not re but maybe ground.
gww1
Solar Expert Posts: 963 ✭✭
I was using a hand held mixer (food) today and I reached over to the sink to wipe something off the finger of my other hand and got a jolt on it from the sink. Any ideals.
Thanks
gww
Thanks
gww
Comments
-
Re: not re but maybe ground.
Is this an older Mixer with two prong plug and metal case?
Sounds like a ground fault (hot wire in mixer is connected to metal case/beaters/etc. One hand on mixer, other hand on grounded sink.
So--Mixer has a hot to metal (case/beater) ground leak. Fix or replace.
Next--The outlet next to the kitchen sink:
If two prong outlet, replace with GFI + three prong outlet.
If three prong outlet and three prong mixer--Check for missing ground on kitchen outlet. In any case, if not GFI protected, replace with GFI outlet.
A remote possibility is the sink is "Hot" and the mixer was (properly) grounded through ground wire in plug. That would mean there is something wrong in your AC mains+earth safety grounding somewhere (age of house will affect grounding/2vs3vsGFI outlets).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: not re but maybe ground.I was using a hand held mixer (food) today and I reached over to the sink to wipe something off the finger of my other hand and got a jolt on it from the sink. Any ideals.
Thanks
gww
1. We can assume that you are not using a GFCI protected receptacle to power the mixer?
2. If it happens only when the mixer is running, then there is either resistive leakage inside the mixer from the hot side of the circuit to exposed metal and that exposed metal is not connected to ground by a third wire in the cord and in the receptacle wiring (defect) or there is capacitive leakage between the mixer wiring and the exposed metal (not a defect) and there is no ground wire connection through cord and receptacle. You may want to try reversing the plug if it is two-wire unpolarized plug.
3. If it happens even when the motor is stopped, then there may be a potential difference between the mixer's grounded metal and the sink metal. That could be a sign of some real problems in the house wiring system and at that point you need to get a real electrician to look directly at your problem. Internet diagnosis will not be safe.
*** And what Bill said.SMA SB 3000, old BP panels. -
Re: not re but maybe ground.
The house is 1968, I believe it has 3 wire. Mixer has two prong. Sink does not shock at any other time. It does have one big and one little prong. (plug/mixer) I may have forced it in bacwards. The mixer was running. I will have to try it with the mixer off. I will do this the next time I feel a little tired. I had just put new back board on the sink and replaced the plug cover with a wider one. I didn't look to see if the ground was connected or just hanging there. I knew this wasn't an electrictions site but most electritions I talked to prior to installing my solar and wind were not really that helpful on the inverter solar side and some guys on here are good at it all. I have live in this place for about 20 years and have never had this happen before and my wife would have told me if it had happened to her. I did install the solar and I am not sure if I put that plug on the inverter or not. I didn't do the whole house cause I run out of room in the 12 breaker sub-panel. I came really close though. You guys have given me things to check out.
Thanks
gww -
Re: not re but maybe ground.
Would using an electrical circuit tester be less painful, i.e. no shock ?
I would be working this out asap, shocks near water can go bad real quick. Especially for kids or pets. -
Re: not re but maybe ground.
When I was a little kid back in the early 1960's -- I would occasionally help my Mom cooking... I learned not to touch the old metal 2 wire hand held mixer and the sink at the same time pretty quickly (nothing to fix there :roll:).
You can get a simple 3 prong tester from the hardware store to do a quick outlet sanity check.
Receptacle tester - Wikipedia
The mixer is probably very old (prior to the advent of double insulated tools). You may have to decide to replace the mixer for safety.
Installing GFI outlets near sinks/tubs/garage sinks/water/outside is the "modern" solution anyway. If the mixer keeps popping the GFI--Then the mixer needs fixing or replacement.
The problem with "testing" is it does not take very much current to zap you... (about 5 mAmps +/-). A DMM will draw much less current and gave give you unreliable readings (very little current will read a voltage on the meter).
A "Wiggy" solenoid volt meter:
http://www.amazon.com/Ideal-61-065-Volt-test%C2%AE-Solenoid-Voltage/dp/B000BVNSLG
Will draw more current--But is probably not going to be sensitive enough to detect 5 mAmp current leak.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: not re but maybe ground.
Thanks guys.
I appretiate the responces. I wasn't that worried but more surprised. I have been under houses in the crawl space laying on the dirt and getting tingled when touching the copper piping. Honestly we still only fixed the pipe altough if the electric bill would have went up we would have looked further. I haven't rushed to fix anything yet but just wanted some avenues for when I get to it. I am happy for the ideals even though this is probly not the proper subject matter for an re forum, but, you guys are smart.
Thanks
gww -
Re: not re but maybe ground.
note that here in the u.s. a gfci is required in any kitchen or bath. this could be a breaker into the main breaker panel, but they sometimes fail when installed in wet basements. the types made to install into an outlet box fair better, but are harder to wire sometimes.
if you could force a polarized plug in backwards into an outlet then replace the outlet so that you can't plug into it backwards. plugging it in backwards could cause you to lose the benefits of having it polarized and re-introduce the shock hazard.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed