Dual batt banks or parallel bank?
![solarix](https://wa.vanillicon.com/a6472bcd4e6f9fdccd5b42329eacca30_100.png)
solarix
Solar Expert Posts: 713 ✭✭
My standard off-grid system is a Magnum 4448PAE inverter with a Midnite classic 200, 8 Trojan L16RE-B batteries and 12 PV panels. Not big enough for the current well-to-do (utility connected) customer so am doing a double system except only 20 panels.
Question for the forum is: Would you combine these together with 2 strings of batteries in parallel (inverters and controllers both stack) or would you split into two systems with one string of batteries for each inverter and controller? It takes the same amount of breakers, and wire etc. either way.
Question for the forum is: Would you combine these together with 2 strings of batteries in parallel (inverters and controllers both stack) or would you split into two systems with one string of batteries for each inverter and controller? It takes the same amount of breakers, and wire etc. either way.
Comments
-
Re: Dual batt banks or parallel bank?
If the AC side needs to be coupled so does the DC side. That's the key. -
Re: Dual batt banks or parallel bank?
I would make up a single battery bank, using low voltage batteries as necessary to avoid paralleling, and attach both CCs and both inverters to it. With their own individual fuses, of course.
Were you thinking of stacking the inverters or just wiring them independently to different groups of loads? For stacking I am pretty sure that they are happiest with a single common battery bank for best performance.
Just remember that the one thing that cannot be shared is the panels. Each CC must have its own group of panels, particularly if they are MPPT type and do not intercommunicate.SMA SB 3000, old BP panels. -
Re: Dual batt banks or parallel bank?Each CC must have its own group of panels, particularly if they are MPPT type and do not intercommunicate.
I think I know what you're getting at, but I'm having trouble with the use of 'particularly'.
Are you trying to say that PWM controllers should have their own array, and that non-communicating MPPT controllers must have their own array?
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Dual batt banks or parallel bank?
no, no not sharing the arrays. Each charge controller will have its own 10 panels. Also seems to me the batteries will be happier if they are two separate banks that get individually managed. I'll set the inverters up in voltage controlled mode so that when below 48.8V the inverter charger will kick on and charge from the grid until over 52.6 volts leaving room to fully utilize the solar charging. -
Re: Dual batt banks or parallel bank?I think I know what you're getting at, but I'm having trouble with the use of 'particularly'.
Are you trying to say that PWM controllers should have their own array, and that non-communicating MPPT controllers must have their own array?
--vtMaps
I don't know what inetdog is trying to say but MPPT controllers, communicating or not, should each have their own array. Otherwise at the very least they will have trouble selecting proper power point due to the connection of other controller(s). PWM's being basically a switch don't care so much. -
Re: Dual batt banks or parallel bank?no, no not sharing the arrays. Each charge controller will have its own 10 panels. Also seems to me the batteries will be happier if they are two separate banks that get individually managed. I'll set the inverters up in voltage controlled mode so that when below 48.8V the inverter charger will kick on and charge from the grid until over 52.6 volts leaving room to fully utilize the solar charging.
You haven't addressed the issue of whether or not the AC side of the inverters will be coupled. If they are then the DC side must be as well.
This would not be the same as a system where some loads are on one inverter and some on another. -
Re: Dual batt banks or parallel bank?Cariboocoot wrote: »I don't know what inetdog is trying to say but MPPT controllers, communicating or not, should each have their own array.
I think the bit about 'communicating' is because some MPPT controllers are stackable and you may have more than one controller per array. example: the Midnite Kid in its "bully" mode.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Dual batt banks or parallel bank?I think the bit about 'communicating' is because some MPPT controllers are stackable and you may have more than one controller per array. example: the Midnite Kid in its "bully" mode.
--vtMaps
But does Bully mode actually do this?SMA SB 3000, old BP panels. -
Re: Dual batt banks or parallel bank?But does Bully mode actually do this?
Yes, from what I read.
Mario's (a Midnite engineer) comment here: http://midniteforum.com/index.php?topic=1710.msg15351#msg15351
-- vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Dual batt banks or parallel bank?
The inverters will be stacked - meaning tied together so the AC outputs are synchronized and work together, but this doesn't mean that their batteries have to be common. I think the less parallelism the batteries have the better - and one set of 8 on each inverter is no parallelism at all. Each inverter pulls what it needs from its bank and if it runs low its charger should turn on (or if the inverters are slaved, does the charging act together as well as the output). -
Re: Dual batt banks or parallel bank?
If the inverters are slaved (in parallel, not to get 240V from two 120V inverters), then they will probably draw each draw similar current from their battery banks. But the inverters have no direct control over the chargers. So the two CCs will start charging at about the same rate and the same time, without any interconnection, as the battery voltages decrease similarly.
If the inverter parallel scheme uses one inverter only for low loads, to minimize the tare load of the other inverter by essentially turning it off) then the two battery banks will not be loaded at all equally and you may even get a situation where one inverter stops because of its low voltage cutoff and the other inverter may or may not take over and pick up the small load.
This is one of the reasons that a single battery bank is more robust and easier to manage.
You could have both CCs working together to make up the current drain of only one of the two inverters.SMA SB 3000, old BP panels. -
Re: Dual batt banks or parallel bank?
Ask the question, ignore the answer. Okay; not my money wasted. -
Re: Dual batt banks or parallel bank?
Finally read the inverter manual. Definitive answer is to run one batt pack shared by both inverters as the parallel inverters are controlled as master/slave where the master does most of the work and will imbalance the batteries if on separate batts. -
Re: Dual batt banks or parallel bank?Finally read the inverter manual. Definitive answer is ...
Definitive answer was the very first reply to this thread. --vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Dual batt banks or parallel bank?
Solirix: Er, thanks Coot. you were right.
Coot: No worries, my pleasure.1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed