What amp breaker do I need to tie into my Panel
CasaBonita
Registered Users Posts: 3
installing a 24 255 watt panel system wired in two series going to a sunny boy 6000 inverter.. size breaker would I use to tie into my square D breaker panel
Comments
-
Re: What amp breaker do I need to tie into my Panel
Welcome to the forum.
There's a few things we need to check on here. One being what the rating of your service panel is. This is important because there are limits to back-feeding.
Which brings us to the next item; what does the local inspector and utility have to say about this? When it comes to tying in your grid tie inverter, they should definitely have something to say about it. If they don't (or for some reason aren't being involved) you may find yourself with big problems like paying for the electricity you export due to not having the right kind of meter installed.
Otherwise the output of 6kW SMA inverter is 25 Amps max for the 240 VAC version. As such it would require a 40 Amp breaker as per NEC rules, and that would need to be on a 200 Amp main service. And we're talking about 8 AWG minimum wire from inverter to breaker. -
Re: What amp breaker do I need to tie into my Panel
Thanks, Inverter is two feet from service panel.. will use the correct wire
System is being installed , in Mazatlan , Mexico.. CFE (power company ) will inspect and supply the smart Meter.. hope to get system at least up and running next week..
Thanks
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed