mstar tri 45 mppt efficient wiring....
jimbob01
Solar Expert Posts: 63 ✭✭
Hi again :-) have 2 x mstar tristar mppt 45s...
6x 235w sharp 38v
will it be more efficient wiring 2 strings @ 114v
0r wiring all in parallel@38v?
mstar is max 150v in ,
no panels get shaded individually.
jim
6x 235w sharp 38v
will it be more efficient wiring 2 strings @ 114v
0r wiring all in parallel@38v?
mstar is max 150v in ,
no panels get shaded individually.
jim
Comments
-
Re: mstar tri 45 mppt efficient wiring....
One question that will be asked: what is the nominal system Voltage? The only way you could get all six panels on one 45 Amp controller is @ 48 Volts where the output would be around 30 Amps max. (It would be just over 45 Amps with the typical derating on a 24 Volt system - a bit dicey.)
Otherwise, if that 38 Volts is Vmp then the Voc will be about 46, and that must be considered when planning an array. Three in series would give a Voc of 138 which with a bit of cold temperature could easily exceed the Morningstar's maximum input Voltage.
If you're dividing up the six panels between two charge controllers for a lower system Voltage then you'd want to go all in parallel to both avoid the high Voc issue and reduce the Voltage down-conversion to improve controller efficiency. -
Re: mstar tri 45 mppt efficient wiring....
the voc is 38v.... -
Re: mstar tri 45 mppt efficient wiring....
the system is 24v -
Re: mstar tri 45 mppt efficient wiring....
so keeping the voltage down conversion to a minimum on a mppt does increase the output from the system? -
Re: mstar tri 45 mppt efficient wiring....
In that case three in series produces a Voc of 114 which would work in cold temps.
But that also means the Vmp is around 30 so you must have two panels in series to have sufficient Voltage for charging the 24 Volt batteries.
If you put three parallel strings of two in series on one 60 Amp controller that would be best. You could do it on one 45 Amp controller, but you may lose a bit of power potential under some conditions (mild 'clipping' of current above 45 Amps). -
Re: mstar tri 45 mppt efficient wiring....
but does keeping the voltage down conversion to a minimum on a mppt increase the output from the system?
thanks. -
Re: mstar tri 45 mppt efficient wiring....but does keeping the voltage down conversion to a minimum on a mppt increase the output from the system?
thanks.
It does increase efficiency a bit. However, you usually do not have much of a choice because of other factors. -
Re: mstar tri 45 mppt efficient wiring....
thanks north guy..
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed