Low Voltage Cut Off
Alaska Man
Solar Expert Posts: 252 ✭✭
What is the recommened LVC for a 12V AGM?
I have mine set to 11.9V, but when the fridge kicks on and the bankis around 80% DOD, the surge has my Xentrex Beeping. It's not a big deal just, "Beep, Beep, Beep" and we all move on.
I went fishing this past weekend and it was the first time both the wife and I were away from the house for an extended period time since I installed the array this past spring. It was comforting to know if the sun didn't keep up that the inverter would cut out and not kill my bank.
Is 11.5v too low if it happens once or twice a year?
I have mine set to 11.9V, but when the fridge kicks on and the bankis around 80% DOD, the surge has my Xentrex Beeping. It's not a big deal just, "Beep, Beep, Beep" and we all move on.
I went fishing this past weekend and it was the first time both the wife and I were away from the house for an extended period time since I installed the array this past spring. It was comforting to know if the sun didn't keep up that the inverter would cut out and not kill my bank.
Is 11.5v too low if it happens once or twice a year?
Comments
-
Re: Low Voltage Cut Off
First off, I hope you mean 80% state of charge (80% of capacity left), not 80% depth of discharge (80% of capacity used up). Second, 11.5V is essentially a dead battery (about 10% of capacity left), so I wouldn't want to go that far. You might be able to get away with setting the low-voltage cutoff at 11.8V (30% state of charge) without risking too much damage to your battery bank. -
Re: Low Voltage Cut Off
There is a huge difference between Un loaded and Under load voltage on a 12 V system. Depending on your cables you will always see a .3 - .5 voltage sag no matter what the actual un-loaded voltage of the batteries are. You know your system better than anyone posting here. Check the voltage drop when the refrigerator comes on and check the drop if it's your biggest load. Personally I set up most 12 V systems at 11.4 v.
You can get into a cycle that is not good where the inverter drops and the will reengage over and over if you set it to high. As the load is dropped the batteries will recover rapidly.
Attachment not found. -
Re: Low Voltage Cut Off
I would also check the voltage at the battery terminals...
For a 12 volt system, if you have 0.5 volts or more of drop (during surge current)--Then the 11.5 volts at the inverter could easily be 12.0 volts at the battery bank.
Or, for short term heavy/surge loads (seconds to minutes), 11.5 volts at the inverter (or even the battery) would not be the "worst thing" in the world. Long term voltage below ~12 volts (minutes/hours) would be a better set point.
But--In the end, battery voltage is a very difficult gauge of battery state of charge (state of charge levels, discharge current, battery temperature, voltage drop, age of battery, etc.).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Low Voltage Cut OffBlackcherry04 wrote: »There is a huge difference between Un loaded and Under load voltage on a 12 V system. Depending on your cables you will always see a .3 - .5 voltage sag no matter what the actual un-loaded voltage of the batteries are. You know your system better than anyone posting here. Check the voltage drop when the refrigerator comes on and check the drop if it's your biggest load. Personally I set up most 12 V systems at 11.4 v.
You can get into a cycle that is not good where the inverter drops and the will reengage over and over if you set it to high. As the load is dropped the batteries will recover rapidly.
Attachment not found.
That happened to me once, I thought I was in disco, Lights on, Lights off, Lights on, Lights off rapidly..... almost had a seizure. ;-) -
Re: Low Voltage Cut OffFirst off, I hope you mean 80% state of charge (80% of capacity left), not 80% depth of discharge (80% of capacity used up). Second, 11.5V is essentially a dead battery (about 10% of capacity left), so I wouldn't want to go that far. You might be able to get away with setting the low-voltage cutoff at 11.8V (30% state of charge) without risking too much damage to your battery bank.
Yes, I always seem to get that backwards, 20% DOD -
Re: Low Voltage Cut Off
Thanks everyone, I think I will bump the set point down a bit and see if it stops the warning sounds.
I cut about 3' off the positive cable from the bank to the inverter, making it as short as I could hoping that would do it............. Nope -
Re: Low Voltage Cut Off
If your 880 Amp hour battery bank is at 80% SOC you should not be seeing 11.9 Volts.
If that is at the inverter, the wires are too small and there's too much Voltage sag.
If that is at the battery, the batteries aren't at 80% SOC and/or their capacity is a lot less than 880 Amp hours. -
Re: Low Voltage Cut Off
I can't speak to his batteries and setup, but I have 1300 amp hrs of 2 v Surrettes all cabled with 4/0 and when my refrigerator goes into defrost and is pulling 80 amps I get a .5 drop in the voltage that will dip and recover to about .3 or so. It's not unusual at all to see 11.7v @ 80% dod. -
Re: Low Voltage Cut Off
TriMetric is showing in the low 80s when it starts to beep at the fridge cycle. Usually the Xentrex, MN CLassic and the Xentrex Control Panel all read the same 12.2-12 .3 range. I watch it closer tonight and see if I can't read how much it sucks the bank down.
Thanks again. -
Re: Low Voltage Cut OffBlackcherry04 wrote: »There is a huge difference between Un loaded and Under load voltage on a 12 V system.
Yeah, I dropped the ball on that one. Thanks for pointing out my error. :cool:
I still would be pretty conservative in setting the low-voltage cutoff, but not for the reason I originally posted. -
Re: Low Voltage Cut OffYeah, I dropped the ball on that one. Thanks for pointing out my error. :cool:
I still would be pretty conservative in setting the low-voltage cutoff, but not for the reason I originally posted.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed