Now to put it together...
Pierre
Registered Users Posts: 1
Hello. I plan on installing my own 7KW PV roof mounted system in the next few days and I could use some professional advice.
I have been a building contractor for 30 years and am experienced in AC electric, but know little about DC or solar installations.
I purchased the following components on the advice of a salesman:
24- JA P6 72-285/3BB PV panels (Multi Crystalline)
1- Xantrex XW6048 Grid-Tie inverter (6000 watts) (open circuit voltage 45)
2- Outback Flexmax 80 charge controllers 80 amps MPPT
16- 12V 170AH solar batteries
1- Xantex XW Distribution Panel
1- Midnite MNVP12 Combiner box
12- 20A 150 VDC single pole din breakers
4- 80A 125VDC single pole breakers
2- Delta LA302DC lightning arrestors
1- Delta LA302R 300VAC lightning arrestors
1- Xantrex Auto Generator Start
1- XW remote system control panel
Here are some of my questions:
How should I wire my panels with the MC4 wires to go into the combiner box? 24 panels and 12 breakers 20A?
Do I have to cut off the end of the MC4 to connect it to the breakers?
Why do I have 12- 50’ MC4 cables? Don’t the panel cables hook into each other?
What size wire should I use to go from the combiner box to the distribution panel (25’)?
How should I connect my batteries to go into the distribution panel? I have only 2- 10’ 4/0 inverter cables and 16- 1’ 2/0 battery cables 4- 80A 125VDC breakers
Will the Outback charge controllers be compatible and communicate with the Xantrex control panel? Why do I have 2 controllers?
Where do I install the 3 lightning arrestors?
Looks like I have to connect the big DC disconnect in the distribution panel to the 80A breakers?? What size wire? Why do I have 4?
Thanks
Pierre ><>
I have been a building contractor for 30 years and am experienced in AC electric, but know little about DC or solar installations.
I purchased the following components on the advice of a salesman:
24- JA P6 72-285/3BB PV panels (Multi Crystalline)
1- Xantrex XW6048 Grid-Tie inverter (6000 watts) (open circuit voltage 45)
2- Outback Flexmax 80 charge controllers 80 amps MPPT
16- 12V 170AH solar batteries
1- Xantex XW Distribution Panel
1- Midnite MNVP12 Combiner box
12- 20A 150 VDC single pole din breakers
4- 80A 125VDC single pole breakers
2- Delta LA302DC lightning arrestors
1- Delta LA302R 300VAC lightning arrestors
1- Xantrex Auto Generator Start
1- XW remote system control panel
Here are some of my questions:
How should I wire my panels with the MC4 wires to go into the combiner box? 24 panels and 12 breakers 20A?
Do I have to cut off the end of the MC4 to connect it to the breakers?
Why do I have 12- 50’ MC4 cables? Don’t the panel cables hook into each other?
What size wire should I use to go from the combiner box to the distribution panel (25’)?
How should I connect my batteries to go into the distribution panel? I have only 2- 10’ 4/0 inverter cables and 16- 1’ 2/0 battery cables 4- 80A 125VDC breakers
Will the Outback charge controllers be compatible and communicate with the Xantrex control panel? Why do I have 2 controllers?
Where do I install the 3 lightning arrestors?
Looks like I have to connect the big DC disconnect in the distribution panel to the 80A breakers?? What size wire? Why do I have 4?
Thanks
Pierre ><>
Comments
-
Re: Now to put it together...
Pierre,
That is a big project to start with!
What size Battery Bank do you have?
You are planning on Grid Tied operations (feeding power back to the utility)? Do you have pre-approval from your utility for GT connection/operation?
-billNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Now to put it together...How should I wire my panels with the MC4 wires to go into the combiner box? 24 panels and 12 breakers 20A?
Do I have to cut off the end of the MC4 to connect it to the breakers?
Why do I have 12- 50’ MC4 cables? Don’t the panel cables hook into each other?
Hi, I'll answer what I can:
With 24 panels (the 72 cell variety), you'd need to create 12 sets of 2 panels in series. I.e. you connect the + and - of two panels together, then you connect your long mc4 cables to the remaining + and - and those cables go to your combiner box. That forms 1 set. If you have 12 MC4 cables in total, then it seems whoever advised you to get them intended for them to be cut in half so that the ends without mc4 connectors go to your breakers in the combiner box.
The outback controller won't talk to the Xantrex components, but it's not necessary that it does. Would have been nice to get everything Xantrex, but the system will work fine with the outback controller. You only have 1 controller listed, the Xantrex control panel is purely to program and monitor the Xantrex inverter. -
Re: Now to put it together...
Here are some of my questions:
How should I wire my panels with the MC4 wires to go into the combiner box? 24 panels and 12 breakers 20A?Do I have to cut off the end of the MC4 to connect it to the breakers?Why do I have 12- 50’ MC4 cables? Don’t the panel cables hook into each other?What size wire should I use to go from the combiner box to the distribution panel (25’)?How should I connect my batteries to go into the distribution panel? I have only 2- 10’ 4/0 inverter cables and 16- 1’ 2/0 battery cables 4- 80A 125VDC breakersWill the Outback charge controllers be compatible and communicate with the Xantrex control panel? Why do I have 2 controllers?Where do I install the 3 lightning arrestors?Looks like I have to connect the big DC disconnect in the distribution panel to the 80A breakers?? What size wire? Why do I have 4?
Frankly the project size here is so large that a first-timer should not be taking it on. You really need the help of a qualified installer on site to work out the details. -
Re: Now to put it together...Pierre wrote:Looks like I have to connect the big DC disconnect in the distribution panel to the 80A breakers?? What size wire? Why do I have 4?
You have 4 strings of batteries (each string is 4 batteries in series), and the 4 strings are in parallel. That is a poor design for batteries that are meant to be frequently cycled, but is not so bad if they are primarily meant to float (for backup use). The four 80 amp breakers are meant to go in each battery string... if one string develops a shorted cell the breaker will hopefully trip before a fire occurs.Cariboocoot wrote: »MidNite combiner boxes come with MC4 connectors built in.
They come both ways. If yours does not have built-in MC4 connectors, then cut the MC4 extension cords in half and put the cut end into the combiner box. Do not ever cut off the MC4 connectors on the solar panels.
I agree with the others that you should get some experienced help... or at least get your salesman to give you a wiring diagram.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed