Not sure if this is the right place to post this...One of my 4 Prosine 3.0's is giving me trouble. The Remote ACS shows erratic voltage readings and warnings about low battery and the inverter often shuts down. The battery voltage is at correct levels and does not fluctuate. I have switched ACS remote displays with the other machines and the same problem crops up. If there are any prosine techs around to help, I would greatly appreciate it as these units are rock-solid inverters and i would like to keep them in service.
Also, one of my inverters was pre-programmed as always on and would love to know how to do that to the other three.
THANKS !!!!
Also, one of my inverters was pre-programmed as always on and would love to know how to do that to the other three.
THANKS !!!!
Comments
-
Re: Inverter Help
Check the voltage on the DC input studs to the inverter--Make sure that there are no loose/dirty/poor connections between the battery and the inverter's DC input.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Inverter Help
good answer...never thought of that -
Re: Inverter Help
Follow up...Have checked DC lugs and voltage is soild inside the unit while ACS still erratic. Also ACS is giving me an occasional "No Communication Error"...have checked cables and jacks but all good. Would love some input form a Prosine Guru as to where to go next...Thanks !!! -
Re: Inverter Help
I need a little more info on how your system is setup.....are the inverters synced to each other how many watts of solar, does it happen at any load range or just one
would love a wiring diagram of your system and a picture -
Re: Inverter Help
4 Prosine Inverters (3kw each) tied in DC parallel to each other from 4 banks of 6v x4 AGMS (16 batteries) fed from 4kw solar mats through 2 Coleman Dump controllers. System goes off grid at 6am and back on at 7pm when bulk charging occurrs through the inverters internal chargers. Entire home is powered by these inverters. My profile shows the Diversion Controllers. System has worked flawlessy until last week with the one inverter shutting down every so often with the ACS showing erratic voltages and communication errors. ...Help !!! -
Re: Inverter Help
is each inverter on it's own bank of batteries, or are they paralleled , if they are paralleled , does that inverter have a longer cable.
check that the bypass switch hasnt been flipped
one thing you could do is switch the communication cables from 2 of the others , also you could isolate that inverter by unhooking the others, ac included and just use the one and add a load to see if it works without ac input
was there a fault number that comes up
it is a lot of work, but without being there to physically look at it, this is what I can come up with -
Re: Inverter Help
just being curious....are each of these inverters on their own breaker box, not sure and you didnt say.....but you can't stack these inverters and you say they run your whole house.......my suggestion is to sell those prosines and get an xw system hybrid or an outback system hybrid....you dont have to buy all the conduit boxes, you just need a good charge controller and with these 2 systems you need the system control panel for the xw or the mate for the outback
I really dont see how this system has held together as long as it has -
Re: Inverter Helpjust being curious....are each of these inverters on their own breaker box, not sure and you didnt say.....but you can't stack these inverters and you say they run your whole house.......my suggestion is to sell those prosines and get an xw system hybrid or an outback system hybrid....you dont have to buy all the conduit boxes, you just need a good charge controller and with these 2 systems you need the system control panel for the xw or the mate for the outback
I really dont see how this system has held together as long as it has
The inverters are only stacked and individually fused on the DC side. Each feeds its own area of the house with individual sub-panels. One of them is dedicated to a split system AC. -
Re: Inverter Helpis each inverter on it's own bank of batteries, or are they paralleled , if they are paralleled , does that inverter have a longer cable.
check that the bypass switch hasnt been flipped
one thing you could do is switch the communication cables from 2 of the others , also you could isolate that inverter by unhooking the others, ac included and just use the one and add a load to see if it works without ac input
was there a fault number that comes up
it is a lot of work, but without being there to physically look at it, this is what I can come up with
Have switched cables and swapped out ACS units to narrow down the trouble. At this point I am fairly convinced the main Control Board is defective... -
Re: Inverter Help
UPDATE:...now I really need your help..Have found a main control board from a Prosine 3.0 but it is from a 12volt inverter where mine is 24volt. The boards look identical but I would like a second opinion before taking the chance and switching them out...THANKS !!! -
Re: Inverter Help
the prosine 3.0 only came in 24 volt option......is the inverter on ebay....I wouldnt touch that one -
Re: Inverter Helpthe prosine 3.0 only came in 24 volt option......is the inverter on ebay....I wouldnt touch that one
No, this is a 12volt unit..see link..
http://www.ebay.com/itm/XANTREX-PROSINE-3-0-SINE-WAVE-POWER-INVERTER-CHARGER-tie-grid-solar-statpower-/231020603511?pt=US_Power_Inverters_&hash=item35c9e6a877
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed