Xw6048 installed ... Load meter error
fca1
Solar Expert Posts: 124 ✭✭
Hi after a busy Saturday changing my system to 48v and installing the xw6048 (what a heavy beast)...
Still not fully deployed only some circuits from the house are connected ...
The load output from the xw is connected to PDu where I can measure the loads and I'm getting some strange numbers out of the combox in terms of loads
Example :
My PDu is showing 460w consumption an the xw is showing 318w with 38w from grid and 371w from the battery ...
Not even the 371+38w give the correct how can I have 409w being raked and only 318 on the loads...
The number is not correct in absolute because I know the PDu is correct confirmed by the amps greeting out of the battery ..
But also the Maths from the combox are strange ...
Maybe my problem not understanding yet the xw.... But...
Any toughs ideas are welcome ..
Still not fully deployed only some circuits from the house are connected ...
The load output from the xw is connected to PDu where I can measure the loads and I'm getting some strange numbers out of the combox in terms of loads
Example :
My PDu is showing 460w consumption an the xw is showing 318w with 38w from grid and 371w from the battery ...
Not even the 371+38w give the correct how can I have 409w being raked and only 318 on the loads...
The number is not correct in absolute because I know the PDu is correct confirmed by the amps greeting out of the battery ..
But also the Maths from the combox are strange ...
Maybe my problem not understanding yet the xw.... But...
Any toughs ideas are welcome ..
Comments
-
Re: Xw6048 installed ... Load meter error
Something get lost in "devices". 371+38 = 409; 409 - 381 = 28; BTW, 28W is exact spec for Xantrex idle consumption. Coinsidence?
In my experience, Xantrex is not very accurate. At times it may be off by 200W or more, so the difference of 460-381 = 79W is well within its tolerances. -
Re: Xw6048 installed ... Load meter errorSomething get lost in "devices". 371+38 = 409; 409 - 381 = 28; BTW, 28W is exact spec for Xantrex idle consumption. Coinsidence?
In my experience, Xantrex is not very accurate. At times it may be off by 200W or more, so the difference of 460-381 = 79W is well within its tolerances.
That's my first impression the xw is really inaccurate in the AC part, still have to check the DC side....
And still not able to get the grid to go zero consumption, always have some power coming from the grid... (expected from the comments here and from the manual)...
will ask Schneider if there is a way to get it to zero and what they have to say about this inaccuracy ...
regards -
Re: Xw6048 installed ... Load meter error
For inaccurate meters, my inverter tells my my watts is higher than my KVA (Power Factor >1). -
Re: Xw6048 installed ... Load meter error
You might want to put a Kill-A-Watt on your lighting loads and check the power factor on them. As NorthGuy said idle power is 28 watts no load. That would be lost in the output reading on the inverter. 200 watt error at full power on XW6048 would be @ 3.3% error in display. I think if I remember correctly it draws from grid to stay qualified on AC1 and keep the ability to sell to grid if set up to do that.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!!
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed