Fairly long run from Inverter to AC Disconnect / Service.
Wally
Registered Users Posts: 11 ✭
I am planning out a 13 KW DC installation at my son’s rural acreage. It will be a roof mount on a new detached garage/storage shed about 200 feet from where the underground service / Main Terminal Box is located in the yard.
Because of the exposed / exterior location of the interconnection site in the yard, I wish to mount the Fronius V11.4-1 Inverter in that building and make the 200 ft run in 1 ½” pvc buried conduit. Probably will use #2 AWG THWN for the 2 hot wires and #6 AWG for the Neutral and GEC runs --- that seem about right? The max rated output current for this inverter at 240 V is 47.5 A AC but will normally be operating at a max of a little less.
Also, this inverter’s AC Terminals accept a max of #4 AWG wire, so what is the best way to transition from #1 or #2 AWG to #4. I don’t like wire nuts and pig tails with that much current so will probably use split bolt connectors --- I kind of remember that MiNite Solar had a neat connector for doing this, but can’t find it now.
I will also need to get power from this Main Terminal Box back to a Sub Panel in this new building. Any problem with running these feed wires in the same conduit with the inverter’s or should they be in a separate conduit?
Because of the exposed / exterior location of the interconnection site in the yard, I wish to mount the Fronius V11.4-1 Inverter in that building and make the 200 ft run in 1 ½” pvc buried conduit. Probably will use #2 AWG THWN for the 2 hot wires and #6 AWG for the Neutral and GEC runs --- that seem about right? The max rated output current for this inverter at 240 V is 47.5 A AC but will normally be operating at a max of a little less.
Also, this inverter’s AC Terminals accept a max of #4 AWG wire, so what is the best way to transition from #1 or #2 AWG to #4. I don’t like wire nuts and pig tails with that much current so will probably use split bolt connectors --- I kind of remember that MiNite Solar had a neat connector for doing this, but can’t find it now.
I will also need to get power from this Main Terminal Box back to a Sub Panel in this new building. Any problem with running these feed wires in the same conduit with the inverter’s or should they be in a separate conduit?
Comments
-
Re: Fairly long run from Inverter to AC Disconnect / Service.
I think you're making it hard on yourself.
Across 200' 240 Volts @ 50 Amps using 6 AWG gives a V-drop of 3.4%. I would not be worrying about trying to fit 4 AWG or larger.
I know of no issue with running a set of wires from the inverter output in the same conduit as a set of wires carrying AC back to the building. -
Re: Fairly long run from Inverter to AC Disconnect / Service.
From what I remember the code allows one to include conductors from the SAME circuit in a conduit. You should not mix circuits, for example conductors from a PV systerm and a wind gen. in the same conduit. I believe that would also apply to feeder conductors and PV conductors in the same conduit.
THWN is not rated for buried conduit as that is considered a wet location as THWN is listed as dry only. However if you use dual rated THWN/THWN-2 or THWN-2 then you should be ok.
Brent -
Re: Fairly long run from Inverter to AC Disconnect / Service.
if for voltage drop reasons you still wish to opt to go #4 then you could use an electrical box with cover to tie the #4 wire to the #6 pigtails to run up to the inverter. not sure the best way to make the tie, but something like this could work,
http://www.solar-electric.com/16220-2.html
or even this,
http://www.solar-electric.com/tbb.html
edit to add-
sorry i got the gauges messed up, but the options i linked still apply. -
Re: Fairly long run from Inverter to AC Disconnect / Service.
Good catch Brent --- didn’t write that correctly, the wire I am planning on is THHN/THWN-2.
I probably could get by with #4AWG, but 500 ft of #2 AWG is $655 delivered and #4AWG $418, so only $237 more and with the 30% Fed Tax Credit a $166 difference.
With close to 20,000 KWH’s output per year over 20 years would be 400, 000 KWH’s, so even a 2% less voltage / power drop could net 8,000 KWH’s at say an average of $0.20 / KWH over these 20 years and be about $1,600. Probably a little over optimistic, but definitely should have a reasonable payback.
Actually, I was more concerned with the voltage drop causing tracking problems for the inverter with resulting dropouts. But I have this same inverter installed here, although on a very short run, and Xcel Energy has hit it with everything from 214V to over 270V and it has never dropped off. Probably more paranoid about this then I need to be.
I just got to thinking about the #2 AWG wire size problem. It has a diameter of 0.378” with 19 strands.
#4 AWG is 0.318” or only 0.060” less. Each of the 19 strands on the #2 wire must be about 0.020” so clip the ends of 3 of them off and I think the remaining 16 will easily fit directly into the AC connector.
Probably the simplest and least loss way to do it. -
Re: Fairly long run from Inverter to AC Disconnect / Service.
Clip the three strands from the middle so the inspector won't catch it...LOL.
They get pretty testy here if they find out someone did that.
Brent
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed