5kVA48V Hybrid Inverter

Options
Jacq721
Jacq721 Registered Users Posts: 1
I have installed a few of these Systems. The System is connected to 10 x 320W Modules with 8 x 180Ah12V AGM Batteries. The Inverter is also connected to the Utility. The System will give power to the Loads and when the Batteries are at 50%, it pulls in the Utility. At this stage the lights, fridge etc. dips. Why does the Loads dip as everything gets its power through the Inverter all the time. It's only the Supply ( Solar, Battery and Utility) that changes? 

Comments

  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Options
    what does the manual say about ''Transfer Speed"? mu inverter does so in 14mili-seconds or so...
     