Another battery cable question.

verdigo
verdigo Solar Expert Posts: 428 ✭✭
I am mainly just wanting to confirm that I have to make all cables the same length from the battery strings to the bus bar, and from the bus bar to the e-panel/inverter/charge controller. Kinda makes putting this stuff in conduit a pan in the butt.

Thanks

Dennis

Comments

  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: Another battery cable question.

    Same total length on any paralleled circuit.

    So total length of all wires from negative bus bar through a battery string to positive bus bar must be the same on all battery strings.

    Positive and negative wires from bus bars to inverter or charge controller do not need to be equal length, they just usually are.
  • verdigo
    verdigo Solar Expert Posts: 428 ✭✭
    Re: Another battery cable question.

    Thanks again. You guys are great.