Outback Flexmax 80A, Midnite Classic 150 || 2 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Raspberry Pi Running Venus OS.
Victron Multiplus II 48V|3000VA Inverter || 4,980 Watts JA Solar Panels || Outback Flexmax 80, Outback Flexmax 60 || 2 EG4 48V 100AH Lifepower 4 Batteries V1 & V2 || Trimetric 2030 || Raspberry Pi running Venus OS.
System B
Victron Multiplus II 24V|3000VA Inverter || 4,160 Watts Intenergy Solar Panels. || Outback Flexmax 80A, Midnite Classic 150 || 2 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Raspberry Pi Running Venus OS.
Comments
-
Inverter Turned On but all Loads being powered by the battery Bank.
System A
Victron Multiplus II 48V|3000VA Inverter || 4,980 Watts JA Solar Panels || Outback Flexmax 80, Outback Flexmax 60 || 2 EG4 48V 100AH Lifepower 4 Batteries V1 & V2 || Trimetric 2030 || Raspberry Pi running Venus OS.
System B
Victron Multiplus II 24V|3000VA Inverter || 4,160 Watts Intenergy Solar Panels. || Outback Flexmax 80A, Midnite Classic 150 || 2 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Raspberry Pi Running Venus OS. -
System now performing normally after turning off then on PV & CC breakers
System A
Victron Multiplus II 48V|3000VA Inverter || 4,980 Watts JA Solar Panels || Outback Flexmax 80, Outback Flexmax 60 || 2 EG4 48V 100AH Lifepower 4 Batteries V1 & V2 || Trimetric 2030 || Raspberry Pi running Venus OS.
System B
Victron Multiplus II 24V|3000VA Inverter || 4,160 Watts Intenergy Solar Panels. || Outback Flexmax 80A, Midnite Classic 150 || 2 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Raspberry Pi Running Venus OS. -
If I'm reading this right, it's probably (sort of) normal.
With full (lead acid) batteries, the controller should be drawing just enough pv power to hold a float voltage and supply any other loads. By rebooting the controller, you're likely starting a new bulk cycle, in which the controller needs to draw more power to raise battery voltage to absorb voltage. With a full bank, this would happen fairly quickly, but would use whatever current is available to get there.
To see if the system is working normally, maybe try waiting for a few minutes after turning on the inverter. If working normally, voltage should stay at about float voltage, and current should be ~1-2% of bank capacity plus whatever loads are using the inverter.
25.2v seems low for a float voltage to me though. Do you have non-LA (eg lithium) batteries?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
With full (lead acid) batteries, the controller should be drawing just enough pv power to hold a float voltage and supply any other loads.25.2v seems low for a float voltage to me though. Do you have non-LA (eg lithium) batteries?
System A
Victron Multiplus II 48V|3000VA Inverter || 4,980 Watts JA Solar Panels || Outback Flexmax 80, Outback Flexmax 60 || 2 EG4 48V 100AH Lifepower 4 Batteries V1 & V2 || Trimetric 2030 || Raspberry Pi running Venus OS.
System B
Victron Multiplus II 24V|3000VA Inverter || 4,160 Watts Intenergy Solar Panels. || Outback Flexmax 80A, Midnite Classic 150 || 2 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Raspberry Pi Running Venus OS. -
I think they should float at something like 27v - you may want to check battery spec to confirm.. Could float be disabled or set lower in the controller?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Float is set to 27.2V but usually does at 27V due to temp compensation on a regular basis. I guess I'll have to monitor things closely and update.System A
Victron Multiplus II 48V|3000VA Inverter || 4,980 Watts JA Solar Panels || Outback Flexmax 80, Outback Flexmax 60 || 2 EG4 48V 100AH Lifepower 4 Batteries V1 & V2 || Trimetric 2030 || Raspberry Pi running Venus OS.
System B
Victron Multiplus II 24V|3000VA Inverter || 4,160 Watts Intenergy Solar Panels. || Outback Flexmax 80A, Midnite Classic 150 || 2 EG4 24V 200AH Lifepower 4 V1 LifePo4 Battery. || Trimetric 2025 || Midnite E-Panel || Raspberry Pi Running Venus OS.
Categories
- All Categories
- 224 Forum & Website
- 132 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 196 Solar Information links & sources, event announcements
- 894 Solar Product Reviews & Opinions
- 255 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 617 Discussion Forums/Café
- 310 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed