My system is done. Last Night i drain the batteries down to a 75% SOC by what the Midnite Kid said along with Whizbang Jr. Today had full sun and it charge my bateries to full. What i would now like to do is add more to my system
1. Have 4 6v batteries in series for a 24v system (225AH).
2.Would like to add 4 more 6v batteries (8 total @450AH) PLUS
3. Take the 4 -100 watt panels i did have and reinstall in series/parellel for 24v and get a PWM Charge Controller for the extra charging of the 8 batteries.
Will this work at charging the 8 6v bateries at 450AH?
1. Have 4 6v batteries in series for a 24v system (225AH).
2.Would like to add 4 more 6v batteries (8 total @450AH) PLUS
3. Take the 4 -100 watt panels i did have and reinstall in series/parellel for 24v and get a PWM Charge Controller for the extra charging of the 8 batteries.
Will this work at charging the 8 6v bateries at 450AH?
1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter
Comments
-
Re: Finally System is done
Total Wattage--Assuming 5% to 13% rate of charge:- 450 AH * 29 volts charging * 1/0.77 rate of charge * 0.05 rate of charge = 843 Watt array minimum
- 450 AH * 29 volts charging * 1/0.77 rate of charge * 0.10 rate of charge = 1,695 Watt array nominal
- 450 AH * 29 volts charging * 1/0.77 rate of charge * 0.13 rate of charge = 2,203 Watt array "cost effective maximum"
- 960 Watt array + 400 Watt additional = 1,360 Watt array
- 1,360 Watt array / 1,695 Watt array (10%) = 0.8 or ~8% of battery capacity
If your daily power needs are mostly during the night--And, of course, you don't draw too much power, you should be fine.
If, however, you have significant power needs during the day (irrigation, office equipment, etc.) full time--Then you should look at your average wattage requirements for the loads--I.e., you want a 5% minimum into the battery bank + enough solar panels to support the loads (especially if this is a full time off grid system as opposed to backup/seasonal/weekend system).
Using PV Watts for Springfield Mo, 37 degree tilt from horizontal, fixed array:
Month
Solar Radiation
(kWh/m2/day)
1
3.93
2
4.20
3
5.18
4
5.54
5
5.71
6
5.80
7
5.92
8
5.99
9
5.44
10
4.95
11
3.83
12
3.29
Year
4.99
Toss the bottom three months (as needing backup genset or simply reducing power needs during poor weather):- 1,360 Watt array * 4.2 Hours of Sun average per day (February) * 0.52 end to end system eff = 2,970 Watt*Hours per day of 120 VAC power
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed