How to connect 18-150watt panel and six 75 watt panel?
JAYMIN
Registered Users Posts: 22 ✭✭
I have total 24 BIPV panel out of that 18 panel has power 150 watt and 6 panel has power 75 WATT can i make two string in each string have 9-150watt panel and 6- 75 watt panel.? voltage will reduce in each string due to 75 watt panel?
Comments
-
We need to know the specs on each of the panels. --vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
vtmaps said:We need to know the specs on each of the panels. --vtMaps
75 watt panel : Size : 1125*982 mm , cell : 24 , Voc : 14.5v , Vmp : 11.75v , Isc : 3.5A , Imp: 2.19A -
The number for the 75 watt panel are not correct. Vmp X Imp = watts. 11.75 volts X 2.19 amps = 25.7 watts.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
vtmaps said:The number for the 75 watt panel are not correct. Vmp X Imp = watts. 11.75 volts X 2.19 amps = 25.7 watts.
--vtMaps -
What battery bank voltage are you trying to run? (12/24/48 volt or something else)?
What solar charge controller are you (trying) to run? Is it an MPPT (maximum power point tracking) or PWM (Plus width modulation)?
Those panels do not map well to 12 or 24 volt battery banks (typically Vmp~18 volts for 12 volt bank and Vmp~36 volts for a 24 volt battery bank). With MPPT type charge controller, you can go >>Vmp nominal for your battery banks (MPPT controllers will take "high voltage/low current" and efficiently down convert to "low voltage/high current" needed to charge the battery bank (within capabilities of the MPPT controller's ratings).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:What battery bank voltage are you trying to run? (12/24/48 volt or something else)?
What solar charge controller are you (trying) to run? Is it an MPPT (maximum power point tracking) or PWM (Plus width modulation)?
Those panels do not map well to 12 or 24 volt battery banks (typically Vmp~18 volts for 12 volt bank and Vmp~36 volts for a 24 volt battery bank). With MPPT type charge controller, you can go >>Vmp nominal for your battery banks (MPPT controllers will take "high voltage/low current" and efficiently down convert to "low voltage/high current" needed to charge the battery bank (within capabilities of the MPPT controller's ratings).
-Bill -
Jaymin,
What are the input requirements of your GT Inverter (voltage range, maximum current, watts, etc.)?
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
min. start voltage : 110V , ax. input voltage : 600V , num of MPPT : 1 , MPPT VOLTAGE RANGE : 100-520V , MAX. INPUT CURRENT : 11A
-
It looks like you would put 9x 150 Watt panels in series, 2x parallel strings.150 watt panel : size : 1125*982 mm , cell : 48 , Voc : 28.7v , Vmp : 23.5v , Isc : 7.02A , Imp: 6.38A
75 watt panel : Size : 1125*982 mm , cell : 24 , Voc : 14.5v , Vmp : 11.75v , Isc : xxxA Imp: 6.38AThe ratings for the panels still do not look correct (the 75 watt panels especially). Anyway, your array would have:
- Vmp-array = 23.5 volts * 9 panels in series = 211.5 volts nominal (standard temperature)
- Voc-array = 28.7 volts * 9 panels in series = 258.3 volts (standard temperature)
- Imp-array = 6.38 Amps * 2 parallel strings = 12.76 amps nominal
- 211.5 volts * 11 amps max input current = 2,321 Watt DC array (standard test conditions)
- 2,321 Watts * 0.77 panel and controller deratings = 1,787 Watt AC output (typical peak in warm/sunny weather)
- 211.5 volts + (3 * 11.75 volts Vmp) = 246.75 volts Vmp-array (9+3 panels)
- 246.75 volts Vmp-array * 11 Amps * 0.77 panel+controller derating = 2,090 Watt typical peak output
Note: fixed calculator errors above.
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - Vmp-array = 23.5 volts * 9 panels in series = 211.5 volts nominal (standard temperature)
-
BB. said:It looks like you would put 9x 150 Watt panels in series, 2x parallel strings.150 watt panel : size : 1125*982 mm , cell : 48 , Voc : 28.7v , Vmp : 23.5v , Isc : 7.02A , Imp: 6.38A
75 watt panel : Size : 1125*982 mm , cell : 24 , Voc : 14.5v , Vmp : 11.75v , Isc : xxxA Imp: 6.38AThe ratings for the panels still do not look correct (the 75 watt panels especially). Anyway, your array would have:
- Vmp-array = 23.5 volts * 9 panels in series = 211.5 volts nominal (standard temperature)
- Voc-array = 28.7 volts * 9 panels in series = 258.3 volts (standard temperature)
- Imp-array = 6.38 Amps * 2 parallel strings = 12.76 amps nominal
- 211.5 volts * 11 amps max input current = 2,321 Watt DC array (standard test conditions)
- 2,321 Watts * 0.77 panel and controller deratings = 1,787 Watt AC output (typical peak in warm/sunny weather)
- 317.25 volts Vmp-array * 11 Amps * 0.77 panel+controller derating = 2,687 typical peak output
- Vmp-array = 23.5 volts * 9 panels in series = 211.5 volts nominal (standard temperature)
-
Jaymin,
Oops... Made a calculator error (did the 3x on the added panels twice)--Fixed original post in bold.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:Jaymin,
Oops... Made a calculator error (did the 3x on the added panels twice)--Fixed original post in bold.
-Bill
BUT TOTAL POWER SHOULD BE 150watt*18panel + 75*6 = 3150WATT
AND ONCE AGAIN THANKS BILL
-
Jaymin,
First, your GT inverter has an 11 Amp maximum input current (vs the ~2x 7.02 amps of each strings Imp). so you lost ~3 amps there.
And next Vmp is temperature dependent. Solar panels are typically rated under mfg. test conditions (flash testing--"full sun" for a few seconds "sun" lamp, cell temperature ~25C). In real life, solar panels get hot in full sun and Vmp fall--Roughly to ~81% of "std" Vmp on a nice spring day (very hot weather, Vmp can fall more. In very cold climates, below freezing, Vmp can be higher than STD test condition rating).
lastly, roughly 95% efficiency of the GT inverter...- Total "derating" 0.81 panel temp * 0.95 GT inverter efficiency = 0.77 = 77% "typical power output" of "panel STD Rating (typical maximum on average spring day at noon time).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:Jaymin,
First, your GT inverter has an 11 Amp maximum input current (vs the ~2x 7.02 amps of each strings Imp). so you lost ~3 amps there.
And next Vmp is temperature dependent. Solar panels are typically rated under mfg. test conditions (flash testing--"full sun" for a few seconds "sun" lamp, cell temperature ~25C). In real life, solar panels get hot in full sun and Vmp fall--Roughly to ~81% of "std" Vmp on a nice spring day (very hot weather, Vmp can fall more. In very cold climates, below freezing, Vmp can be higher than STD test condition rating).
lastly, roughly 95% efficiency of the GT inverter...- Total "derating" 0.81 panel temp * 0.95 GT inverter efficiency = 0.77 = 77% "typical power output" of "panel STD Rating (typical maximum on average spring day at noon time).
-Bill -
My pleasure Jaymin. If I was not awake, I would not be reading the forum.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed