What breakers are compatible with the XW PDP?
new2PV
Solar Expert Posts: 305 ✭✭
HI looking to add some breakers for the XW PDP what DC breakers are compatible? Will the midnite solar ones work? . I have been getting some pretty crazy prices for the DC breakers in 60AMP...
XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
Comments
-
Believe that Schneider still uses the E-Frame breakers, that are 1" wide for many/all of the DC breaker positions in the PDP. These will be the "CD" style, although believe that the CDs are no longer made. The CF is a much better breaker, IMO, if you need 1" wide breakers.
MidNite uses F-frame breakers, IIRC but primarily for 125 and up Ratings, usually for Inverter connections.
But, before you buy any of these breakers, please make sure that you have the system designed, and you know what you will need to do the job that needs to be done, IMO.
FWIW, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
The Host of this site carries some of the SQ-D E-Frame breakers ... they are kinna hidden:
http://www.solar-electric.com/inverters-controllers-accessories/inverters/xain/nexaxwseinan.html
Again, FWIW, VIcOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Thanks, Vic. The 60 amp will be for the charge controller input and output, however I am sizing the array for a max short circuit current output 48 amps , conductors will be sized at 65 amps.XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
-
I have been working with this host of this site to work out a deal for some breakers, also the sales staff is very friendly and respond quickly to all my questions.:-)XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
-
new2PV,
Just to be clear, if you are working with MPPT type charge controllers... They are (more or less) constant power devices. Meaning it is the power in = power out, and not current in = current out.
For example:- 100 Vmp * 40 amps Imp = 4,000 Watts input
- 4,000 Watts input / 52 Volts battery charging = 77 amps charging battery.
- 60 amp breaker * 0.80 = 48 amps continuous (if you run >~80% of breaker rating, it may trip at some point)
- 60 amps / 0.80 NEC derating = 60 amps * 1.25 NEC derating = 75 amp minimum ~ 80 amp rated breaker (and wiring)
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
The Schneider MMPPt-60-150 will only output 3500 watts with an allowable input of 6700 watts. I am not sure if this breaker is a 100% rated breakers, all the midnite solar DC breakers are 100% current rated. The instructions say to plan your ARRAY current to max 48 amps to allow increased output at colder temps, do you think the 60a breaker will trip at 48 amps??XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
-
Solar arrays/PV electronics are a mess with NEC/UL/etc...
Technically, Imp falls (slightly) as temperature drops. Mostly, Imp/Isc is proportional to the amount of sun hitting the panels (direct, reflections from sand/water/snow). So--On the array side, panel temperature itself is not really an issue (the temp coeff for Imp is something like 1/5 of Vmp--or even a bit less, and in the opposite direction).
However, with MPPT controllers, you can easily have a 20% or greater change in Vmp which will affect the output current Ibatt by 20% (add variation in battery voltage, I=P/Vbatt) and the output side of the MPPT controller can vary quite a bit.
However, most MPPT controllers will current limit to their rated (or programmed) current limit.
While it appears that NEC requires the 60 amp output to be derated to 48 amps (80% of rated value)--I don't think that is correct. Instead, if you plan on 60 amp output, then the output breaker needs to be sized to 60 amps * 1.25 NEC derating or >=75 amps minimum.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
The Schneider MMPPt-60-150 will only output 3500 watts with an allowable input of 6700 watts. I am not sure if this breaker is a 100% rated breakers, all the midnite solar DC breakers are 100% current rated. The instructions say to plan your ARRAY current to max 48 amps to allow increased output at colder temps, do you think the 60a breaker will trip at 48 amps??
Which is really odd, since Vmp increases with lower temperature, but Imp and Isc actually go down for all of the panels I have checked the specs on.
You do not want the low temperature string Voc to be above the DC volts interrupting capacity of the breaker, and changing the current spec will not affect that directly.
SMA SB 3000, old BP panels. -
The breakers recommended by Schneider are 60A for PV input and 80 for DC battery. The input breaker is a 100% rated DC breaker here are the numbers, not sure on the output breaker being a 100% current rated breaker.
PV/MPPT60 DC-Breaker (ARRAY DISCONNECT) Airpax 60A 160VDC MAGNETIC LONG-DLY PNL- MT UL/CSA MFG p/n: 279-1-33909-60
DC Battery Breaker (BATTERY DISCONNECT) Carling Series, 80A/125Vdc/12pc Mfg P/N: EA1-B0-16-680-32A-BFXW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array -
Which is really odd, since Vmp increases with lower temperature, but Imp and Isc actually go down for all of the panels I have checked the specs on.
You do not want the low temperature string Voc to be above the DC volts interrupting capacity of the breaker, and changing the current spec will not affect that directly.
Your are probably correct I could have read that wrong, but they did mention because of factors like snow they are suggesting 48 amps@25C array sizing as max input.XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed