3-phase AC current measurements with clamps
lazza
Solar Expert Posts: 336 ✭✭✭
Hi,
We're about to put in an Efergy E2 energy monitor for a house that has 3 phase electricity. The system is with a neutral, hence a Wye system, so each phase gives 230V between it and the neutral wire.. can I therefore simply put one clamp around the neutral wire to measure the total power consumption?
We're about to put in an Efergy E2 energy monitor for a house that has 3 phase electricity. The system is with a neutral, hence a Wye system, so each phase gives 230V between it and the neutral wire.. can I therefore simply put one clamp around the neutral wire to measure the total power consumption?
Comments
-
Re: 3-phase AC current measurements with clamps
No--You cannot.
The neutral wire carries the difference of the A/B/C three phase legs...
If you run 10 Amps A to Neutral => 10 amps on Neutral
If you run 10 amps on A+B+C then neutral would have (ideally) zero amps.
Its Vector Math, so the additions are not simple (if you have 10 amps on all three A-N with 1.0 PF and B-N with 0.5 PF and C-N with 0.67 PF, you will have some sort of non-zero current on the Neutral).
However--I do have a question... In the US, we use Delta and Wye (or "Y" or "Star") transformers from the utility (each has their own advantages/problems).
In the US we us Phase to Neutral (120 VAC) and Phase to Phase (240 VAC for Delta, 208 VAC for Wye).... And higher voltages too.
Are you using both Phase to Neural and Phase to Phase for this installation--Or just Phase to Phase (and no neutral needed)? Or only Phase to Neutral? (I don't know how the standard residential grid power is wired in Europe/Spain).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: 3-phase AC current measurements with clampsHi,
We're about to put in an Efergy E2 energy monitor for a house that has 3 phase electricity. The system is with a neutral, hence a Wye system, so each phase gives 230V between it and the neutral wire.. can I therefore simply put one clamp around the neutral wire to measure the total power consumption? -
Re: 3-phase AC current measurements with clampsHi,
We're about to put in an Efergy E2 energy monitor for a house that has 3 phase electricity. The system is with a neutral, hence a Wye system, so each phase gives 230V between it and the neutral wire.. can I therefore simply put one clamp around the neutral wire to measure the total power consumption?
If all of the loads are purely resistive, you can calculate the power knowing only the magnitude of the currents and voltages.SMA SB 3000, old BP panels.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed