Power Rating of PV Array
In the KU265 datasheet, I see three power rating numbers:
There is Pmax, under STC section; there are another two, Pmax and PTC, under NOCT section.
I think I understand the first and the last, but what about the Pmax in the NOCT section? How is this number obtained and should it be used in determining the number of panels or should PTC be used?
Not sure if I can attached the datasheet successfully, but here is link just in case http://www.kyocerasolar.com/assets/001/5740.pdf
Regards
Peter
Comments
-
Hi Peter,
Personally, I would not use PTC (believe that this used to be referred to Pacific Test Conditions). Many PVs seem to not have this rating these days.
This was stolen from the following document:
http://www.gosolarcalifornia.ca.gov/equipment/pv_modules.php" ... PTC are 1,000 Watts per square meter solar irradiance, 20 degrees C air temperature, and wind speed of 1 meter per second at 10 meters above ground level. PV manufacturers use Standard Test Conditions, or STC, to rate their PV products. STC are 1,000 Watts per square meter solar irradiance, 25 degrees C cell temperature, air mass equal to 1.5, and ASTM G173-03 standard spectrum. The PTC rating, which is lower than the STC rating, is generally recognized as a more realistic measure of PV output because the test conditions better reflect "real-world" solar and climatic conditions, compared to the STC rating. All ratings in the list are DC (direct current) watts. ... "
NOCT Ratings are much more meaningful, so would use those to estimate approximate PV module output.
Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
When you are designing a system use the STC numbers in the formulas that calculate the minimum size of your cables and circuit breakers. In the winter I occasionally achieve STC power levels for sustained periods of time.... my cables and breakers are sized for that.
When you are designing a system use the NOCT numbers in the formulas that determine the size of your battery (off grid) or the amount of energy that you will produce.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Hi Vic,
Thank you for your comment!
What is confusing is that in the datasheet, both Pmax and PTC are listed under the same NOCT condition, it makes me wonder which one should be used. Over/under design aside, I want to understand the story behind the Pmax number. Kyocera must have a reason to put both two numbers there. The data sheet is not much help, it would be a lot better with some graphs/explanation in there.
Regards
Peter -
Hi VtMaps,
Thank you! and Yes, agree with you. The worst condition should be considered for each component of the entire system.
Regards
Peter -
PZhou said:Hi Vic,
Thank you for your comment!
What is confusing is that in the datasheet, both Pmax and PTC are listed under the same NOCT condition, it makes me wonder which one should be used. Over/under design aside, I want to understand the story behind the Pmax number. Kyocera must have a reason to put both two numbers there. The data sheet is not much help, it would be a lot better with some graphs/explanation in there.
Regards
PeterHi Peter,
In my opinion, the PTC rating is essentially useless. In the OLD days, IIRC, a PTC Rating was required for any PV modules that were installed in California, in order to qualify for the CA Grid-Tied PV system Rebates.
Believe that this rating gave way to NOCT. Even NOCT can be a bit of an optimistic rating, as it is specified at 20 degree C Ambient temperature, and 1.5 MPS air motion.
Frequently, many of those here, multiply the STC Pmax rating by 0.77 for most systems, and by perhaps 0.80 for systems at higher altitudes, in order to approximate PV typical PV Production.
If you use a PV String Design Tool from the manufacturer of your Grid Tie (GT) inverter, for from the manufacturer of any CCs that you plan to use, you can find a nominally-ideal string configuration for your system and its environment, and determine the approximate PV production with varying conditions.
That Kyocera Data Sheet that you linked to, has at least one error, IMO -- the Parent part number for that PV module series seems to be missing one digit in the model number, a leading number 2, in front of the 60 (reads KU-60) in the graphics at the top. Kyo seems to be one of the few companies that still shows PTC ratings, and I do agree that the PTC rating does not belong in with the NOCT ratings, without a note that PTC is rated under different Cell temperature than is NOCT.
I would forget about PTC, it is a hold-over from times long-past.
FWIW, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Thank you Vic for the thorough explanation!
Regards
Peter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed