Which side do I connect the charge controller
This is a newbie question. I am learning about solar on an off grid cabin in Northern Ontario. I have 12 deep cycle batteries and 12 100watt panels. I am using 3 MPPT charge controllers. I incorrectly just wired up all of the batteries in a line, positive to positive, negative to negative with the invertor on one end and the charge controllers on the other end. I gather that this causes an imbalanced load and will soon wear out the last battery that is connected to the load. Now I am wiring the batteries according to a guide so that the load is balanced.
My question is do I connect the charge controllers to where the load is drawn to the invertor or at the other end far away from the load? It might be obvious but I cannot seem to find clear instructions and I was worried that at full sunlight I might be overloading my invertor and the batteries could act as a buffer.
Comments
-
Stop!
What brand/model/AH/voltage rating of batteries do you have? Placing 10 batteries in series will generally not give you a "standard" voltage for most inverters--And if these are 12 volt storage batteries, that will give you 120 VDC nominal voltage--There are a few inverters that can use that voltage, but mostly UPS type computer backup power systems. And these become very difficult to charge (few, if any, solar charge controllers can charge a 120 VDC bank).
Tells us a bit more of your system components (batteries, charge controllers, inverter, etc.).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Bill I hooked them up so that the end voltage is still 12 volts. It is a parallel set up not series.
-
Dailypix said:
My question is do I connect the charge controllers to where the load is drawn to the invertor or at the other end far away from the load? It might be obvious but I cannot seem to find clear instructions and I was worried that at full sunlight I might be overloading my invertor and the batteries could act as a buffer.
But to answer your question, you need bus bars. One bus bar would be for the positive and one for negative. The positive cable from each battery goes (via a fuse) to the positive bus bar. The positives from the inverter and controller also connect to the positive bus bar (via fuses). The negative bus bar receives the negative cable from each battery as well as the inverter and controller.
You will go to a lot of trouble and expense to hook up those batteries correctly and safely, but for what? 12 batteries in parallel is an unworkable scheme. You will not get satisfactory results no matter what you do.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
And just to complete the guidelines, bypassing the problem of massively parallel batteries:
Whether you use a bus bar or a wiring harness you should connect the CC and the inverter to the same points. (Making sure that you have a separate fuse for each.)
SMA SB 3000, old BP panels. -
To understand how best to connect parallel batteries to equalize resistance (and current flow):
http://smartgauge.co.uk/smartgauge.html
However, as talked about above--12x 12 volt batteries in parallel is going to be a pain. You can get a DC current clamp type DMM so you can measure current flow during charging/discharging (find weak batteries, shorted cell, bad wiring connections).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thank you for the comments. If I understand correctly even if I create two separate 6 battery banks connected in series to give me a 24 volt system I am still running 2 sets of 6 batteries in parallel no? Jut two banks of 6 rather than one long bank of 12. At what point does hooking everything up in parallel become a disaster? I believe that my inverter only goes up to 24 volts.
But my question of where I hook up the charge controller was answered. Thank you. I created a well insulated bus bar for the positive and negative sides and connected each of the batteries with the same length of #1 gauge wire. At around the middle I connected very thick welder cable to the invertor with a good DC fuse close to the batteries.
-
Dailypix said:
if I create two separate 6 battery banks connected in series to give me a 24 volt system I am still running 2 sets of 6 batteries in parallel no? Jut two banks of 6 rather than one long bank of 12. At what point does hooking everything up in parallel become a disaster? I believe that my inverter only goes up to 24 volts.
Going to 24 volts will reduce the parallelness of your bank, but it is still too parallel.
In order to get to a 24 volt system, you are suggesting that you make a big 12 volt battery out of six little 12 volt batteries in parallel, and then take two of those big 12 volt batteries and put them in series to make a big 24 volt battery. That will work, but you can do better. It is better to put two of your little 12 volt batteries in series to make a little 24 volt battery. Then take six of those little 24 volt batteries and put them in parallel to make a big 24 volt battery.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Why does my battery drain when I attach it to my solar panel?
-
Joebar17 said:Why does my battery drain when I attach it to my solar panel?
-
Aguarancher said:Joebar17 said:Why does my battery drain when I attach it to my solar panel?
The only panels I know of with a built-in blocking diode are the small portable "battery maintainer" panels that are designed to be connected without a CC.
You panel may have diodes inside its terminal box, but they are in parallel with sub-sections of the panel and are used to keep the panel safe when it is used where it will be partially shaded at some times during the day. They are called bypass diodes.
SMA SB 3000, old BP panels. -
The amount of reverse current into a 12 volt panel from a 12 volt battery bank is usually so small of current, that nobody worries about it.
And pretty much all of the present solar charge controllers will prevent reverse current flow into the panels at night.
Only very small systems, or systems with a small solar panel/array use to "float" batteries during storage (without any charge controller) would reverse current flow possibly be a problem.
Of course, if you connect a solar panel "backwards" to the battery bank, you will have a dead short through the panel and probably the excessive current flow will ruin the solar panel.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
With the limited amount of information provided, it's hard to tell what his set-up is.
-
A picture is worth a thousand words...
2 - 255W + 4 - 285W PV - Tristar 60 amp MPPT CC / 3 - 110W PV -wired for 36V- 24V Sunsaver MPPT CC / midnite bat. monitor.
1 KW PSW inverter 24V / 2.5 KW MSW inverter-24V ~ 105 AHR battery.
3 ton GSHP.- 100 gallon warm water storage / house heat - radiant floor / rad
9 -220W PV - net meter - Enphase inverters and internet reporting system.
420 Gallon rain water system for laundry.*** 6" Rocket Mass Heater with 10' bed for workshop heat.Current project is drawing up plans for a below grade Hobbit / underground home.Google "undergroundandlovinit" no spaces.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed