Is there a simple breaker solution between the battery and inverter?
TucsonAZ
Solar Expert Posts: 139 ✭✭
I know there's the $200 plus disconnect boxes but what were people doing a decade ago? Is there a simple breaker solution to put between the inverter and the batteries for a low budge throw your codes out the window application?
Also, with a 1,500 watt Cotek pure sine 24v inverter, how big of a DC breaker do I actually need?
Also, with a 1,500 watt Cotek pure sine 24v inverter, how big of a DC breaker do I actually need?
Comments
-
Re: Is there a simple breaker solution between the battery and inverter?
To answer the second question first, 1500 Watts @ 24 Volts is 62.5 Amps. Depending on how low a Voltage the inverter allows (could be 21) this may be as much as 72 Amps. Apply the NEC derating (avoids nuisance trips) and you basically get a 100 Amp breaker. For best results consult the instructions for the inverter regarding sizing of DC wiring and over-current protection.
To answer the first question second, cheap and easy ain't in it. You can get an appropriate size DC breaker for <$50 http://www.solar-electric.com/stfubr1.html but you may need to be handy at fabricating to come up with a mount for it. -
Re: Is there a simple breaker solution between the battery and inverter?Cariboocoot wrote: »To answer the second question first, 1500 Watts @ 24 Volts is 62.5 Amps. Depending on how low a Voltage the inverter allows (could be 21) this may be as much as 72 Amps. Apply the NEC derating (avoids nuisance trips) and you basically get a 100 Amp breaker. For best results consult the instructions for the inverter regarding sizing of DC wiring and over-current protection.
To answer the first question second, cheap and easy ain't in it. You can get an appropriate size DC breaker for <$50 http://www.solar-electric.com/stfubr1.html but you may need to be handy at fabricating to come up with a mount for it.
Awesome, thank you! I came up with this after I typed my post:
http://www.amazon.com/STINGER-SCBM150-Marine-Circuit-Breaker/dp/B002LARRTO/ref=pd_sim_sbs_e_10?ie=UTF8&refRID=1XK7QBN8XXJJ4KV1TR06
I like the MidNite 100a more and if I can use a 100a (I will check specs) that would be my first choice so I will do a little more research, fabricating is what I live for (: -
Re: Is there a simple breaker solution between the battery and inverter?
You should size the breaker for the surge current not the rated current. Your inverter also has a 3000W surge rating, so I'd say you need at least a 150A breaker.
BTW, Off-topic:
The cotek 1500W/24V inverter and the Victron 1600W/24V have almost identical specs, yet the cotek weighs 5.3kg, and the Victron 10kg, guessing that's because of a bigger transformer. -
Re: Is there a simple breaker solution between the battery and inverter?
That's a nice inverter for sure, I'm sure the components are substantially better and I would have liked to get a higher quality unit but the Cotek and 1kw of solar panels cost me what that Victron costs so I will have to stick with the Cotek as my backup inverter bought before the inverter it's meant to back up (:
I will disagree on the 150a breaker but I have read this:
http://www.midnitesolar.com/pdfs/Carling_A-DTime-Delays.pdf
As such, I'm fairly certain even with a 3,000 watt surge which is right at 125% of the breakers rated amps that the breaker won't trip for what the inverter is rated to do. I'm not factoring in the 91% efficiency but with that said, I'm not looking to run my inverter at surge capacity beyond a few seconds at a time (which the breaker can handle) and in all honesty would have been fine with a 700watt inverter for my needs I just wanted to be on the safer side. My way of saying that I would rather the breaker trip if I'm pushing the inverter over the 3,000 watt surge it's intended for. -
Re: Is there a simple breaker solution between the battery and inverter?I will disagree on the 150a breaker but I have read this:
http://www.midnitesolar.com/pdfs/Carling_A-DTime-Delays.pdf
Aha, good data that. I'd rather err on the side of a too-big breaker than too small, since the currents generated by a short circuit will be much larger than the normal operating currents. I guess with those numbers and your planned usage you should be OK. -
Re: Is there a simple breaker solution between the battery and inverter?You should size the breaker for the surge current not the rated current. Your inverter also has a 3000W surge rating, so I'd say you need at least a 150A breaker.
Actually, no. Most 'surge' ratings are for such a brief time that a breaker rated for the continuous current will hold for that period. Breakers actually need more than their rated current for a certain period of time before they trip so momentary surges should not cause nuisance trips. Plus most people do not run their inverters anywhere near capacity (which is a good thing).BTW, Off-topic:
The cotek 1500W/24V inverter and the Victron 1600W/24V have almost identical specs, yet the cotek weighs 5.3kg, and the Victron 10kg, guessing that's because of a bigger transformer.
Quite probably. The small Cotek/Samlex inverters have notoriously poor surge duration (less than 1 second), and a tiny transformer is one reason for this.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed