Panels and New MX60
nigtomdaw
Solar Expert Posts: 705 ✭✭
Hi have a friend who has the following Panels
Two are; Shell SP140-PC
140 watts 24 volt
SCC 4.7 amps
OCV 42.8V
Rated current 4.25 amps
Rated voltage 33.0
The other four are Sharp NT-R5E3E
175 watts 24 volt
SCC 5.40 A
OCV 44.4 V
Current 4.95 A
Voltage 35.4 V
He has a nominal 24v system, my take on wiring these up would be two strings consisting of 1 x Shell x 2 Sharp then parallel identical strings to MX or is therea better option, he lives in Spain so very rarely to we see temps below freezing and if so a few degrees over night. Or are the panels close enough spec to have 2 x Shell + 2 x Sharp + 2 x Sharp and have 3 Parallel Strings ? Which is best, or is there another option.
Thanks
Two are; Shell SP140-PC
140 watts 24 volt
SCC 4.7 amps
OCV 42.8V
Rated current 4.25 amps
Rated voltage 33.0
The other four are Sharp NT-R5E3E
175 watts 24 volt
SCC 5.40 A
OCV 44.4 V
Current 4.95 A
Voltage 35.4 V
He has a nominal 24v system, my take on wiring these up would be two strings consisting of 1 x Shell x 2 Sharp then parallel identical strings to MX or is therea better option, he lives in Spain so very rarely to we see temps below freezing and if so a few degrees over night. Or are the panels close enough spec to have 2 x Shell + 2 x Sharp + 2 x Sharp and have 3 Parallel Strings ? Which is best, or is there another option.
Thanks
Comments
-
Re: Panels and New MX60
Nigel,
Option #1:“two strings consisting of 1 x Shell x 2 Sharp then parallel identical strings to MX”
String STC Vmp would be 33.0 V + (2 x 35.4 V) = 103.8 V
String Imp would be ~lowest of individual modules in string, or ~4.25 A
Estimated STC power for array would be 103.8 V x 4.25 A x 2 = ~882.3 W
Option #2:“2 x Shell + 2 x Sharp + 2 x Sharp and have 3 Parallel Strings”
Shell string STC Vmp would be 2 x 33.0 V = 66.0 V
Shell string STC Imp = 4.25 A
Each Sharp string STC Voc would be 2 x 44.4 V = 88.8 V
Each Sharp string STC Vmp would be 2 x 35.4 V = 70.8 V
Each Sharp string STC Imp = 4.95 A
Array Vmp voltage would would be ~lowest of individual strings in array, or ~66.0 V
Estimated STC power for the array would be 66.0 V x (4.25 A + 4.95 A + 4.95 A) = 933.9 W
Analysis
Option #1 advantages:- Only two strings, so individual string circuit breakers not required
- Lower array current specs = lower power loss in wiring to controller
- Array Voc is fairly high. Applying the U.S. NEC temp correction factor of 110% for ambient temps down to 0 C (32 F) results in an array voltage of 131.6 V x 110% = 144.76 V. This is within the MX60’s overall limit of 150 V, but it exceeds the operational limit of ~141 V.
- Option #1 configuration results in lower array power spec than Option #2
- Option #1 configuration results in lower operating efficiency (~1% point) for MX60 due to higher input voltage
- Array Voc is relatively low (85.6 V), and will operate well within MX60 limits even with NEC TCF.
- Option #2 configuration results in higher array power spec (~5.8%) than Option #1
- Option #2 configuration results in higher operating efficiency (~1% point) for MX60 due to lower input voltage
- Three strings, so individual string circuit breakers are required
- Higher array current specs = higher power loss in wiring to controller
I’d suck up the additional costs for circuit breakers and heavier gauge wire and go with Option #2 due to higher power and more conservative array Voc.
HTH,
Jim / crewzer -
Re: Panels and New MX60
Jim I could just say thanks as normal, but I cut and pasted your detailed reply to my friend (customer who I sold the MX60 to, never met him lives about 30 minutes away)
I gave the credit to you in others words I told him this was from my friend and expert in USA he emailed me this evening and it says it all
Hi Nigel, just a quick email to say that I rewired my panels as to your instructions and, behold, I am now getting almost double the output! Thanks once again for your help and advice.
Regards Chris
Thats about as good as it gets, pour yourself a large one
Regards Nigel Sunny Spain ps he took option 2 -
Re: Panels and New MX60
Nigel,
I'm glad that the suggestions worked out for you and your friend. As for pouring myself a large one, my plan is to put it on your "tab" and I will collect if I'm ever in your neighbourhood.
Regards,
Jim / crewzer -
Re: Panels and New MX60
Im sure the tab will run long and deep in one direction only:cool:
regards
Nigel -
Re: Panels and New MX60
:D8)
Jim / crewzer
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed