Need help finding a charger to charge an eight battery bank system
Off-grid Texan
Solar Expert Posts: 25 ✭
I have an eight battery bank wired in series and parallel for 12v. They're 232Ah Interstate golf cart batts. I currently charge my batts whenever the gen is running to keep them up when the suns not out but the digital display on the charger never EVER shows a charge of more than 60-63% (about 12.2v) when the charger quits. The charger I'm using is one I had in my shop. It's a Schumacher 10A/20A. I've read on the NAWS site that I might need upwards of 26-60 amp charger to get a complete charge. Thoughts, comments, suggestions, recommendations?
Thanks!
Thanks!
Comments
-
Re: Need help finding a charger to charge an eight battery bank system
Has anyone yet mentioned that having four parallel battery strings is not a good idea? I know it would be a further outlay but you should consider going to a 24 Volt system if at all possible.
A bit about why: http://forum.solar-electric.com/showthread.php?15989-Battery-System-Voltages-and-equivalent-power
That said, you have 4 * 232 Amp hours or 928 Amp hours @ 12 Volts. Ideally you should have a peak charge current around 92 Amps for that. Which isn't going to happen. There's no single charge controller that will produce that kind of current. In terms of a stand-alone charger this big Iota comes close: http://www.solar-electric.com/ioen12vo90am.html
In solar panels you'd actually need like 1440 Watts of panel and two MPPT controllers to handle it. Another reason to investigate going up to a 24 Volt system. -
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »Has anyone yet mentioned that having four parallel battery strings is not a good idea? I know it would be a further outlay but you should consider going to a 24 Volt system if at all possible.
A bit about why: http://forum.solar-electric.com/showthread.php?15989-Battery-System-Voltages-and-equivalent-power
That said, you have 4 * 232 Amp hours or 928 Amp hours @ 12 Volts. Ideally you should have a peak charge current around 92 Amps for that. Which isn't going to happen. There's no single charge controller that will produce that kind of current. In terms of a stand-alone charger this big Iota comes close: http://www.solar-electric.com/ioen12vo90am.html
In solar panels you'd actually need like 1440 Watts of panel and two MPPT controllers to handle it. Another reason to investigate going up to a 24 Volt system.
Again, thnx...looks like I'm going 24v.
Like Edison said..."Those who never made mistakes are people who never tried anything new!" -
Re: Need help finding a charger to charge an eight battery bank systemBlackcherry04 wrote: »Actually you have 4 , 6 V GC-2 's batteries that are 232 Amp hrs each.
Could have sworn he said "an eight battery bank". That would be four parallel strings of two in series giving 928 Amp hours @ 12 Volts as they are 232 Amp hour 6 Volt batteries (probably the same East Penn PS2200's I use). -
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »Could have sworn he said "an eight battery bank". That would be four parallel strings of two in series giving 928 Amp hours @ 12 Volts as they are 232 Amp hour 6 Volt batteries (probably the same East Penn PS2200's I use).
-
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »
That said, you have 4 * 232 Amp hours or 928 Amp hours @ 12 Volts.
Why would it be 4 * 232 and not 8 * 232? -
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »Has anyone yet mentioned that having four parallel battery strings is not a good idea? I know it would be a further outlay but you should consider going to a 24 Volt system if at all possible.
And here's a short discussion of why parallel batteries are problematic.Cariboocoot wrote: »That said, you have 4 * 232 Amp hours or 928 Amp hours @ 12 Volts. Ideally you should have a peak charge current around 92 Amps for that. Which isn't going to happen. There's no single charge controller that will produce that kind of current.
The midnite Classic is rated 96 amps. (but I'm not suggesting you use it in this situation... operating any controller at its maximum rating continuously will shorten its life). As Cariboocoot mentioned, you should be reconfiguring your system to 24 volts.Cariboocoot wrote: »In terms of a stand-alone charger this big Iota comes close: http://www.solar-electric.com/ioen12vo90am.html
Off-grid Texan, what generator do you have? The Iota charger has poor power factor and huge inrush currents... not a problem if you are powering it from the grid, but may be a problem if your generator is not larger than you think it needs to be.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan wrote: »Why would it be 4 * 232 and not 8 * 232?
You put two 6 Volt 232 Amp hour batteries in series to get 12 Volts: the Amp hours does not add up with a series connection, only the Voltage does.
You put four of these 232 Amp hour 12 Volt strings in parallel to get 928 Amp hours @ 12 Volts: the Amp hours add up in parallel, the Voltage doesn't. -
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »You put two 6 Volt 232 Amp hour batteries in series to get 12 Volts: the Amp hours does not add up with a series connection, only the Voltage does.
You put four of these 232 Amp hour 12 Volt strings in parallel to get 928 Amp hours @ 12 Volts: the Amp hours add up in parallel, the Voltage doesn't.
GOTCHA! I did not know the amp hours didn't add up when in series. I'm assuming they do in parallel?? -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan, what generator do you have? The Iota charger has poor power factor and huge inrush currents... not a problem if you are powering it from the grid, but may be a problem if your generator is not larger than you think it needs to be.
--vtMaps
You think my gen could be an issue? I thought a gen was a gen only dif being output. I have a harbor Freight special 4000W peak 2300W nominal...so far that bad boy runs everything on my property. -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan wrote: »GOTCHA! I did not know the amp hours didn't add up when in series. I'm assuming they do in parallel??
Yes: series connection adds Volts but not Amps, parallel connection adds Amps but not Volts.
The generator issue vtMaps is one of power factor PF: 92 Amps * 12 Volts is 1104 Watts on the DC side, but with a poor PF the draw on the generator can be a lot more than 1104 Watts. In fact it can be around 1400 Watts. If the generator can't supply that it will be overloaded. -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan wrote: »You think my gen could be an issue? I thought a gen was a gen only dif being output. I have a harbor Freight special 4000W peak 2300W nominal...so far that bad boy runs everything on my property.
The generator can probably handle that Iota, there's really only one way to find out... try it. One thing for sure: the Iota will use up most of the capacity of that generator... you may not be able to power anything else other than the Iota.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »Yes: series connection adds Volts but not Amps, parallel connection adds Amps but not Volts.
The generator issue vtMaps is one of power factor PF: 92 Amps * 12 Volts is 1104 Watts on the DC side, but with a poor PF the draw on the generator can be a lot more than 1104 Watts. In fact it can be around 1400 Watts. If the generator can't supply that it will be overloaded.
I knew the voltage and amperage changed w/ series vs parallelling but I didn't know amp hours changed. Thanks.
In regards to the gen's power output even at the 1400 watt range it's still within the gens limits easily and many times we've ran the gen soley to charge the batts with no other load. Or am I missing something here? -
Re: Need help finding a charger to charge an eight battery bank systemThe generator can probably handle that Iota, there's really only one way to find out... try it. One thing for sure: the Iota will use up most of the capacity of that generator... you may not be able to power anything else other than the Iota.
--vtMaps
I know those Iotas aren't cheap...any other alternatives? I want quality of course. (Buy nice or buy twice! Right?) -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan wrote: »I knew the voltage and amperage changed w/ series vs parallelling but I didn't know amp hours changed. Thanks.
In regards to the gen's power output even at the 1400 watt range it's still within the gens limits easily and many times we've ran the gen soley to charge the batts with no other load. Or am I missing something here?
I think you are missing something. You have been charging with a SMALL schumacher charger... not much of a load.
Also, the Iota may draw 1400 watts (probably closer to 1250 watts), but the VA may be much higher. Your generator needs to have a watt rating higher than the VA of the Iota.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan wrote: »I know those Iotas aren't cheap...any other alternatives? I want quality of course. (Buy nice or buy twice! Right?)
Actually, the Iotas are cheap. and rugged. But they are not PF corrected and may be a problem with generators. A high quality PF corrected charger will cost three times as much as the Iota.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Need help finding a charger to charge an eight battery bank systemI think you are missing something. You have been charging with a SMALL schumacher charger... not much of a load.
--vtMaps
You have a point good Sir. -
Re: Need help finding a charger to charge an eight battery bank system
And if you're changing to a 24 Volt system spend the money on an inverter-charger; the built-in chargers they have are much better than the stand-alone units in terms of PF and programming for charge profile. -
Re: Need help finding a charger to charge an eight battery bank systemActually, the Iotas are cheap. and rugged. But they are not PF corrected and may be a problem with generators. A high quality PF corrected charger will cost three times as much as the Iota.
--vtMaps
I tell you what...this solar biz is gettin' more and more expensive! Freedom definately costs more than a buck o' five! -
Re: Need help finding a charger to charge an eight battery bank systemAlso, the Iota may draw 1400 watts (probably closer to 1250 watts), but the VA may be much higher. Your generator needs to have a watt rating higher than the VA of the Iota.
I just looked at the Iota spec sheet... it can draw up to 21.8 amps from your generator (maximum inrush current = 40 amps) and Iota recommends that it be powered from a circuit with a 30 amp circuit breaker. I wouldn't make a bet that your generator can handle that.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »And if you're changing to a 24 Volt system spend the money on an inverter-charger; the built-in chargers they have are much better than the stand-alone units in terms of PF and programming for charge profile.
I haven't even began to investigate those combo units or anything at a 24v setting. Care to help me save some time since I am going to swap over to 24v and recommend a good combo to look into?? -
Re: Need help finding a charger to charge an eight battery bank systemI just looked at the Iota spec sheet... it can draw up to 21.8 amps from your generator (maximum inrush current = 40 amps) and Iota recommends that it be powered from a circuit with a 30 amp circuit breaker. I wouldn't make a bet that your generator can handle that.
--vtMaps
Yup...20 amp breakers. Good call. -
Re: Need help finding a charger to charge an eight battery bank systemI just looked at the Iota spec sheet... it can draw up to 21.8 amps from your generator (maximum inrush current = 40 amps) and Iota recommends that it be powered from a circuit with a 30 amp circuit breaker. I wouldn't make a bet that your generator can handle that.
--vtMaps
Yep: 21.8 Amps @ 120 Volts is 2616 Watts as far as the generator is concerned. Or in simple terms "ouch".
Off-grid power is very expensive. It's even more expensive if you have to do it twice before getting it right. -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan wrote: »I haven't even began to investigate those combo units or anything at a 24v setting. Care to help me save some time since I am going to swap over to 24v and recommend a good combo to look into??
How big is the inverter you have now?
Do you need 240 Volts?
Have you got a budget?
Basically the Outback FX series or the Magnum line offer very good inverter-chargers for the money. Have a look at our host's listings: http://www.solar-electric.com/oupooffgrand.html and http://www.solar-electric.com/maensiwainac.html -
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »How big is the inverter you have now?
Do you need 240 Volts?
Have you got a budget?
Basically the Outback FX series or the Magnum line offer very good inverter-chargers for the money. Have a look at our host's listings: http://www.solar-electric.com/oupooffgrand.html and http://www.solar-electric.com/maensiwainac.html
I currently have a 2000W nominal inverter. I'd like 240v but I have that on my gen if I need to run my water well to fill my tank for a short period or run the dryer if need be. It's not a deal breaker. -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan wrote: »I currently have a 2000W nominal inverter. I'd like 240v but I have that on my gen if I need to run my water well to fill my tank for a short period or run the dryer if need be. It's not a deal breaker.
There's more than one way to supply 240 VAC, but if you only have a couple of items to run at that Voltage and are happy with using the generator to do that you can skip the 240 Volt inverters and autotransformers.
Outback's built-in charger works better than the Magnum's, as it ramps up from zero current rather than starting out at maximum and adjusting downwards.
I may sound like a broken record but Outback's inverters are functionally superior to the others. They were designed by very smart people (who now run MidNite). -
Re: Need help finding a charger to charge an eight battery bank systemCariboocoot wrote: »There's more than one way to supply 240 VAC, but if you only have a couple of items to run at that Voltage and are happy with using the generator to do that you can skip the 240 Volt inverters and autotransformers.
Outback's built-in charger works better than the Magnum's, as it ramps up from zero current rather than starting out at maximum and adjusting downwards.
I may sound like a broken record but Outback's inverters are functionally superior to the others. They were designed by very smart people (who now run MidNite).
Cool. I was kinda partial to the Outback (not sure why, maybe the reviews and price) but good to know they run MidNite.) Thanks again for all your help! -
Re: Need help finding a charger to charge an eight battery bank system
If your inverter is working for you, and your batteries are still in good condition, all you really need is a decent automotive battery charger like the wheeled jobs you can buy at Sears. With a 40a or 50a quick charge, a 2a slow charge and a 200w "start" charge setting, you can get your batteries back in shape.
The best choice is their deluxe wheeled unit, as it has the higher charge voltages and also gives you a 6v setting. Not many choices on these kinds of units anymore, unless you don't mind spending $500 at your parts house. Look for a sale or figure on about $200 for the best wheeled shop charger at Sears.
Charge the battery from your generator. Can split your battery cabling into 2 sets of 4 when you get a holding charge of 12.6 or higher. Might take a couple to several hours when charging all eight at 50a rate. When your charge/spec gravity is at about 90% you can equalize one-half of your eight using the 250a charge function. Once the batteries are highly charged, the charger will not overheat and you can get an hour or more at the highest rate. Might need to do that now and afterwards, every 3-4 months. Lots on this site about when to Equalize...
24v is "better" but, this idea might be all you need to get the most out of the gear you now have and take time to learn more about all the electric principles that go into sizing and making optimum use of your investment. -
Re: Need help finding a charger to charge an eight battery bank systemall you really need is a decent automotive battery charger like the wheeled jobs you can buy at Sears. With a 40a or 50a quick charge, a 2a slow charge and a 200w "start" charge setting, you can get your batteries back in shape.
The best choice is their deluxe wheeled unit, as it has the higher charge voltages
Most automotive battery chargers do NOT have appropriate charge profiles for deep cycle batteries. They may be adequate for bulking up the battery bank, but they do not have high enough (or adjustable) absorb voltages for deep cycle batteries. What is the model number of their deluxe charger with the higher voltages?Can split your battery cabling into 2 sets of 4 when you get a holding charge of 12.6 or higher.
What do you mean by "holding" charge? If there is a charge imbalance (measured with DC clamp ammeter), then it is a good idea to charge each 12 volt battery while it is disconnected from the rest of the bank.When your charge/spec gravity is at about 90% you can equalize one-half of your eight using the 250a charge function. Once the batteries are highly charged, the charger will not overheat and you can get an hour or more at the highest rate.
This doesn't make sense... usually by the time the batteries are at 90% SOC their charge acceptance is reduced. Equalization is done at a higher voltage than absorb, but NOT at high current. Also, equalization should not be done until the batteries are as fully charged as they can get at normal absorb voltage, and even then equalization should only be done if one or more cells in the battery have not reached 100% SOC as determined by measuring the specific gravity.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Need help finding a charger to charge an eight battery bank systemOff-grid Texan wrote: »Cool. I was kinda partial to the Outback (not sure why, maybe the reviews and price) but good to know they run MidNite.) Thanks again for all your help!
I just installed an outback VFX3648 this weekend, replacing a stand-alone inverter and an IOTA charger and I gotta say I LOVE IT.
The Iota was great, but with the PF/inrush, it would kill my 3500 generator if anything else was running.
With the Outback, I even set it up to use my little 1400 generator and not once did it trip the generator circuit breaker nor bog down due to overloading.
Wish I had made that investment a year ago when I went from 12v to 24v. Lesson learned.Off-Grid in Central Florida since 2005, Full-Time since June 2014 | 12 X Sovello 205w panels, 9 X ToPoint 220w panels, 36x ToPoint 225w panels (12,525 watts total) | Custom built single-axis ground mounts | Complete FP2 Outback System: 3 x FM80, 2 x VFX3648, X240 Transformer, FLEXnet-DC, Mate-3, Hub-10, FW500 AC/DC | 24 x Trojan L16RE-B Batteries 1110ah @ 48v | Honda EU7000is Generator and a pile of "other" Generators | Home-Made PVC solar hot water collector | Custom data logging software http://www.somewhatcrookedcamp.com/monitormate.html
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed