Transformerless inverter grounding
lamagra
Registered Users Posts: 8 ✭
I would like to confirm the idea that, for transformerless inverters, the PV grounding system's point of return (i.e. where the neutral and ground are connected) should be in the same panel where the PV system is connected. In other words, connecting the PV grounding system to the existing grounding system, if the PV system is connected to a subpanel for instance, could lead to tripping of RCDs upstream of the inverter, up to the main panel.
Comments
-
Yes--With Any GT inverter, you do not tie the Neutral and Earth (Safety) ground anywhere except in the main breaker panel (typically).
What you do not want are parallel current paths--Some "return" current flows in the White wire (US) and other current flows in Green Wire/conduit fittings. You can get problems with over heating green wires/conduit connections/metal electrical boxes if that happens.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Yes but in the case of PV, if the point of neutral-ground bonding is at the main breaker panel while the PV system itself is connected to a subpanel, then unwanted tripping will occur upstream. On the other hand, bonding the PV's neutral with ground at the point of connection (i.e. subpanel) will solve this issue by restricting the tripping to the PV connection. Don't you agree? Please keep in mind that I'm talking specifically about grid-tied unisolated inverters.
-
I am not quite sure I am following your question...
I believe you are in Lebanon (or nearby)? I do not know how your electrical systems are installed there...
However, a transformerless vs transformer isolated GT inverter would not change the AC subpanel/mains wiring requirements.
In many countries, as I understand, the neutral is either "floating" or bonded at the utility distribution transformer. In the US, the neutral is bonded both at the pole transformer and at each home in the Main AC panel (to local home cold water pipe, ground rod, etc.).
In the US, GFI (ground fault interrupter or residual current breakers) are only installed on "branch circuits" (wires from banel breakers to final wire runs (or in the electrical outlets themselves).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
The return path of any fault current at the DC side of the inverter will have to pass through the main panel even if the connection is made at the subpanel for instance?
-
Lamagra,
I think you are a bit off base here. You refer to things like "PV neutral" , "neutral ground bond". None of these terms are relevant to transformerless inverters.
Also you CAN connect a TL inverter to a "sub panel" , in fact larger systems are almost always done that way
-
lamagra said:The return path of any fault current at the DC side of the inverter will have to pass through the main panel even if the connection is made at the subpanel for instance?"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
lamagra said:The return path of any fault current at the DC side of the inverter will have to pass through the main panel even if the connection is made at the subpanel for instance?
-
They shut down too quickly sometimes. We had to replace a TL because of this."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed