Proper battery cycling and maintenance.
Thank you guys for your time and the invaluable information you bring to this community.
Thx shawn.
System #2 is a off grid water system @ 1590w (6 Kyocera 265's) on a 6 module DPW top of pole mount. Feeding a Granfas deep well pump and pump controller at 580 feet. 2 x 2800 gallon above ground poly storage tanks, and 1 x 1200 gallon underground cistern and a Granfas 24v booster pump feeding a 90 gallon carbon fiber pressure tank.
Vag woodstove for heat.
Follow our journey at
https://www.facebook.com/ShawnpHarvey
Comments
-
Hi Shawn,
There are many variables in battery care and maintenance. And, seems that what has been working fine for a period of time will sometimes need to be changed a bit as a battery bank ages.
A few thoughts;
Battery EQ voltage should be temperature compensated -- set your chargers to do this as a default, or do the compensation manually, based on battery temperature, if the charger does not have the compensation of EQ as an option.
EQ voltage should be near the minimum recommended by the battery manufacturer, unless you are having an issue with the bank, that an EQ might be able to resolve -- too great a variation is SGs between cells in the bank, concern about Stratification, etc.
Try to only add water (Distilled) to the bank fairly early in an Absorb, or when doing an EQ, to allow thorough mixing.
Follow manufacturer's guidelines on Absorb, Float and EQ voltages, and EQ duration.
Make sure that every charge source uses a Remote Temperature Sensor (RTS or BTS).
Measure SG readings of each cell in the battery bank and record those readings in the Battery Logbook. Marking each cell with a unique number/letter (or similar) will allow consistency ...
And, so on. Just to get things rolling. Good Luck, Vic
Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Well the important thing with lead is that you charge it to 100% SOC regularly. How you do that is a matter of experience, but gettnig the right absorb voltage, and using the best tech you can find (WBJr) to trigger float is a good start. The alternative is to monitor some charge cycles and assess charge acceptance and/or SG to get the absorb duration. They also like water. For FLA diligent maintenance, for VRLA diligence with avoiding over charging. Thats about it.
1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
Victron have on there site a thing on batery maintenance amoungst other things.2225 wattts pv . Outback 2kw fxr pure sine inverter . fm80 charge controller . Mate 3. victron battery monitor . 24 volts in 2 volt Shoto lead carbon extreme batterys. off grid holiday home
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed