Running a step down transformer off of an off grid 120v inverter?
imcloud
Registered Users Posts: 25 ✭✭
I need to run a 120vac in 5a 30vac out step down transformer, can I do that with my 120 v system, I have a 1000 watt 12v-120 v inverter, 2 100ah batteries, and a 200 ish watt solar panel. but the system doesnt pull 30vac 5 a all the time, more like 1.5 to 2 a constant...
Comments
-
Yes, it can be done. The big question is how much energy (Watts*Hours per day) your subsystem uses (and possibly look at running it from 12 or 24 VDC--If practicable).
Using a Kill-a-Watt Hour type meter will help you figure out how much energy per day your subsystem will take:
https://www.solar-electric.com/kiacpomome.html
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I was told by the company that sells the inverters that an inverter wont run a step down transformer? This is for an irrigation control. I used inverters before and they make 120v 60hz and never had a problem running anything, including pcs and laptops so I cant understand why they would say it wouldnt work?
-
Sounds like it may be a modified sine wave (MSW) inverter, which would likely play havoc with any attempt to go through a step down transformer.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case.
-
The waveform could well be an issue, but would likely depend on the transformer circuitry. For example, a laptop steps 120v down to 5v, 3v, etc internally, but the ac is rectified to dc as part of the process.
A square or ragged MSW supply may saturate a transformer core designed for PSW only?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
what type would you guys recommend?
-
Something like a Morningstar 300w sine wave inverter (sold by our hosts).
There may be other ways to do it, but based on what you've told us, that's what I would do.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
will 300w be enough? the transformer in the controller says 24vac 4.2a and 7vac 3.2a max...
-
imcloud said:will 300w be enough? the transformer in the controller says 24vac 4.2a and 7vac 3.2a max...
I run a 24v sprinkler timer off a transformer just fine, last 5 years, pure sine inverter
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
its 1 transformer with 2 windings, so there are 4 low voltage wires coming out and going to the control.. Hey I want to thank everyone for responding thus far, thanks a lot for the help guys I really do appreciate it, its a lot of money to invest on a whim and I will feeel a lot better about it with some experienced know how behind my purchase...
-
If this transformer with the voltage / current ratings you've quoted is the only thing you will run off the inverter, 300W will be more than enough.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case.
-
24vac 4.2a and 7vac 3.2a24 x 4.2 = 100.8 watts
7 x 3.2 = 22.4
123.2 watts total, well within the Suresine 300 rating
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Those numbers are likely outputs - 120v input would be somewhat higher, but should still be well within limits even with really inefficient transformer. Unlike some cheap inverters I've used, the MS will easily do rated output, and handles surges to about double rated.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
the input says 120v 5a
-
sorry correction its 120v 2.8a
-
I can get a decent deal on a samlex pst 600 12 will that be a decent option
-
The Samlex is a good inverter for your needs, much better than the cheap unknown offerings, it at least is UL listed, and has a real warranty.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I am going to try that inverter and see if that will work our for me... I will do 2-100w panels, with a charge controller, 2 100ah batteries, and the samlex inverter... Is there anything else I will need? I was told that the panels need to be mounted at 18* pointing south, is that accurate?
-
Really need to understand your loads... And remember that your AC inverter is a load itself--They can draw ~6 watts to 20-40+ Watts for the larger inverters.
For example, 200 Watts of panels
http://www.solarelectricityhandbook.com/solar-irradiance.htmlHartford
Measured in kWh/m2/day onto a solar panel set at a 63° angle from vertical or 27 degrees from horizontal:
Average Solar Insolation figures
(Optimal summer settings)
So, for September, you would get around:Jan Feb Mar Apr May Jun 2.91
3.73
4.50
4.80
5.20
5.53
Jul Aug Sep Oct Nov Dec 5.42
5.16
4.71
3.92
2.88
2.61
- 200 Watts * 0.52 system eff * 4.71 hours of sun (average Sept sun) = 490 Watt*Hours per day
- 490 WH per day / 24 hours = 20 Watts average power
200 AH of storage batteries, for long term/off grid usage, suggest 50% max discharge and 2 days of storage:- 200 AH * 12 volts * 0.85 AC inverter eff * 1/2 days storage * 0.50 max discharge = 510 WH per day
- 510 WH per day / 24 hours = 21 Watt average AC load
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
imcloud said:I will do 2-100w panels, with a charge controller, 2 100ah batteries, and the samlex inverter... Is there anything else I will need?
DoD= depth of discharge= amount removed from that battery SoC= state of charge= amount remaining in that batterySo, 0% DoD= 100% SoC, 25% DoD= 75% SoC, 50% DoD= 50% SoC, 75% DoD= 25% SoC, 100% DoD= 0% SoCA/C= air conditioning AC= alternating current (what comes from the outlets in your home) DC= direct current (what batteries & solar panels use) -
wow Bill, thanks, OK so if I understand that correctly, I will have around 500 watts per day and the converter itself would use 150 of them leaving me with around 350watts per day... So I really would need to know how many watts per day my control uses total while irrigating and sitting idle...
Am I understanding that correctly? The max the control can pull is 2a at 120v so that is 240w ? would that be 240w so with that math I would need 5760 watts just to run the control? In reality the control is going to be running at about 1/4 of its capability and only for around 5 hours a day. But I wont know what that costs in Watts until its setup and running....
-
imcloud said:wow Bill, thanks, OK so if I understand that correctly, I will have around 500 watts per day and the converter itself would use 150 of them leaving me with around 350watts per day... So I really would need to know how many watts per day my control uses total while irrigating and sitting idle...
Am I understanding that correctly? The max the control can pull is 2a at 120v so that is 240w ? would that be 240w so with that math I would need 5760 watts just to run the control? In reality the control is going to be running at about 1/4 of its capability and only for around 5 hours a day. But I wont know what that costs in Watts until its setup and running....
I think I still don't understand what loads you are running on this transformer. However, if the loads connected to the transformer are off, the transformer will not be drawing much power on the primary side. I don't know what "1/4 of its capability" means. As Bill said, you need to better describe what you are doing.Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case. -
this https://www.hunterindustries.com/sites/default/files/OM_ACC_EM.pdf
is running 20 of these for 15m each a day so total is 1 running for every 15m for 5 hours... just in the summer, not when its raining obviously... the 151's...
https://www.hunterindustries.com/sites/default/files/br_pgv_1in.pdf
-
On first glance I can't tell what the nominal power consumption of the controller is. It says what the max power is (1.2A at 120VAC), but I'm sure it is way less than that. The valves you are pointing to clearly say they have an inrush current of 350mA (which will be only for a fraction of a second when the valve is first turned on), and 190mA holding (when the valve is open). If you really only have one valve open at a time, all the valves will be consuming nominally 190mA at 24VAC, which is less than 5W. I'm guessing that the controller will consume way less than the spec, since it looks like you can have it run all the valves at once. Anyway, I'd bet you are using less than 20W total for the 5 hours, and that only totals 100 watt hours.
Is this system in use now, but you just want to move it to solar? If so you can actually measure how much 120VAC current it is consuming.
Off-grid cabin: 6 x Canadian Solar CSK-280M PV panels, Schneider XW-MPPT60-150 Charge Controller, Schneider CSW4024 Inverter/Charger, Schneider SCP, 8S (25.6V), 230Ah Eve LiFePO4 battery in a custom insulated and heated case. -
so the controls specs are -
- Transformer Input: 120/230 VAC, 50/60 Hz, 2A max at 120V, 1A max at 230V
- Max AC Current Draw: 120 VAC, 2 Amps; 230 VAC, 1 Amp (max computed with all programs running and optional accessories installed)
- Transformer output: 24 VAC, 4A, at 120 VAC
- Decoder Line (path) output: 34 V peak-to-peak
- Decoder Power draw: 40 mA per active output
And the valves, which will there are 20 of, and the program is going to be simple 20 valves, on 1 at a time for 15 minutes each only for 1 cycle each.. so 20 starts with 5 hours of run time, the valve specs are...
• 24 VAC solenoid – 350 mA inrush, 190 mA holding, 60 Hz (North America) – 370 mA inrush, 210 mA holding, 50 Hz (most international locations)...
thats the only thing it will run... -
tomorrow I am going to go to a facility that has one of these controllers running, Im gonna put a kill a watt meter on it and see what it is pulling when at idle, when opening a valve, and when running...
-
I am also thinking about putting a timer on the system if I have to, what if I cut the stand by losses by shutting off the inverter for the off times? the controllers manual says ----
Power Failures ........................................................................ The ACC’s real time clock is independent of external power or the 9 VDC battery, and will keep time during a power failure of virtually any length. When external power is restored, the ACC will still have the correct time and will be ready to irrigate. Quick Start................................................................................ A Power Outage message will be stored in the Alarm Log, with time of the outage. Another log is stored when power is restored.
so I am thinking if I cut the power and then restart it before and after the 5 hr cycle my off times will not draw any energy from the cells...
-
using something like this https://www.amazon.com/MISOL-Controller-display-program-programmable/dp/B0090MTLFO/ref=sr_1_4?ie=UTF8&qid=1504706174&sr=8-4&keywords=12v+timer
unless that may cause an issue with the inverter needing to be started before the load? in which case the inverter will have to run all the time and I can shut the clock off with a 120v timer switch, depending on the losses.. or 2 timers, 1 12v that turns on a few minutes before the 120v...
-
Just to be clear: 1x Controller and 20x valves, 1x valve at a time?
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
yes that is correct and each valve for 15minutes 1 time a day
-
I would suggest sizing the system to run the loads (transformer+inverter) 24x7 (don't cycle the inverter and use the 9 volt backup battery). Keep the system "simple". (for example, can somebody program the unit when on 9 volt power, or do they have to turn on the AC power, etc.).
Also, I did not size the system for winter operation (less sun). If you shut down the system for 3 months of winter--Then sizing the array/battery bank for when you have more sun will keep the system smaller/less expensive.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed