Charge settings check

verdigo
verdigo Solar Expert Posts: 428 ✭✭
I just re-programmed my Classic 150 with the WB Jr. Would appreciate any comments on my charge settings. The batteries are GC2-HXD Interstate @ 464ah.
Absorb = 56.4
Float 52.8
EQ 62.4
End amps @1% 4.64

Thanks

Dennis

Comments

  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: Charge settings check
    verdigo wrote: »
    I just re-programmed my Classic 150 with the WB Jr. Would appreciate any comments on my charge settings. The batteries are GC2-HXD Interstate @ 464ah.
    Absorb = 56.4
    Float 52.8
    EQ 62.4
    End amps @1% 4.64

    Thanks

    Dennis

    Looks like the Absorb Voltage is too low. Ought to be at least 57.6 and probably 58-ish.
    Float could stand to be pushed up a bit too. Possibly 55.
    EQ on the other hand is a tad higher than normal.
    Not sure End Amps applies when using SOC ending with the WhizBang Jr.

    I won't ask what Interstate recommends because they probably don't.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,642 admin
    Re: Charge settings check

    This is the Interstate Battery Charging FAQ:

    -Bill

    http://www.batteries-faq.com/activekb/questions.php?questionid=1

    Charging recommendations for 6-volt deep cycle batteries. GC2-XHD, GC2-HD, GC2-RD



    Nominal Battery Voltage

    Charging Current

    Bulk Charge Voltage (2.41 VPC)

    Absorption Voltage (2.55 VPC)

    Absorption Time in Hours

    Float Voltage (2.23 VPC)

    Equalization Voltage (2.6 VPC)

    Equalization Time in Hours



    6 Volt (3 cells)

    C / 10

    7.23

    7.65

    2 to 4

    6.7

    7.8

    2



    8 Volt (4 cells)

    C / 10

    9.64

    10.2

    2 to 4

    8.92

    10.4

    2



    12 Volt (6 cells)

    C / 10

    14.46

    15.3

    2 to 4

    13.4

    15.6

    2



    24 Volt (12 cells)

    C / 10

    28.92

    30.6

    2 to 4

    26.8

    31.2

    2



    36 Volts (18 cells)

    C / 10

    43.38

    45.9

    2 to 4

    40.2

    46.8

    2



    48 Volts (24 cells)

    C / 10

    57.84

    61.2

    2 to 4

    53.5

    62.4

    2




    Notes: 1. All charging voltages shown above are for 80 degrees F. For every 10 degrees above 80 F reduce voltage by 0.028 VPC. For every 10 degrees below 80 F increase the voltage by 0.028 VPC.
    2. VPC = Voltage Per Cell
    3. Charging current; C = The amp hour (Ah) capacity rated at the 20 hour rate.
    4. Float condition is for long term storage / (several weeks) inactivity. 5. Equalize every 4 to 8 weeks or when the difference in specific gravity readings vary by 0.020 points or more and always after a normal charge.

    Other Charging Notes/Tips/ Definitions: Temperature Compensation: Increase voltage by .028 volts per cell for every 10 degrees below 80 F. Decrease voltage by .028 volts per cell for every 10 degrees above 80F. Typical phases on multi-stage chargers: Bulk: Initial phase where the voltage builds and the most current is provided to the battery. This is typically where the maximum current that the charger is capable of providing is supplied to the battery. i.e. A 10 amp charger will provide at or near 10 amps during this phase. Absorption: The phase where the voltage set point is held constant. Current will decrease gradually during this point as the battery internal resistance comes up. Float:

    The maintenance or finishing phase of the charging cycle. Voltage is set at a minimum during this phase (usually 13.0c-13.5v) and current drops significantly. The battery should be nearly complete by the time this phase is reached. An anti sulfation stage may be added where voltage spikes to high levels for very brief time periods for a set amount of time determined by the charger manufacturer, to convert the battery active material back to it's original state. Badly sulfated batteries will not usually respond to this charging regime and will need to be replaced.

    [h=3][/h]
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • verdigo
    verdigo Solar Expert Posts: 428 ✭✭
    Re: Charge settings check

    For Bill. Isn't that chart set up for the 10 hour charge rate? I use to use those numbers but some on the forum said more or less that it was a bit too aggressive for RE applications.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,642 admin
    Re: Charge settings check

    I would start with these numbers... Monitor water usage (refill every ~2 months when cycling seems to be reasonable, filling every less than 1 month is probably over charging, and not filling every 6 months is probably under charging).

    You want to batteries to fizz somewhat near the end of charging--And you can adjust the absorb time (as well as voltage set point) to get the battery bank ~90% State of Charge (several times a week on average).

    More or less, solar RE systems have a limited amount of time to charge during the day (maybe ~6 hours on average over the year of "reasonable" sun for a fied array). So, that means, for batteries being cycled (say below 75% SOC), you need to get them recharged "somehow"... That means higher voltages and longer absorb times (especially during winter).

    You may even end up with different settings during winter/summer months.

    2320 Watts * 1/59 volts charging * 0.77 panel+controller derating = ~30 amps peak "average" charge current
    30 amps / 464 AH capacity = 0.065 = 6.5% Rate of charge

    You have close to a minimum array for charging a daily use battery bank--So it will probably spend "less time" at the absorb set point (less than 80% SOC, battery bank is usually below absorb set point, above ~90% the batteries will be at set point--At higher charging currents, the set point will be reached sooner --- like 85% or lower SOC).

    So, how has your Specific Gravity been looking? Are you getting the battery bank >90% SOC at least once or twice a week?

    If the batteries are using lots of water and/or getting "hot", then lowering your set point voltage and/or absorb time (2-4 hours vs 4-6 hours) would be good.

    -Bill

    PS: With my "non-expert" eyes, I don't see these values as being "high" for a flooded cell battery. They seem quite mild and may need to be raised (especially during winter/short charging periods).
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • verdigo
    verdigo Solar Expert Posts: 428 ✭✭
    Re: Charge settings check

    Specific gravity is 2.70-2.75. Since this is going to be grid tied it won't get much cycling, and when the project is finished the array will total at least 3000 watts which according to the classic sizing tool anyway will give me 49 amps charging current. Maybe that's not peak average? In any case I will increase the array wattage to get to the 10% goal. The higher voltages do make since to make the most of the available sun for a given day. I have cycled the batteries a few times but probably no more than 80%. I'm not hooked into the house yet, so I have only ran loads on extension cords. I hope the wizzband jr will help me get a better handle on SOC.

    Thanks
  • BB.
    BB. Super Moderators, Administrators Posts: 33,642 admin
    Re: Charge settings check
    verdigo wrote: »
    Specific gravity is 2.70-2.75.

    1.270 sg to 1.275 sg?

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • verdigo
    verdigo Solar Expert Posts: 428 ✭✭
    Re: Charge settings check

    Yeah. Maybe a little over charged huh?
  • BB.
    BB. Super Moderators, Administrators Posts: 33,642 admin
    Re: Charge settings check

    That is typically pretty much a full charge.... You are not cycling them very much at this point--So you do not need to run on the high side for voltage/absorb time.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • verdigo
    verdigo Solar Expert Posts: 428 ✭✭
    Re: Charge settings check

    Thanks for your help.

    Dennis