Basic and likely stupid question, but here goes........

This switch is rated at 32V and 300A continuous. Can I use it at 48V if the current is kept below 200A?

http://www.amazon.com/gp/product/B000MMFJH0/ref=ox_sc_act_title_7?ie=UTF8&psc=1&smid=A1UNWS4MSNTF2A

http://www.bluesea.com/products/6007/m-Series_Mini_Selector_Battery_Switch_-_Red

Comments

  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    Re: Battery switch rating question
    balee123 wrote: »
    This switch is rated at 32V and 300A continuous. Can I use it at 48V if the current is kept below 200A?

    Unfortunately, no. Not safe at all. Use a Midnite panel mount circuit breaker... they make great switches and are NRTL listed.

    Those rotary battery switches are not listed for use in a home, even if you stay within their ratings.

    read: http://www.amplepower.com/primer/burnt_sw/index.html

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Options
    Re: Battery switch rating question

    The big problem with using a DC switch above its voltage rating is not that the insulation will simply break down when exposed to the higher voltage. It is that the switch contacts will not be able to separate fast enough or far enough to control the DC arc which will form as the contacts separate under load.
    SMA SB 3000, old BP panels.
  • zoneblue
    zoneblue Solar Expert Posts: 1,220 ✭✭✭✭
    Options
    Re: Battery switch rating question

    .. and maybe weld, and remain connected when you most need it disconnected. Or melt completely and short to metal surrounding, thus making much bigger problems. As Bill says... that would spoil your day.
    1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
    http://zoneblue.org/cms/page.php?view=off-grid-solar