2AWG cables into Morningstar TS-MPPT-60
However, why doesn't Morningstar use threaded studs instead of those hokey clamp-down terminals? One could then use proper lugs without needing to faff about doing what I did. It really bugs me when manufacturers make me have to reengineer what they should have done right in the first place. Hrumph.
John
40' Crown bus with 2kW of tiltable panels on the roof:
Eight Sharp 255W, two Morningstar TS-MPPT-60, Magnum MS2000, Champion C46540 generator converted to propane, eight golfcart batteries, and maybe a small Exeltech inverter for the fridger.
Southern California
You can crimp a lug to the fine stranded cable ends, and fit it that way. I used Anderson ends, and modified them.
why would you need 2 wire in or out of 60 amp controller? sounds like bad system not controller fault.
froggersix wrote: »why would you need 2 wire in or out of 60 amp controller? sounds like bad system not controller fault.
Because I had the 2AWG cable already! I'm just using what I already have. Besides, too large is better than too small. Also, it is the largest size recommended by Morningstar.
John40' Crown bus with 2kW of tiltable panels on the roof:
Southern California
Why in CandyLand are you using 2/0 cable on this 60amp charge controller...??
A plain old 8 guage wire works for the solar input.
A plain old 6 or 4 guage works on the battery output...
jamming 2/0 cable on this controller is just wanton overkill cubed. bigger is not better... better is better...
the 8,6,and4 guage wire will carry ALL the amps this little controller can handle....
2/0 wire is INSANITY to bend and shape and workwith anyway....
-- cake cake cake
~1.5Kw PV in parallel
Morningstar MPPT-60 controllers (2) in parallel
3 Trojan tr-1275's in parallel 450ah total
Samlex 2,000 watt 12-volt inverter hardwired -
I am actually quite happy that they are supporting larger AWG wire for their controller. Ideally, you want around 0.05 to 0.10 maximum voltage drop from controller to battery bank for a 12 volt battery bank (you wan the controller to "accurately" measure the battery bank voltage for fast charging and accurate absorb/float settings).
Using a generic voltage drop calculator, 2 awg wire, and 60 amps, what is the longest cable run (one way run) that it could support with a maximum of 0.10 volt drop?
http://www.calculator.net/voltage-drop-calculator.html
Turns out, that 5 feet (one way run) of #2 cable gives 0.94 volt drop:
Voltage drop: 0.094
Voltage drop percentage: 0.65%
Voltage at the end: 14.406
That is actually a good "fit" for a typical system design...
Personally, I would like if more charge controllers used remote voltage sense leads, or if not that, you could program in the wire length+gauge or resistance--And the controller can then measure/estimate the voltage at the battery terminals (battery bus).
-- cake cake cake
Er, no, I'm not! I'm using 2 gauge, not 2/0. Obviously even I know better than to use 2/0 for a 60A controller! As I explained, I'm using it because I had it, but 4 gauge would have been OK as well. I keep the 2/0 for each house battery bank's cabling, and use 4/0 for the inverter and for the starter interconnection from the house batteries (my 42MT starter draws 900A or more, so only 4/0 is good there).
OK?
Southern California
Iceni John wrote: »
OK?
John
Lawdy... I musta been drinkin last night... I thought you wrote 2/0 wire! LOL my bad! I have the same controller 4 guage is just perfect...
cheers
cake
I'd have to pull up a book for the mppt 60 but the pwm versions do use remote sensing leads, and I always recommend they be used, even with properly sized feed cables.
The MorningStar TS family does have sense leads (small wires from controller to battery terminals to directly measure battery voltage).