Pulling 12 volts from a 24 volt bank
littleharbor2
Solar Expert Posts: 2,101 ✭✭✭✭✭
I was wondering what your thoughts are on tapping 12 volts from a 24 volt bank of batteries? The scenario is a simple 2-12 volt series wired bank of batteries. You can pull 12 volts from one of the two batteries, and I know this isn't the best thing to do due to the imbalancing of the batteries voltage. What I am proposing is tapping BOTH batteries and paralleling that. Seems the load on the batteries would be even at that point. I must be missing something here or this scenario would be a common and simple way of getting 12 volts out of a 24 volt module/battery bank setup.
Your thoughts are much appreciated. Little Harbor 2
Your thoughts are much appreciated. Little Harbor 2
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Comments
-
Re: Pulling 12 volts from a 24 volt banklittleharbor2 wrote: »I was wondering what your thoughts are on tapping 12 volts from a 24 volt bank of batteries? The scenario is a simple 2-12 volt series wired bank of batteries. You can pull 12 volts from one of the two batteries, and I know this isn't the best thing to do due to the imbalancing of the batteries voltage. What I am proposing is tapping BOTH batteries and paralleling that. Seems the load on the batteries would be even at that point. I must be missing something here or this scenario would be a common and simple way of getting 12 volts out of a 24 volt module/battery bank setup.
Your thoughts are much appreciated. Little Harbor 2
What you are missing is the explosion that will occur. You can't hook up two 12 volt batteries in series (24 volts) and parallel (12 volts) at the same time.
You need a Dc to DC converter. A company called 'Solar Converters' makes high quality ones.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Pulling 12 volts from a 24 volt bank
The "practical" ways of taking 12 volts from a 24 volt battery bank:- Wiring 12 volts from one battery: If loads are very tiny--It can be done. Larger loads will "unbalance" the batteries. The tapped battery will always be under charged or the untapped battery will always be over charged (you have to over charge the untapped battery to get the tapped battery fully charged--very bad for either battery).
- DC to DC converter: 24 volt battery to 12 VDC output... Common solution. Really not much different that using a 24 volt AC inverter and powering loads at 120 VAC and skipping the whole 12 VDC output--Many times, 120 VAC just ends up being easier to use everywhere vs 12 VDC appliances (issues of 10.5 to 15.5 volts from a flooded cell battery bank and many "12 volt" loads not really living well in those ranges. Higher end DC converters are around the same price as 120 VAC inverters (in many cases).
- DC to DC converter: For some vehicles that need both 24 volts for engine starting and 12 volts for other loads--There are DC to DC converters that are designed to connect from low bank to high bank. They are "bi-directional" isolated output converters. They keep the high/low bank battery voltages "identical"---You can discharge/charge either high 12v or low 12v bank or 24 VDC and the converter will keep the charge on both banks identical. Again, not a cheap solution.
- 24v to 12v charge controller: Basically get a 24 volt charge controller (you can use some MPPT charge controllers for this function) to charge a 12 volt VDC battery bank. Advantage is you have a full off grid 12 volt battery+charge controller--Handles surge current well and is a backup to 24 volt power. Downside is you have an "extra" 12 volt battery to maintain.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Pulling 12 volts from a 24 volt bank
So if you tap into one battery you get 12 volts. Now you tap into the other battery and pull an equal amount of power out of it would you not be discharging the two batteries at the same rate and not be causing the problem of discharging the bank unevenly? I'm missing where the "Explosion" happens.2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Re: Pulling 12 volts from a 24 volt bank
Yes--If the loads are naturally balanced--Yes, you can do this pretty well.
The dead short was read from this:What I am proposing is tapping BOTH batteries and paralleling that. Seems the load on the batteries would be even at that point.
You cannot "parallel" the wiring. Each load would require its own +/- leads. You cannot "Parallel" high+low bank batteries by just wiring them together.
You can use isolated output DC to DC converters to "parallel" the high+low bank of batteries...
To connect (for example) two 12 volt light bulbs. Connect the low bulb to ground and +12 volts. And the second bulb to +12 and +24 volt leads. If the bulbs are "balanced" current--Then there would be close to zero current flowing through the +12 line back to the battery bank.
Some loads (like filament lamps) can be connected in series (like a pair of 12 volt lamps)--Because they naturally balance their current flow.
Other loads (motors, LED/CFL lamps, other non-linear loads)--Their I*V curves do not generally allow them to connect in pure series (without the middle voltage connection). Generally they will fail because one unit will see close to 24 volts when the other is near zero volts.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Pulling 12 volts from a 24 volt banklittleharbor2 wrote: »So if you tap into one battery you get 12 volts. Now you tap into the other battery and pull an equal amount of power out of it would you not be discharging the two batteries at the same rate and not be causing the problem of discharging the bank unevenly? I'm missing where the "Explosion" happens.
-
Re: Pulling 12 volts from a 24 volt bank
Looking at a diagram of a pair of batteries wired in serial, then thinking about drawing current from them in parallel (while they're still wired in serial), leads me to conclude that, in effect, the positive terminal of one battery would simultaneously be connected to both terminals of the other battery. I'm pretty sure the technical term for that is either "explosion" or (at very least) "what could possibly go wrong?".... -
Re: Pulling 12 volts from a 24 volt bank
I am understanding now where the problems lie. Thanks to all for your timely input. This forum is the best source of knowledge around.2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed