Hydrometer

hemmjo
Solar Expert Posts: 90 ✭✭
Looking for a good, easier to read hydrometer. The batteries in our installation are monitored most of the year by people whose skills are not in this area. They take readings and send them to me. Often when I get them I often question the accuracy and value of the report.
We are using a Brady Instruments #1-77-8 that we got from NAWS. http://www.solar-electric.com/batteries-meters-accessories/batteries/baacma/brin1bahy.html This hydrometer is not easy to ready, has no temp reading etc. I have a hard time reading the numbers on the float myself
I see that MidNite Solar now has a hydrometer. http://www.solar-electric.com/batteries-meters-accessories/batteries/baacma/midnite-solar-battery-hydrometer.html Reading the info it seems to be temperature compensated, etc, has a dial type scale, I am wondering if anyone has experience with it?
Thanks,
John
http://villagemountainmission.org/
We are using a Brady Instruments #1-77-8 that we got from NAWS. http://www.solar-electric.com/batteries-meters-accessories/batteries/baacma/brin1bahy.html This hydrometer is not easy to ready, has no temp reading etc. I have a hard time reading the numbers on the float myself
I see that MidNite Solar now has a hydrometer. http://www.solar-electric.com/batteries-meters-accessories/batteries/baacma/midnite-solar-battery-hydrometer.html Reading the info it seems to be temperature compensated, etc, has a dial type scale, I am wondering if anyone has experience with it?
Thanks,
John
http://villagemountainmission.org/
Two systems in the Dominican Republic http://villagemountainmission.org/
installed Feb 2014 at 19.796189° -70.893594°, Classic 150 + WBJR, KISAE SW1210, MN Battery Monitor, IOTA DLS 55/IQ4, 4- Solar World 275w, 4-6v x 225ah Trace Batteries
installed Feb 2015 at 19.795733° -70.893372°, same components as above
Honda PowerMate PC0497000, 7000/8750w generator - powers the well and chargers maybe once a week
installed Feb 2014 at 19.796189° -70.893594°, Classic 150 + WBJR, KISAE SW1210, MN Battery Monitor, IOTA DLS 55/IQ4, 4- Solar World 275w, 4-6v x 225ah Trace Batteries
installed Feb 2015 at 19.795733° -70.893372°, same components as above
Honda PowerMate PC0497000, 7000/8750w generator - powers the well and chargers maybe once a week
Comments
-
Re: Hydrometer
We have a Hydrovolt and I love it. It is easy to read. Saves time when having to read a couple dozen cells. The readings matched those of the float type. I did a comparison when I first bought it.Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M -
Re: Hydrometer
Mountain don
Do you mesure cells in a row with out cleaning? How is it cleaned?
Thanks
gww -
Re: Hydrometer
Always rinse out the hydrometer with a couple of shots of distilled water after use--Otherwise they will get scummy and sticky inside.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Hydrometer
Bill
thank youWe have a Hydrovolt and I love it. It is easy to read. Saves time when having to read a couple dozen cells.
Mostly I was curious about when measuring multiple cells if it was needed to rinse every cell. I currently use an uncompensated extech optical which I wipe between cells. I had absolutly no luck using the squeeze bulb hydrometer that I got from naws. couldn't read it and half the time I made one heck of a mess on the battery with electrolite. I must get the jitters or something. If a guy could go through the cells with out rinsing everytime and had temp comp and could read the numbers, I would have to spend another $30-$45 bucks.
Thanks
gww -
Re: Hydrometer
I do not use batteries--So no direct experience... But you do not need to rinse between cells (in my humble opinion).
The issues are usually when the electrolyte dries.
Be careful to pull electrolyte from below the surface... I have seen "floating debris" and you will pull in air (bubbles on float causes false readings). And be sure not to damage the top of the plates/separators either with the tube.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Hydrometer
Bill
Thanks I think, More money to be spent but sound like it will be worth it.
Ok, I don't just think but actually mean,
Thanks
gww
Ps Bill it was a link you posted once for the extec optical and also for the sears clamp meter. I bought both and have really liked both. -
Re: Hydrometer
You are very welcome GWW,
Somebody else here posted the link for the Sears meter first a few years ago--And that is when i purchased my first clamp meter (with my own money). Other than the temperature probe failing in a few weeks, the rest of the meter has been a joy to use.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Hydrometer
Received a Hydrvolt for Christmas, from me.
Just used it for the first time today. AMAZING compared to all conventional types I've used over the years!
All guesswork regarding temperature etc is gone!
LOVE it! So easy to read!
One note though, my dealer mentioned I should consider some type of mini clamp or whatever on the little fill/drain tube. Seems he's encountered several where it has fallen out of the Hydrovolt and down into the battery. So far mine seems tight, but it's something I'm going to look at. Might try a bit of Marine GOOP (glue). We shall see. -
Re: Hydrometer
Bill
I used the temp lead for a year, stuck about a foot down in the corner of my batt. to measure batt temp. It corroded and no longer works. I still use the dc clamp all the time. really is helpfull to compare readings and see it things are working.
gww -
Re: Hydrometer
Don't stick metal rods/temp probes down in the battery--The chances of shorting a plate is there. You don't want a face full of acid spray.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Hydrometer
Bill
Fork truck, I ment the corner of the battery out side plastic inside steel battery case.
Thanks though
gww -
Re: Hydrometer
Oh, OK GWW... Just want to keep everyone safe.
I do like IR Temperature guns... Clean and quick. And usually close enough for government work.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Hydrometer
couldn't read it and half the time I made one heck of a mess on the battery with electrolite.
I have only used my Hydro Volt for five months, never seen it drip once, if keep your fingers off the bulb. Very easy to read.
Paul -
Re: HydrometerToManyTrees wrote: »(I have) never seen it drip once, if keep your fingers off the bulb. Very easy to read.
Paul
Could there be something wrong with the one "gww1" has? Perhaps the suction tube loose? And not completely filling it before trying to read? -
Re: Hydrometer
When I talked about being messy, I was talking about the bradly hydometer I bought from naws not the hydrovolt which I don't own yet. As I pointed out, I might just be shaky. I used to try and fill then empty 3 times before mesuring and evey once in a while I would pull it out of the hole while sqeezing the bulb. Probly me and not equipt although with the optical I have less problim but do remove a small bit of electrolite every time I measure. I did not like the bradly and also could not read it but to just get close. I do like the extec optical which states that the electrolite is small enough to cool to the room temp quickly, however if that was the case my sg would not go down as the battery heats up which it does sometimes during eq. The optical is very easy to read. I think the hydrovolt would be good expesially if you can get away without rinsing between each cell. I haven't spent the money yet, but would like to have something I could read to compare with what I have. I find the bradly worthless.
gww -
Re: Hydrometer
I rinse it thoroughly after I am finished with all the readings for the session. I used a small wipe of sealant on the tube fitting for just in case.Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M -
Re: HydrometerWhen I talked about being messy, I was talking about the bradly hydometer I think the hydrovolt would be good expecially if you can get away without rinsing between each cell. I haven't spent the money yet, but would like to have something I could read to compare with what I have. I find the bradly worthless.
gww
I'm sure you'll find a huge difference between it and the Hydrovolt. As to rinsing between cells, unless one cell is really dead compared to the rest, the wee little bit left from the previous cell tested would be for all intents and purposes, totally overwhelmed by the relative huge volume drawn in from the next cell to be tested. -
Re: Hydrometer
After many of us asking Wind-Sun to carry the HydroVolt, a few months ago it appeared on their store site:
http://www.solar-electric.com/batteries-meters-accessories/batteries/baacma/midnite-solar-battery-hydrometer.html
The sample tube on the HydroVolt was, and perhaps still is TOO SHORT for batteries with a considerable amount of electrolyte reserve (above the plates).
Generally the HydroVolt is very easy to read. Sometimes the scales hang-up and need a bit of a rap to begin moving.
Normally still use the Freas glass Hydro, and on occasion will use the HV. The only real concern, for me, regarding the HV, is that it has a large wetted-area inside. This retains a reasonable amount of electrolyte, and over a very long time period, may export a bit of electrolyte from the first cell measured ... yea, know that this is probably a 'fly speck' in the scheme of things. Usually begin a measuring session on one of the chronically high SG cells.
Personally, rinse any hydro three times after a measuring session, with Distilled Water, and try to let the Hydro hang vertically, allowing some of the water to drip out.
Thanks wind-sun for stocking the HydroVolt. Opinions for those who can tolerate them. VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum.
Categories
- All Categories
- 224 Forum & Website
- 132 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 196 Solar Information links & sources, event announcements
- 894 Solar Product Reviews & Opinions
- 255 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 617 Discussion Forums/Café
- 310 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed