Inverter cable and breaker sizing
SwampYankee
Registered Users Posts: 16 ✭
Off grid 12V
600AH bank
I have a 2000W Wagan Elite that according to the manual the recommended fuse is an ANL 300A with #4 gauge cables. This doesn't sound right...a 300A fuse on 4 gauge wire??
I have a bunch of 0 gauge....can that be used with a 250A Breaker?. Is there a difference between a breaker and slow burn fuse? I always thought you fuse the system to protect the wire and thus 4 gauge does not rate a 300A fuse.
My run will be about 6ft. Can anyone tell me what size wire I would use with a 250A breaker for this inverter?
inverter specifications:
Overload protection: 2,000 W – 2,100 W
Reverse polarity protection: fuse
Short circuit protection: shutdown
High temperature protection
Working temperature: -10°C to 40°C
Input volt: 12 V DC
Output volt: 120 V AC
Output Waveform: Pure Sine Wave
TrueRated™ Power: 2,000 W
Surge power: 4,000 W
Maximum Efficiency: Approximate 90%
Frequency: 60 Hz
No load current draw: < 1.5 A
Total Harmonic Distortion: < 5%
Low battery alarm: 10.5 V ± 0.3 V
Low battery shut down: 9.5 V ± 0.3 V
High voltage protection: 15.5 V ± 0.5 V
Swamp
600AH bank
Input volt: 12 V DC
Frequency: 60 Hz
Swamp
Re: Inverter cable and breaker sizing
ABYC (American boating and yachting council) only allows around 130-160 Amps maximum for a 4 AWG cable (they allow 30-35 amps for a 14 AWG cable where NEC allows 15 amps--really 20 amps, another issue--maximum).
And 2/0 for 300 amp fuse.
If you want to run the inverter at 2,100 watts:- 2,100 watts * 1/0.85 typical inverter eff * 1/10.5 volt cutoff * 1.25 NEC derating = 294 amp minimum branch circuit rating
- 2,100 watts * 1/0.85 typical inverter eff * 1/10.5 volt cutoff = 235 amp minimum branch circuit rating
And then there is voltage drop (simple calculator). For 235 amps and 0.5 volt maximum drop at 6 feet round trip for cable: 2 AWG for 0.5 volt drop.
Using the ABYC table, a minimum of 1 AWG cable.
Using NEC table 310-16 would be 300-350 circular mill cable minimum (plus even more deratings for temperature, conduit fill, etc.).
The reality is, most people will not run their inverter more than ~50% of capacity and only near rated capacity for a few seconds when starting motors (saws, well pump, etc.).
For a 600 AH flooded cell battery bank--The typical rule of thumb power support would be:- 600 AH * 12 volts * 0.85 inverter eff * 1/20 Hour discharge rate= 306 Watts long term average power for cabin (2 days storage, 50% max discharge)
- 600 AH * 12 volts * 0.85 * 1/8 Hour = 765 Watts maximum continuous discharge
- 600 AH * 12 volts * 0.85 * 1/5 Hour = 1,224 Watts short term maximum discharge
- 600 AH * 12 volts * 0.85 * 1/2.5 Hour = 2,448 Watts maximum starting power
You could easily "dial back" the current rating to ~1,224 Watts as the maximum continuous power you would pull from that size battery bank--Save yourself lots of copper and expensive fuses/switches.
Thank you Bill for the detailed answer. -
There is no chance 4 AWG will take 300 Amps.
Are you sure they didn't say 4/0?
2000 Watts on a 12 Volt system will come close to 200 Amps at maximum output/minimum input Voltage. 4 AWG would be at its limit around 1/2 that current.
If you want to use the 250 Amp breaker you need at least 2/0 (00) and 3/0 (000) would be better.
Depending on the distance involved and how close to maximum you run the inverter 4/0 may be preferable. It usually is on a 12 Volt system. -
Re: Inverter cable and breaker sizingCariboocoot wrote: »There is no chance 4 AWG will take 300 Amps.
I just checked again and it is 4AWG. Chinese manual probably. -
Its pretty common in the "cheap chinese" segment to find provided cables in that (lame) size range. Perhaps this is a good time to reevaluate whether you trust the health and wellbeing of your house and family to this product???1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
If your inverter is 12 V use 4/0, you'll never regret it. The cost is very small in the scheme of things and you won't get as much of a voltage sag as you would with the other sizes. The Fuse /Breaker should be sized to the size cable your using.