Battery link leads
freddyuk
Registered Users Posts: 11 ✭✭
Is there a diagram for connecting 48v battery bank of 8 x 220ah/12v so 4 in series x 2 banks in parallel with balancing leads? Also for a 48/10000/120 victron Quattro what size cables are appropriate for the links between batteries? Lengths can be short. Advised link to inverter is 2 x 50mm cables up to 5m length.
Comments
-
Re: Battery link leads
First question: where are you getting 220 Amp hour 12 Volt batteries? Just checking. Such a thing would be really large and typically that is the Amp capacity of a 6 Volt battery. That's a big bank: over 10kW hours @ 50% DOD.
Wiring is the same for any two parallel strings, the strings simply have more batteries in them. Cable should be large enough to handle the maximum expected current which is basically the maximum capacity of the inverter divided by the minimum operating Voltage. Or consult the installation manual because they usually have the best recommendations for installation (especially for keeping the warranty valid). Links between batteries also must meet this maximum current spec. The cables to the inverter may need to be larger in order to keep the V-drop at maximum load to a minimum (not as much of a problem with a 48 Volt system as with a 12 Volt one). -
Re: Battery link leadsCariboocoot wrote: »First question: where are you getting 220 Amp hour 12 Volt batteries? Just checking. Such a thing would be really large and typically that is the Amp capacity of a 6 Volt battery. That's a big bank: over 10kW hours @ 50% DOD.
While I don't know the source of the original poster's batteries, I do know that our host sells Universal AGM 12-volt batteries with up to 250 Amp-hour capacity (C/20). -
Re: Battery link leadsWhile I don't know the source of the original poster's batteries, I do know that our host sells Universal AGM 12-volt batteries with up to 250 Amp-hour capacity (C/20).
Yup. 154 lbs. each. Like I said: really large.
I just felt it necessary to check the specs due to the Amp hours coinciding with the standard GC2's; people do get confused about these things and it's best to make sure we're dealing with the right numbers. -
Re: Battery link leadsCariboocoot wrote: »Yup. 154 lbs. each. Like I said: really large.
I just felt it necessary to check the specs due to the Amp hours coinciding with the standard GC2's; people do get confused about these things and it's best to make sure we're dealing with the right numbers.
Batteries sourced from UK supplier. They are flooded wet lead acid not AGM's. So will require and have maintenance and recovery if things go wrong! Site is a small processing plant using some heavy amps for maybe 2 hours in a day. Hopefully low DOD will extend lifetime. 10KW PV should keep things topped up. Maximum load maybe 6-7 kw/240v peak via Victron inverter with generator backup if required.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed