Studer - DC and AC voltage measurement accuracy
Ram
Registered Users Posts: 11 ✭✭
Dear friends,
I recently bought and installed a Swiss-made Studer grid-tie system. XTM2600 inverter and Variotrack 65 charger with a RCC-02 remote. To my surprise I find that the battery voltage readings by the Variotrack and the XTM (as shown on the RCC) differ by 0.4V for a 48 volt system which seems to be a fairly large discrepancy. The inaccuracy is not just the display - it is also in the data log. (Readings were taken at night when Variotrack current was zero and the battery draw was also zero to eliminate cable losses). I also find that the AC-In voltage reading is about 5 volts higher than my Class 1 energy meter at 230V - an error of 2%. The Taiwan-made Axpert inverter manual says DC voltage accuracy is +/- 0.3% so I am left wondering why a Swiss-made product cannot do better. Any observations from other Studer owners (there are a few on this forum I believe) or users of other reputed systems on whether such inaccuracy is considered "normal"?
Best - Ram
Bangalore, India
I recently bought and installed a Swiss-made Studer grid-tie system. XTM2600 inverter and Variotrack 65 charger with a RCC-02 remote. To my surprise I find that the battery voltage readings by the Variotrack and the XTM (as shown on the RCC) differ by 0.4V for a 48 volt system which seems to be a fairly large discrepancy. The inaccuracy is not just the display - it is also in the data log. (Readings were taken at night when Variotrack current was zero and the battery draw was also zero to eliminate cable losses). I also find that the AC-In voltage reading is about 5 volts higher than my Class 1 energy meter at 230V - an error of 2%. The Taiwan-made Axpert inverter manual says DC voltage accuracy is +/- 0.3% so I am left wondering why a Swiss-made product cannot do better. Any observations from other Studer owners (there are a few on this forum I believe) or users of other reputed systems on whether such inaccuracy is considered "normal"?
Best - Ram
Bangalore, India
Comments
-
+/- 0.3% ...
48 volts x 1.003 = 48.144 volts
48 volts x 0.997 = 47.856 volts
48.144 - 47.856 = 0.288 volt difference, round up to 0.3 volts difference.
You show a 0.4 volt difference, which not significantly worse.
Is there any voltage drop caused by connections or cables?
Maintaining +/-0.3% for more than 1 year is not easy, without re-calibration.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed