Never mix batteries. Especially different brands/capacities!
They will not charge equally and in some cases (I have seen this personally), they can overcharge the weaker ones and start on fire/explode.
If your original batteries are less than a year old (6 months preferred) then you can add the same exact brand/capacity to the bank but you will effectively bring the new batteries down to the age of the old ones very quickly.
Also, you will have charge inbalances between the old and new batteries for a few months until they both "age" properly.
If the original bank is older than a year, you are better off replacing the entire bank.
Off-Grid in Central Florida since 2005, Full-Time since June 2014 | 12 X Sovello 205w panels, 9 X ToPoint 220w panels, 36x ToPoint 225w panels (12,525 watts total) | Custom built single-axis ground mounts | Complete FP2 Outback System: 3 x FM80, 2 x VFX3648, X240 Transformer, FLEXnet-DC, Mate-3, Hub-10, FW500 AC/DC | 24 x Trojan L16RE-B Batteries 1110ah @ 48v | Honda EU7000is Generator and a pile of "other" Generators | Home-Made PVC solar hot water collector | Custom data logging software http://www.somewhatcrookedcamp.com/monitormate.html -
Thanks, I thought that a series chain was more tolerant for variations among the batteries. Good to know.
Sunpower 3 x 435 watt panels, 48 v 215 AH battery bank (Sam's club), Midnite Kid and WBjr, Fujitsu 9RLS3 split duct AC, Outback FX 3048T + transformer 2000W 120/220V, GrapeSolar Fridge. -
Series batterys have their own form of balance problems. The lowest cell easily gets reverse charged, and easily gets overcharged. The latter is sort of workable, if you keep the water up, the latter kills cells rapidly.
1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
Ok, I've got a battery bank question... Currently running 8 crown 6v batteries that are only 2 months old and am considering adding a 2nd string of the same batteries to double my battery bank.
Assuming I wire the 2nd battery bank the same way can I..?
negative connector to the 1st string hooks to a amp shunt and then to inverter so can I hook the new ground from the 2nd string to the same shunt connector on the amp shunt? Shunt is rated for 500 amps.
connect the pos wire from the new string to the first string's spare pos post to inverter battery post? I'm running 0/4 ga wire from this post to the inverter so it can easily handle the amperage. I just want to make sure it won't harm my first string batteries by connecting these two 48v pos wires.
Current setup is 48v 395 amp/hr battery bank but well pump keeps tripping the low voltage warning when I take my pre-sunrise shower ect. so I want to enlarge the battery bank. Currently 4500 watts in panels but may increase to 5600w in near future since that would about max out my PT-100 charge controller for best bang for the buck and winter use.
I realize it shouldn't be a problem but just trying to be super safe with this set up.
Conext XW+ 4868 inv
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
-
foolami said:Current setup is 48v 395 amp/hr battery bank but well pump keeps tripping the low voltage warning when I take my pre-sunrise shower ect. so I want to enlarge the battery bank.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
SOC is rarely below 80%. Context battery meter shows that pump draws about 2050 watts which seems high for a 1 hp new pump. Low battery disconnect at 47.2v. Grid Supply set at 49.2v although I set it at 48.5 v for a few days working on this problem. Recharge set at 48.4v.
Load shave is on but at 0 amps. Sell is disables and also set at 0.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
-
All wire connections are tight, I double checked them.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
-
I would verify the SOC with a hydrometer first.
Also, IMO, there is no way even a load of 3000w should drag your battery voltage down that low.
I would make sure that you have the proper sized wires going from the batteries to the inverter, that all connections are tight and maybe even do a load test on the batteries individually (old school clamp on load tester). PI am thinking you have a bad battery in that string or one of them is not being charged properly and that is what is causing the voltage to sag so much.Off-Grid in Central Florida since 2005, Full-Time since June 2014 | 12 X Sovello 205w panels, 9 X ToPoint 220w panels, 36x ToPoint 225w panels (12,525 watts total) | Custom built single-axis ground mounts | Complete FP2 Outback System: 3 x FM80, 2 x VFX3648, X240 Transformer, FLEXnet-DC, Mate-3, Hub-10, FW500 AC/DC | 24 x Trojan L16RE-B Batteries 1110ah @ 48v | Honda EU7000is Generator and a pile of "other" Generators | Home-Made PVC solar hot water collector | Custom data logging software http://www.somewhatcrookedcamp.com/monitormate.html -
You have your LBCO incorrectly set BTW. Use the default on the XW. As the previous post, if you are not charged the load will be high on a 1HP pump. The inversion loss will go up because the battery is not charged. This is a prime example of why battery based grid tie often ends in battery failure."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed