The conduit from the array to the combiner box, if it outside the building, can it be in the gray PVC conduit ??
0
·
Share on Twitter
Comments
Solar Guppy
Solar Expert
Posts:
1,987
✭✭✭
August 2008
#2
Re: Wiring Question
You may like to read this
http://www.nmsu.edu/~tdi/pdf-resources/CC122.pdf
It is allowed in the NEC but the local inspectors may and or can require EMT
0
·
Share on Twitter
n3qik
Solar Expert
Posts:
741
✭✭
August 2008
#3
Re: Wiring Question
Thanks, was hoping to save some $$ but not this time.