6/3 romex no ground wire sub panel connection?
Skip
Registered Users Posts: 18 ✭✭
I am confused about hooking up my PVPowered 3500 Grid Tie Inverter to the sub panel in my garage. My home was built in 1975 and the sub panel is wired to the Main panel with 6/3 romex, no-ground wire, at 240vac with neutral wired to grounding block at main panel. My question is, will I be allowed to wire the GT Inverter to this sub panel for my ac connection to feed the solar power to the main panel? I will be grounding the solar panels to the inverter and then to a ground rod at the inverter location. The sub panel ONLY feeds a 240vac outlet in the garage, NO 120 vac connections from the sub panel and the 240vac outlet will be abandoned before the system is charged. The sub panel neutral is connected to an isolated neutral block in the sub panel, So my only ground will be to the solar panels connected to the DC ground on the inverter and inverter to the ground rod. I am hoping the the grounded neutral at the main panel can be disconnect from the neutral grounded bus bar and connected only to the equipment ground bar at the main panel and will be sufficient for grounding the AC side of the inverter. So the short of it all is: can the white neutral wire be used for the EGC wire that is only connected to the ground buss bar at both the sub panel and the main panel instead of using a solid ground wire? Any info will be greatly appreciated, and thanks for looking.
24 - 250 watt poly panels, 6000 watt SolarCity H6 Hybrid Grid Tied Inverter Mohave County Az.
Comments
-
I found the answer I was looking for so I thought I'd share it do to the lack of replies:
NATIONAL ELECTRICAL CODE
ARTICLE 250
GROUNDING AND BONDING
250.118 Types of Equipment Grounding
Conductors.
The equipment grounding conductor
run with or enclosing the circuit conductors shall be
one or more or a combination of the following:
(1)
A copper, aluminum, or copper clad aluminum
conductor. This conductor shall be solid or
stranded; insulated, covered, or bare; and in
the form of a wire or a busbar of any shape
24 - 250 watt poly panels, 6000 watt SolarCity H6 Hybrid Grid Tied Inverter Mohave County Az. -
Sorry, I missed your post...
I am not a code guy--But, as I recall, you can use the conduit as safety ground for residential. But for commercial, you must pull a green wire ground (and perhaps, new residential requires a green wire ground too with new NEC?).
If you do not need the neutral in your sub panel, yes, you can lift the white wire at both ends, "phase tape" both ends with green electrical tape, and tie it to the safety ground in the main panel and to the local panel ground in your garage. Note that the subpanel may have a moveable "bonding" screw in the isolated neutral bus so you can ground the bus to the panel box.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I forgot to add--Your green wire/safety ground for the solar array (and inverter?)--Lighting wise, the array ground should go down the outside of the building to a ground rod next to the foundation.
For electrical safety (code wise), you should have a ground wire from the remote ground rod/array ground tied back to your main ground rod (and/or cold water pipe ground). You want the two grounds tied together so you do not have a electrocution risk. You want a solid copper connection between the two electrical grounds (trip breaker if there is a short circuit). Ground Rods can have as much as 25 Ohms to earth ground resistance. That is not enough to trip even a 15 amp breaker at 120 VAC:- V=I*R
- I = V/R = 120 VAC / 25 Ohms - 4.8 Amps AC
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Hi Bill, I want to thank you for the info, I am having a licensed solar installer install the system, I just needed to know that the existing wiring would work for the sub panel, my city puts homeowner solar installers through hell
24 - 250 watt poly panels, 6000 watt SolarCity H6 Hybrid Grid Tied Inverter Mohave County Az.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed