Fuse sizing on solar system
wingnutter
Registered Users Posts: 12 ✭
HI folks,
Can anyone help me I am a bit confused about the size of fuse I should be using between my batteries and inverter?
I have 4 x 535 amp 6 volt batteries ( 24 V) and I am about to hook them up to a Studer C 2600 inverter can anyone explain how I can calulate the fuse size I need?
Also can I use a normal VAC fuse for this?
Thanks in advance.
David
Can anyone help me I am a bit confused about the size of fuse I should be using between my batteries and inverter?
I have 4 x 535 amp 6 volt batteries ( 24 V) and I am about to hook them up to a Studer C 2600 inverter can anyone explain how I can calulate the fuse size I need?
Also can I use a normal VAC fuse for this?
Thanks in advance.
David
Comments
-
Re: Fuse sizing on solar system
If you don't have the Inverter's manual, you should be OK with:- Vmin=minimum voltage inverter will run out=21 volts assumed
- Eff=Inverter's efficiency at maximum load=85% estimated
- Pinv=Maximum Inverter Power Output=2,600 watts? (can use max needed load instead)
- Derating=Wiring derating (bundles, conduit, hot temperatures)=assume 80% max current of branch rating or 1.25x max load current from NEC
Branch Circuit/Min fuse rating = 146 amps * 1.25 = 183 amps min wire/breaker/fuse
Round up to next standard wire rating/fuse rating... (again, if you only plan on a 1,000 watt load maximum, you can back down on the fuse/wire ratings to the lower load). You don't want to run the fuses/breakers at 100% load--will will get a lot of nuisance tripping (Outback sells breakers that are supposed to be rated at 100% load--so they may be an exception).
Note, AC current is easier to interrupt vs DC. Fuses, Switches, etc. are actually larger to handle DC interrupt current vs the same rating (and higher voltages) of AC circuits.
Lastly, with fuses and breakers, there is the Maximum Interrupt current... In theory, the maximum interrupt current rating should be larger than the current you will get with a dead short on your battery bank... However, large battery banks can supply tremendous amount of energy. Normally, shorts are not "dead shorts" but failures in wiring or equipment and the fuses/breakers (proper working voltage and DC rated) will work fine.
You can look through here for a selection of fuses/breakers that may meet your needs.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed