Grid faults- Neutral-Ground at 70V!

HI forum.
Wasnt quite sure under what topic to put this as it isnt directly related to solar, but I know there are some seriously good electrical experts and I hope you can help me.
My house is in Spain, where there is a 230V T-T system, the neutral being grounded at the transformer substation a few hundred meters away (in theory). However, the last few days my RCD has been tripping.
When I measured the voltages I was in for a surprise. L-N is normal at 230V. But, N-Ground has been oscillating between 60V and 70V! When this drops below 50V the RCD no longer trips. Voltage between L-Ground is around 280V
.
My first thoughts were a problem with my ground rod. However, i've been to my neighbours houses in the street and they all have exactly the same anomaly.
I have called the distribution company, who i have little faith in. So I'd like to know what on earth could be causing this anomaly in voltages?
Thanks for any assistance
Larry
Wasnt quite sure under what topic to put this as it isnt directly related to solar, but I know there are some seriously good electrical experts and I hope you can help me.
My house is in Spain, where there is a 230V T-T system, the neutral being grounded at the transformer substation a few hundred meters away (in theory). However, the last few days my RCD has been tripping.
When I measured the voltages I was in for a surprise. L-N is normal at 230V. But, N-Ground has been oscillating between 60V and 70V! When this drops below 50V the RCD no longer trips. Voltage between L-Ground is around 280V

My first thoughts were a problem with my ground rod. However, i've been to my neighbours houses in the street and they all have exactly the same anomaly.
I have called the distribution company, who i have little faith in. So I'd like to know what on earth could be causing this anomaly in voltages?
Thanks for any assistance
Larry
Comments
I have hunted down bad wiring (and small scale circuit board shorts) by connecting to a common point (earth ground in this case)--And go to each home and see which has ground to Hot with near zero (or lowest voltage). The point where Ground to Hot is lowest is probably near the point of shorting.
I have not tried this with electrical, but you could try "direction finding" similar to RF signal hunting. Take two metal rods and place them X meters apart and measure the voltage between them.
Then take one of the rods and rotate 45 degrees and drive it into the ground and measure.
The point at which the measured voltage is the greatest, a line through the two rods will point towards (or 180 degrees away) from the source of the voltage. (and conversely, the point at which you measure zero voltage will point 90/270 degrees from the voltage source).
This is exactly how you rotate a directional antenna to find a radio source.
Then move XX meters away and try the same experiment. In theory, you would find the second line--And where the original and the new line cross should be the source of the ground voltage.
Be careful when driving rods/measuring voltages--I have measured >60 VAC and received a good electric shock from two ground electrodes 50 feet apart when there were grounding problems around electric pumps.
Electrical flow may be quite varied due to ground water/moisture levels and free ions (pollutants, fertilizer, irrigation, water pipes in ground, etc.)... So it may not be accurate enough to work (vs free air signal propagation for radio waves).
The gas company measures ground potential to find problems with gas line galvanic protection systems (gas lines are charged and insulated from earth to prevent corrosion).
-Bill
That's not a problem until you have a common point of reference. There is at least one copper wire that connects from your house to the site with the different ground potential. That wire provides the common point of reference... it has the same potential at each end, but each end of the wire is referenced to a different ground rod.
--vtMaps