Should I use an Input DC BUS for my FlexMax 80 Charge controllers or keep their input separate
                
                    richardimorse                
                
                    Registered Users Posts: 98 ✭✭                
            
                        
            
                    Hi, I was thinking about the need to use a 4 pole GRDi for the 140V DC input to my 3 FlexMax 80 charge controllers and noticed that the GRDi has separate DC +VE connections one for each FlexMax 80 controller, then I was thinking about using SPD's to protect the controller input (i.e. the other end of the combiner cables).
If I bus the 140V inputs i.e. add the Current, then distribute to my 3 charge controllers via the GRDi then I only need one SPD instead of 3 SPDs which would be required without the bus, the Flexmax has the 80A overload protection setting to ensure each controller doesn't overload.
Then again, if I bus the inputs, if the SPD doesn't work I will for sure blow up all three charge controllers and be left with generator power only.
So maybe it is better to either:
1) Rely on the combiner SPD and GFDi for protection keeping controller inputs separate
2) Install 6 SPDs in total at both ends of the power cable 3 in the combiners and 3 for the charge controllers (sounds expensive)
                
                        
        
        
      If I bus the 140V inputs i.e. add the Current, then distribute to my 3 charge controllers via the GRDi then I only need one SPD instead of 3 SPDs which would be required without the bus, the Flexmax has the 80A overload protection setting to ensure each controller doesn't overload.
Then again, if I bus the inputs, if the SPD doesn't work I will for sure blow up all three charge controllers and be left with generator power only.
So maybe it is better to either:
1) Rely on the combiner SPD and GFDi for protection keeping controller inputs separate
2) Install 6 SPDs in total at both ends of the power cable 3 in the combiners and 3 for the charge controllers (sounds expensive)
Comments
- 
            Putting the inputs to the controllers on a common bus doesn't seem like a good idea to me. Among other things, (assuming CCs are not really underpanelled) you could end up with a single controller having to handle 3x overpanelling. They can generally limit overpanel current to a point, but that may really be pushing it.
I'd just do the SPDs near the building entrance, presumably at the controllers.Off-grid.
Main system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter - 
            MPPT controllers do not like to share a single solar array... The MPPT function assumes that a single controller has complete control of a single array. The controller "finds" Pmax-power by varying the current it draws from the solar panels while monitoring panel voltage... Then "solves" the equation for Pmp=Vmp*Imp. And then adjusts current drawn from panels to hold Voltage at ~Vmp. (newer MPPT controllers don't "sweep the array" every 5-15 minutes like older controllers--But this explanation is close enough for now).
When you have multiple MPPT controllers on a single array, they will confuse each other as each one tries to "sweep" the array.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset 
Categories
- All Categories
 - 232 Forum & Website
 - 140 Solar Forum News and Announcements
 - 1.4K Solar News, Reviews, & Product Announcements
 - 199 Solar Information links & sources, event announcements
 - 899 Solar Product Reviews & Opinions
 - 256 Solar Skeptics, Hype, & Scams Corner
 - 22.5K Solar Electric Power, Wind Power & Balance of System
 - 3.5K General Solar Power Topics
 - 6.7K Solar Beginners Corner
 - 1K PV Installers Forum - NEC, Wiring, Installation
 - 2.1K Advanced Solar Electric Technical Forum
 - 5.6K Off Grid Solar & Battery Systems
 - 428 Caravan, Recreational Vehicle, and Marine Power Systems
 - 1.1K Grid Tie and Grid Interactive Systems
 - 656 Solar Water Pumping
 - 816 Wind Power Generation
 - 624 Energy Use & Conservation
 - 620 Discussion Forums/Café
 - 313 In the Weeds--Member's Choice
 - 75 Construction
 - 124 New Battery Technologies
 - 108 Old Battery Tech Discussions
 - 3.8K Solar News - Automatic Feed
 - 3.8K Solar Energy News RSS Feed