HOW TO DESIGN OFF GRID SOLAR SYSTEM WITH 4500WATTHOUR daily load
JAYMIN
Registered Users Posts: 22 ✭✭
hello dear friends
kindly help me the design of off grid solar system with 4500 watt hour daily load.
Regards
Jaymin Bavishiya
kindly help me the design of off grid solar system with 4500 watt hour daily load.
Regards
Jaymin Bavishiya
Comments
-
JAYMIN said:kindly help me the design of off grid solar system with 4500 watt hour daily load.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Also, how many people?
Does the system need to grow later?
How do you get water?
Do you need to cool the living space?
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
dear sir i have a daily load 4500kwh , days of autonomy : 2 days , no i do not want to grow system in later or sooner , i am living in warm place average 5.5 sunshine hour/day in a year
-
A quick off grid system design, using our standard rules of thumbs as a starting point. Assume flooded cell lead acid batteries, 50% maximum discharge (for longer battery life):
- 4,500 WH per day * 1/0.85 AC inverter eff * 2 days of storage * 1/0.50 maximum discharge * 1/48 volt battery bank = 441 AH @ 48 volt battery bank
Next, size of solar array, two calculations needed. One based on size of battery bank. The second based on hours of sun per day and your loads.
First size of battery bank--5% to 13% rate of charge is typical recommendation. 5% can be OK for weekend/sunny season usage. 10%+ is recommended for full time off grid usage (9+ months a year):- 441 AH * 59 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 1,690 Watt array minimum
- 441 AH * 59 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 3,379 Watt array nominal
- 441 AH * 59 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 4,393 Watt array "cost effective" maximum
http://solarelectricityhandbook.com/solar-irradiance.htmlSurat
Measured in kWh/m2/day onto a solar panel set at a 69° angle from vertical:
Average Solar Insolation figures
(For best year-round performance)
Toss bottom three months (assume use genset/less power), December has 5.18 hours of sun (on average) per day:Jan Feb Mar Apr May Jun 5.57
6.16
6.54
6.35
6.02
5.38
Jul Aug Sep Oct Nov Dec 4.12
4.15
5.12
5.81
5.70
5.18
- 4,500 WH per day * 1/0.52 off grid system eff * 1/5.18 hours of sun per day = 1,671 Watt array minimum (break even for December)
- 1,671 Watt array * 1/0.75 derating = 2,228 Watt array (75% of rated power)
- 1,671 Watt array * 1/0.65 derating = 2,571 Watt array (65% of rated power)
- 3,379 Watt array * 0.52 off grid system eff * 5.18 hours "average" December day = 9,102 Watt*Hours per day
A 441 AH @ 48 volt battery bank will support a useful maximum of ~4.5 kWatt AC inverter nicely (technically 1kW per 100 AH @ 48 volts or 4.41 kW inverter) and a ~4,410 Watt array maximum (too much charging current for battery bank can cause overheating of battery bank).
The above is a rules of thumbs design for a full time off grid home/cabin. If your needs are different (say running an off grid business with nearly 100% of loads during the day)--Then may need to adjust array size (and possibly could use a smaller AH battery bank). If you have large (for example) well pump with high starting surge current--That could make other design changes.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:A quick off grid system design, using our standard rules of thumbs as a starting point. Assume flooded cell lead acid batteries, 50% maximum discharge (for longer battery life):
- 4,500 WH per day * 1/0.85 AC inverter eff * 2 days of storage * 1/0.50 maximum discharge * 1/48 volt battery bank = 441 AH @ 48 volt battery bank
Next, size of solar array, two calculations needed. One based on size of battery bank. The second based on hours of sun per day and your loads.
First size of battery bank--5% to 13% rate of charge is typical recommendation. 5% can be OK for weekend/sunny season usage. 10%+ is recommended for full time off grid usage (9+ months a year):- 441 AH * 59 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 1,690 Watt array minimum
- 441 AH * 59 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 3,379 Watt array nominal
- 441 AH * 59 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 4,393 Watt array "cost effective" maximum
http://solarelectricityhandbook.com/solar-irradiance.htmlSurat
Measured in kWh/m2/day onto a solar panel set at a 69° angle from vertical:
Average Solar Insolation figures
(For best year-round performance)
Toss bottom three months (assume use genset/less power), December has 5.18 hours of sun (on average) per day:Jan Feb Mar Apr May Jun 5.57
6.16
6.54
6.35
6.02
5.38
Jul Aug Sep Oct Nov Dec 4.12
4.15
5.12
5.81
5.70
5.18
- 4,500 WH per day * 1/0.52 off grid system eff * 1/5.18 hours of sun per day = 1,671 Watt array minimum (break even for December)
- 1,671 Watt array * 1/0.75 derating = 2,228 Watt array (75% of rated power)
- 1,671 Watt array * 1/0.65 derating = 2,571 Watt array (65% of rated power)
- 3,379 Watt array * 0.52 off grid system eff * 5.18 hours "average" December day = 9,102 Watt*Hours per day
A 441 AH @ 48 volt battery bank will support a useful maximum of ~4.5 kWatt AC inverter nicely (technically 1kW per 100 AH @ 48 volts or 4.41 kW inverter) and a ~4,410 Watt array maximum (too much charging current for battery bank can cause overheating of battery bank).
The above is a rules of thumbs design for a full time off grid home/cabin. If your needs are different (say running an off grid business with nearly 100% of loads during the day)--Then may need to adjust array size (and possibly could use a smaller AH battery bank). If you have large (for example) well pump with high starting surge current--That could make other design changes.
-Bill -
The efficiencies (roughly) work out as:
81% of rated actual solar output power at nominal operating temperatures (typical summer day--Vmp falls as solar cells get hot)
95% for charge controller
80% typical for flooded cell battery
90% typical for AGM/Sealed battery
85% typical for DC to AC inverter- 0.81 panel derating * 0.95 GT inverter = 0.77 typical efficiency (from solar panel STD ratings to useful AC power)
- 0.81 panel derating * 0.95 charge controller eff * 0.80 flooded cell batt * 0.85 AC inverter = 0.52 typical end to end off grid AC efficiency
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed